Welcome to the The Garage Journal Board forums. You are currently viewing our boards as a guest which gives you limited access to view most discussions and access our other features. By joining our free community you will have access to post topics, communicate privately with other members (PM), respond to polls, upload content and access many other special features. Registration is fast, simple and absolutely free so please, join our community today! If you have any problems with the registration process or your account login, please contact contact us. |
|
|||||||
![]() |
|
Thread Tools | Display Modes |
|
|
#21 |
|
Union Wireman
Join Date: Jan 2006
Location: Las Vegas
Posts: 875
|
once you start getting into the 2000a range bus duct becomes more of an option. we have several 2000a bus ducts and several 4000a bus ducts here at the plant. we installed a 4000a generator connection box here and used 9 parallel runs of 750 mcm at a cost of $18 per foot. the total job cost was around $70k
|
|
|
|
|
|
#22 | |
|
Member
Join Date: Jul 2009
Location: Ontario Canada
Posts: 35
|
Quote:
|
|
|
|
|
|
|
#23 |
|
Senior Member
Join Date: Mar 2009
Location: Southwestern Ohio
Posts: 200
|
|
|
|
|
|
|
#24 |
|
Senior Member
Join Date: Oct 2011
Location: winnipeg, manitoba, canada
Posts: 357
|
definitely 5000
i believe the generator was 100MW |
|
|
|
|
|
#25 |
|
Senior Member
|
|
|
|
|
|
|
#26 |
|
Senior Member
Join Date: Dec 2009
Location: Indiana
Posts: 449
|
Maybe you may have used 500KCMIL this is sometimes referred to as
"500,000" (circular mils). 100MW at 13800 volts would be roughly 4188 amps. I am assuming you used MV90 or MV105 cable in a ductbank or above ground conduit. It would take (9) 500,000 circular mil (or 500KCMIL) cables for each phase to accomplish this primary. However most unlikely one would use a single 4500 or 5000 KCMIL cable. If this is in fact true I would love to see a picture of this cable or at least the specifications on the wire and the connectors to terminate such cable. |
|
|
|
|
|
#27 |
|
Senior Member
Join Date: Dec 2009
Location: Indiana
Posts: 449
|
![]() The copper mass of a 5000KCMIL would be roughly 2.25 inch diameter. If insulated the following would be present 1. Copper conductor 2. Inner semi-conducting layer 3. XLPE insulation 4. Outer semi-conducting layer 5. Semi-conducting tape 6. Copper wire screen 7. Separator tape 8. PE outer sheath You could be really close to a 4inch diameter !!!The cable below is 15000 volt 750KCMIL it has copper mass .9 inch diameter over all structure is 1.75 inch diameter. I cannot imagine handling cable over twice that size I would love to see it. I am sure somewhere in the world something like that would exist.
|
|
|
|
|
|
#28 |
|
Senior Member
|
Also, take a look in the NEC at the ampacity table. the ampacity difference between a 1750KCM and 2000KCM is 15 AMPS. the size difference is 250KCM, which in itself is good for 255amps. This is part of the reason you don't see much over 750 kcm as it's cheaper to add additional parallel runs rather than a larger size wire. I've done numerous jobs with 500 KCM, a few with 600 and even less with 750, I've never done anything larger than that. not to mention none of the supply houses stock it so you'd have to order a 500' minimum.
Last edited by Gooch; 04-15-2012 at 08:42 PM. |
|
|
|
|
|
#29 |
|
Member
Join Date: Feb 2011
Posts: 45
|
Prh44, Imagine pulling 750 triplex copper in a substation. Not fun at all
|
|
|
|
|
|
#30 | |
|
Senior Member
Join Date: Oct 2010
Location: Long Island
Posts: 2,963
|
Quote:
|
|
|
|
|
|
|
#31 | ||
|
Senior Member
Join Date: Dec 2009
Location: Indiana
Posts: 449
|
Quote:
Quote:
. Takes some rigging doesnt it!
|
||
|
|
|
|
|
#32 |
|
Senior Member
Join Date: Oct 2010
Location: Mountains
Posts: 1,493
|
The larger/largest industrial and commercial centers frequently have poco transformers and switching on site. With transformer secondary cables sized upwards of 2000, often paralleled, or large bus bars feeding the facility. It's not uncommon to also have a medusas nest of 1000, 750, & 500 cables as well.
Last edited by Roots; 04-16-2012 at 07:54 PM. |
|
|
|
|
|
#33 | |
|
Senior Member
Join Date: Mar 2009
Location: Central PA
Posts: 2,448
|
Quote:
|
|
|
|
|
|
|
#34 | |
|
Senior Member
Join Date: Oct 2010
Location: Mountains
Posts: 1,493
|
Quote:
|
|
|
|
|
|
|
#35 |
|
Senior Member
Join Date: Sep 2011
Location: Walnut Grove, CA
Posts: 592
|
Wow, that spool of 4/0 marine cable I have left over from my last inverter install now looks sorta puny! I was only dealing with about 500 amps at 12VDC... At least my stuff is very fine strand and more flexible (and expensive) than the typical on-shore stuff.
I can't think of any application in my situations where I'd ever need to go past 4/0. After that I start moving the voltage up. Heck, a lot of medium size boats are moving to 24 or 36 as their base voltage with DC/DC converters at the end to power the device just to get away from pulling huge cables. It ends up being cheaper and easier in the end. |
|
|
|
|
|
#36 | |
|
Senior Member
Join Date: Dec 2009
Location: Indiana
Posts: 449
|
Quote:
I wired an induction furnace were the phase conductors were actually hollow and water cooled! The voltage and hertz were variable, its been a while I can not remember the upper limit for the Hertz. That was pretty cool to see. I have some photos somewhere I will try to find them. |
|
|
|
|
|
|
#37 | |
|
Senior Member
Join Date: Sep 2005
Location: Minneapolis
Posts: 6,540
|
Quote:
|
|
|
|
|
|
|
#38 |
|
Senior Member
Join Date: Apr 2012
Location: Texas
Posts: 343
|
In commercial installations, I always laugh at multiple runs of 500 when 750 would have been fine. Till I have to bend it into the generator MLCB, that is!!!!
|
|
|
|
|
|
#39 |
|
Senior Member
Join Date: May 2011
Location: Peachland B.C. Canada
Posts: 212
|
largest to date for me, 8 runs per phase of 1000 MCM for feeds from the 13.8 Kv gen's and 6 gen sets on site. no pics sorry they wont even let us take our cell phones on site.
|
|
|
|
|
|
#40 |
|
Senior Member
Join Date: Dec 2006
Location: Michigan Thumb
Posts: 836
|
Induction heating is the area of my job. We build heat treat, tube Welders, brazing units, bonding systems, and billet heaters. Anywhere from line frequency to 450 kHz. Water cooling of the "wires" is required. Without it copper melts. The systems I work on go from 6kW on the low end to 3 mW of power on the high end. All kinds of strange conductors utilized to insure efficient power transfer. But when it goes bang it's spectacular. Some of the neatest things on my desk are from the melted results.
|
|
|
|
![]() |