You are currently viewing our boards as a guest which gives you limited access to view most discussions and access our other features. By joining our free community you will have access to post topics, communicate privately with other members (PM), respond to polls, upload content and access many other special features. Registration is fast, simple and absolutely free so please, join our community today!

If you have any problems with the registration process or your account login, please contact contact us.

Go Back   The Garage Journal Board > The Garage > Lighting & Electrical

Sponsored Links (Register now to hide all advertisements)

Reply
 
Thread Tools Search this Thread Display Modes
Old 02-24-2012, 04:59 PM   #1
elguappo
Member
 
elguappo's Avatar
 
Join Date: Dec 2008
Location: SACRAMENTO, CA
Posts: 95
Question Getting electrical to a small, external shed?

Im going to be building a small (4x8) shed in my side yard, and want to be able to have a light and at least 1 outlet over there to plug things into. Maybe even an externally mounted, motion sensing security light.

Its only about 25' from the main panel, but there is a concrete walkway in between. I can dig under that, no problem, but my questions come to: How far do I need to go?

I imagine conduit at least 12" below grade is needed.
Will I need a small sub panel in the shed?
Is there anything else obvious I am missing?

Thanks!
elguappo is offline   Reply With Quote
Old 02-24-2012, 05:11 PM   #2
p_mori7
Senior Member
 
p_mori7's Avatar
 
Join Date: Mar 2010
Location: Montreal, QC., Canada
Posts: 2,150
Default Re: Getting electrical to a small, external shed?

12" or so should be fine. I would not use a sub-panel. If you have room in your main panel, add a 15A breaker, and run black 12/2 UF (underground feeder, sometimes grey colored) from your box to an outlet in the shed. From the outlet you can power your lights.
__________________
My build thread here: http://www.garagejournal.com/forum/s...ad.php?t=63078
p_mori7 is offline   Reply With Quote
Sponsored Links (Register now to hide all advertisements)
Old 02-24-2012, 05:40 PM   #3
pattenp
Senior Member
 
pattenp's Avatar
 
Join Date: Jun 2008
Location: Virginia - USA
Posts: 5,816
Default Re: Getting electrical to a small, external shed?

Use direct bury UF 12/2, this is good for 120V 20A. Can be direct buried 12" if not over 120V @ 20A with GFCI protection. No sub-panel is needed just use a junction box for splitting to outlet and light. If the feed is not GFCI protected from the source (GFCI breaker or GFCI outlet) then the feed needs to be buried 24" if direct buried, 18" in PVC conduit, 6" in metal conduit.

Last edited by pattenp; 02-24-2012 at 05:53 PM.
pattenp is offline   Reply With Quote
Old 02-24-2012, 05:44 PM   #4
theoldwizard1
Senior Member
 
Join Date: Feb 2011
Location: SE MI
Posts: 12,381
Default Re: Getting electrical to a small, external shed?

Quote:
Originally Posted by elguappo View Post
... but there is a concrete walkway in between. I can dig under that, no problem, ...
If the walk way is small (less than 4') you can actually push a pipe under it.
theoldwizard1 is offline   Reply With Quote
Old 02-24-2012, 05:56 PM   #5
ishiboo
Senior Member
 
Join Date: Oct 2010
Location: Oshkosh, WI
Posts: 4,328
Default Re: Getting electrical to a small, external shed?

Quote:
Originally Posted by theoldwizard1 View Post
If the walk way is small (less than 4') you can actually push a pipe under it.
Or use a running garden hose if the soil is soft to excavate under it, just keep pushing until you get through to the other side.

patten's idea of 12-2 or 14-2 UF sounds like a plan.

You could also run 12-3 or 14-3 and have a MWBC, doubling your capacity for only a small increase in cost. I believe a MWBC is still acceptable to a shed even with the 1-circuit limit?
ishiboo is offline   Reply With Quote
Old 02-24-2012, 06:05 PM   #6
pattenp
Senior Member
 
pattenp's Avatar
 
Join Date: Jun 2008
Location: Virginia - USA
Posts: 5,816
Default Re: Getting electrical to a small, external shed?

A multiwire branch circuit is considered a single circuit for the purpose of this section, NEC 225.30 Number of Supplies.

Quote:
Originally Posted by ishiboo View Post
Or use a running garden hose if the soil is soft to excavate under it, just keep pushing until you get through to the other side.

patten's idea of 12-2 or 14-2 UF sounds like a plan.

You could also run 12-3 or 14-3 and have a MWBC, doubling your capacity for only a small increase in cost. I believe a MWBC is still acceptable to a shed even with the 1-circuit limit?
pattenp is offline   Reply With Quote
Old 02-24-2012, 06:21 PM   #7
SGKent
Senior Member
 
Join Date: Feb 2010
Location: Citrus Heights CA
Posts: 461
Default Re: Getting electrical to a small, external shed?

we ran a sub panel so we could run a compressor in the shed at night so it doesn't bother the neighbors.
SGKent is offline   Reply With Quote
Old 02-24-2012, 10:46 PM   #8
6768rogues
Senior Member
 
Join Date: Nov 2007
Location: Western NY
Posts: 1,401
Default Re: Getting electrical to a small, external shed?

Quote:
Originally Posted by theoldwizard1 View Post
If the walk way is small (less than 4') you can actually push a pipe under it.
I agree, push or drive a pipe under it and slide a conduit or wire through it.
__________________
Why a cool garage? Chicks dig 'em. Alcohol may intensify the effect. As John Belushi said in Animal House, "I suggest you drink and drink heavily."
6768rogues is offline   Reply With Quote
Old 02-25-2012, 12:11 AM   #9
elguappo
Member
 
elguappo's Avatar
 
Join Date: Dec 2008
Location: SACRAMENTO, CA
Posts: 95
Default Re: Getting electrical to a small, external shed?

Thanks guys.
Getting the wires under the walkway is the easy part (FOR ME).
I am pretty pissed because I specified to the monkey doing the walkway and pad under the trash cans, that I wanted conduit pipes at least 2" run under the walkway in at least 2 spots. He put down some 1/2" EMT. Not pleased.

I will have to take down a 5' section of fence to trench under it. It had to come down anyway to get rebuilt, so no big deal.

1 other question: how do I transition from the box to in the wall to the foundation to into the ground?

Thanks
elguappo is offline   Reply With Quote
Old 02-25-2012, 08:35 AM   #10
pattenp
Senior Member
 
pattenp's Avatar
 
Join Date: Jun 2008
Location: Virginia - USA
Posts: 5,816
Default Re: Getting electrical to a small, external shed?

If you are using direct bury UF cable then you need conduit from where it exits the ground to in the shed. The conduit can stop once it enters the shed and the cable can be run in the wall to where ever you place the box.
pattenp is offline   Reply With Quote
Old 02-25-2012, 01:48 PM   #11
elguappo
Member
 
elguappo's Avatar
 
Join Date: Dec 2008
Location: SACRAMENTO, CA
Posts: 95
Default Re: Getting electrical to a small, external shed?

Quote:
Originally Posted by pattenp View Post
If you are using direct bury UF cable then you need conduit from where it exits the ground to in the shed. The conduit can stop once it enters the shed and the cable can be run in the wall to where ever you place the box.
Thanks Pattenp,
I was more meaning at the main panel on the house, into the ground.
elguappo is offline   Reply With Quote
Old 02-25-2012, 02:51 PM   #12
matt151617
Senior Member
 
Join Date: Dec 2011
Location: Plattsburgh, NY
Posts: 360
Default Re: Getting electrical to a small, external shed?

You can run Romex from the panel to a junction box close to where it passes through the foundation, then run the conduit starting from the junction box out to the shed. Or you can just start the conduit at the panel.
matt151617 is offline   Reply With Quote
Old 02-25-2012, 04:00 PM   #13
pattenp
Senior Member
 
pattenp's Avatar
 
Join Date: Jun 2008
Location: Virginia - USA
Posts: 5,816
Default Re: Getting electrical to a small, external shed?

Have you decided to use UF cable? If so, UF can be installed the same as NM sheathed cable, meaning you can run one continuous UF cable with no splices from your house main panel out into the shed. The only places you need conduit is where the UF cable exits the house to where it enters the earth and where it exits the earth and enters the shed. Put bushings on the ends of conduit where the cable exits/enters the conduit to protect the cable from being cut. Use LB boxes where the cable will exit and enter the house wall and shed wall. Use short stubs of conduit just long enough to pass through the house foundation and shed wall. The conduit in the ground can stop after the sweep elbow.



Last edited by pattenp; 02-25-2012 at 04:21 PM.
pattenp is offline   Reply With Quote
Old 02-25-2012, 07:22 PM   #14
elguappo
Member
 
elguappo's Avatar
 
Join Date: Dec 2008
Location: SACRAMENTO, CA
Posts: 95
Default Re: Getting electrical to a small, external shed?

Perfect.
EXactly what I wanted to know.
Thanks guys!
elguappo is offline   Reply With Quote
Old 02-27-2012, 01:39 PM   #15
VHF
Senior Member
 
Join Date: Oct 2008
Location: NW Wisconsin
Posts: 400
Default Re: Getting electrical to a small, external shed?

Quote:
Originally Posted by elguappo View Post
...I wanted conduit pipes at least 2" run under the walkway in at least 2 spots. He put down some 1/2" EMT. Not pleased.
This is metal EMT conduit, not PVC, right? A single run of 12-2 UF should fit through a 1/2" EMT. Run 12-2 UF end-to-end. You would just be using the EMT as a sleeve under the concrete.
VHF is offline   Reply With Quote
Old 02-27-2012, 02:05 PM   #16
Highbeam
Senior Member
 
Join Date: Feb 2011
Location: South Puget Sound
Posts: 1,897
Default Re: Getting electrical to a small, external shed?

Ick, 12/2 is a tight fit in 1/2" romex. I would go bigger for ease of install.

I just had to buy 100 feet of 14/3 and the cost was DOUBLE the cost of 14/2.
Highbeam is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Sponsored Links (Register now to hide all advertisements)


All times are GMT -5. The time now is 03:39 AM.