You are currently viewing our boards as a guest which gives you limited access to view most discussions and access our other features. By joining our free community you will have access to post topics, communicate privately with other members (PM), respond to polls, upload content and access many other special features. Registration is fast, simple and absolutely free so please, join our community today!

If you have any problems with the registration process or your account login, please contact contact us.

Go Back   The Garage Journal Board > The Garage > Lighting & Electrical

Sponsored Links (Register now to hide all advertisements)

Reply
 
Thread Tools Search this Thread Display Modes
Old 04-14-2012, 11:25 AM   #21
rockwithjason
Union Wireman
 
rockwithjason's Avatar
 
Join Date: Jan 2006
Location: Las Vegas
Posts: 1,525
Default Re: What size service conductors do commercial buildings use

once you start getting into the 2000a range bus duct becomes more of an option. we have several 2000a bus ducts and several 4000a bus ducts here at the plant. we installed a 4000a generator connection box here and used 9 parallel runs of 750 mcm at a cost of $18 per foot. the total job cost was around $70k
rockwithjason is offline   Reply With Quote
Old 04-14-2012, 11:40 AM   #22
Rob_b
Member
 
Join Date: Jul 2009
Location: Ontario Canada
Posts: 87
Default Re: What size service conductors do commercial buildings use

Quote:
Originally Posted by awdblazer View Post
i have pulled parallel 5000kcm with a jacket rated for 13.8kV
generator leads to a step up transformer
Why would they even bother with such large cable? I've seen where bussbars are used for things like that. A site I worked with in Honolulu used bussbars from their transformers to the MCC gear. They had 4 - 5000amp step down 13400/480V that had a 200' + run to the MCC gear.
Rob_b is offline   Reply With Quote
Sponsored Links (Register now to hide all advertisements)
Old 04-14-2012, 01:08 PM   #23
foolishpride
Senior Member
 
foolishpride's Avatar
 
Join Date: Mar 2009
Location: Southwestern Ohio
Posts: 226
Default Re: What size service conductors do commercial buildings use

Quote:
Originally Posted by awdblazer View Post
i have pulled parallel 5000kcm with a jacket rated for 13.8kV
generator leads to a step up transformer
5000 KCM? I think you put one too many zeros in that.
foolishpride is offline   Reply With Quote
Old 04-15-2012, 12:36 PM   #24
awdblazer
Senior Member
 
Join Date: Oct 2011
Location: winnipeg, manitoba, canada
Posts: 683
Default Re: What size service conductors do commercial buildings use

definitely 5000
i believe the generator was 100MW
awdblazer is offline   Reply With Quote
Old 04-15-2012, 06:00 PM   #25
Gooch
Senior Member
 
Join Date: May 2009
Location: Petersberg, IA
Posts: 611
Send a message via AIM to Gooch Send a message via MSN to Gooch
Default Re: What size service conductors do commercial buildings use

Quote:
Originally Posted by awdblazer View Post
definitely 5000
i believe the generator was 100MW
so the wire was about the size of 4" pipe?
Gooch is offline   Reply With Quote
Old 04-15-2012, 06:43 PM   #26
PRH44
Senior Member
 
PRH44's Avatar
 
Join Date: Dec 2009
Location: Indiana
Posts: 549
Default Re: What size service conductors do commercial buildings use

Quote:
Originally Posted by awdblazer View Post
definitely 5000
i believe the generator was 100MW
Maybe you may have used 500KCMIL this is sometimes referred to as
"500,000" (circular mils).
100MW at 13800 volts would be roughly 4188 amps.
I am assuming you used MV90 or MV105 cable in a ductbank or above ground conduit.
It would take (9) 500,000 circular mil (or 500KCMIL) cables for each phase to accomplish this primary.
However most unlikely one would use a single 4500 or 5000 KCMIL cable. If this is in fact true I would love to see a picture of this cable or at least the specifications on the wire and the connectors to terminate such cable.
PRH44 is offline   Reply With Quote
Old 04-15-2012, 07:27 PM   #27
PRH44
Senior Member
 
PRH44's Avatar
 
Join Date: Dec 2009
Location: Indiana
Posts: 549
Default Re: What size service conductors do commercial buildings use

Quote:
Originally Posted by Gooch View Post
so the wire was about the size of 4" pipe?


The copper mass of a 5000KCMIL would be roughly 2.25 inch diameter. If insulated the following would be present
1. Copper conductor
2. Inner semi-conducting layer
3. XLPE insulation
4. Outer semi-conducting layer
5. Semi-conducting tape
6. Copper wire screen
7. Separator tape
8. PE outer sheath

You could be really close to a 4inch diameter !!!



The cable below is 15000 volt 750KCMIL it has copper mass .9 inch diameter over all structure is 1.75 inch diameter. I cannot imagine handling cable over twice that size I would love to see it. I am sure somewhere in the world something like that would exist.

PRH44 is offline   Reply With Quote
Old 04-15-2012, 08:38 PM   #28
Gooch
Senior Member
 
Join Date: May 2009
Location: Petersberg, IA
Posts: 611
Send a message via AIM to Gooch Send a message via MSN to Gooch
Default Re: What size service conductors do commercial buildings use

Also, take a look in the NEC at the ampacity table. the ampacity difference between a 1750KCM and 2000KCM is 15 AMPS. the size difference is 250KCM, which in itself is good for 255amps. This is part of the reason you don't see much over 750 kcm as it's cheaper to add additional parallel runs rather than a larger size wire. I've done numerous jobs with 500 KCM, a few with 600 and even less with 750, I've never done anything larger than that. not to mention none of the supply houses stock it so you'd have to order a 500' minimum.

Last edited by Gooch; 04-15-2012 at 08:42 PM.
Gooch is offline   Reply With Quote
Old 04-15-2012, 08:54 PM   #29
fast one
Member
 
Join Date: Feb 2011
Posts: 47
Default Re: What size service conductors do commercial buildings use

Prh44, Imagine pulling 750 triplex copper in a substation. Not fun at all
fast one is offline   Reply With Quote
Old 04-15-2012, 10:00 PM   #30
rlitman
Senior Member
 
Join Date: Oct 2010
Location: Long Island
Posts: 4,693
Default Re: What size service conductors do commercial buildings use

Quote:
Originally Posted by Gooch View Post
Also, take a look in the NEC at the ampacity table. the ampacity difference between a 1750KCM and 2000KCM is 15 AMPS. the size difference is 250KCM, which in itself is good for 255amps. This is part of the reason you don't see much over 750 kcm as it's cheaper to add additional parallel runs rather than a larger size wire. I've done numerous jobs with 500 KCM, a few with 600 and even less with 750, I've never done anything larger than that. not to mention none of the supply houses stock it so you'd have to order a 500' minimum.
Yes. This is due to the skin effect. It's not something you'd notice with smaller cables at 60hz, but it does come into play with these kind of sizes.
rlitman is offline   Reply With Quote
Old 04-16-2012, 06:24 PM   #31
PRH44
Senior Member
 
PRH44's Avatar
 
Join Date: Dec 2009
Location: Indiana
Posts: 549
Default Re: What size service conductors do commercial buildings use

Quote:
Originally Posted by rlitman View Post
Yes. This is due to the skin effect. It's not something you'd notice with smaller cables at 60hz, but it does come into play with these kind of sizes.
I agree, you really waste copper mass when get into the larger sizes. For that reason alone smaller parallel runs make a more logical choice.

Quote:
Originally Posted by fast one View Post
Prh44, Imagine pulling 750 triplex copper in a substation. Not fun at all
sounds like you had the pleasure . Takes some rigging doesnt it!
PRH44 is offline   Reply With Quote
Old 04-16-2012, 07:47 PM   #32
Roots
Senior Member
 
Join Date: Oct 2010
Posts: 1,790
Default Re: What size service conductors do commercial buildings use

The larger/largest industrial and commercial centers frequently have poco transformers and switching on site. With transformer secondary cables sized upwards of 2000, often paralleled, or large bus bars feeding the facility. It's not uncommon to also have a medusas nest of 1000, 750, & 500 cables as well.

Last edited by Roots; 04-16-2012 at 07:54 PM.
Roots is offline   Reply With Quote
Old 04-16-2012, 07:48 PM   #33
Alchymist
Senior Member
 
Alchymist's Avatar
 
Join Date: Mar 2009
Location: Central PA
Posts: 3,076
Default Re: What size service conductors do commercial buildings use

Quote:
Originally Posted by rlitman View Post
Yes. This is due to the skin effect. It's not something you'd notice with smaller cables at 60hz, but it does come into play with these kind of sizes.
Quote:
Originally Posted by PRH44 View Post
I agree, you really waste copper mass when get into the larger sizes. For that reason alone smaller parallel runs make a more logical choice.
Some of the high power RF stuff I worked with used tubing for conductors - all the current was carried in the tube, the hollow inside would have carried very little current even if present. The higher the frequency, the less the core carries. Noticeable at 400 Hz also.
Alchymist is offline   Reply With Quote
Old 04-16-2012, 07:52 PM   #34
Roots
Senior Member
 
Join Date: Oct 2010
Posts: 1,790
Default Re: What size service conductors do commercial buildings use

Quote:
Originally Posted by Alchymist View Post
Some of the high power RF stuff I worked with used tubing for conductors - all the current was carried in the tube, the hollow inside would have carried very little current even if present. The higher the frequency, the less the core carries. Noticeable at 400 Hz also.
It that very reason, skin effect, that larger bus bars are often tubes or square - hollow inside.
Roots is offline   Reply With Quote
Old 04-16-2012, 09:13 PM   #35
Zelatore
Senior Member
 
Join Date: Sep 2011
Location: Walnut Grove, CA
Posts: 781
Default Re: What size service conductors do commercial buildings use

Wow, that spool of 4/0 marine cable I have left over from my last inverter install now looks sorta puny! I was only dealing with about 500 amps at 12VDC... At least my stuff is very fine strand and more flexible (and expensive) than the typical on-shore stuff.

I can't think of any application in my situations where I'd ever need to go past 4/0. After that I start moving the voltage up. Heck, a lot of medium size boats are moving to 24 or 36 as their base voltage with DC/DC converters at the end to power the device just to get away from pulling huge cables. It ends up being cheaper and easier in the end.
Zelatore is offline   Reply With Quote
Old 04-17-2012, 01:21 PM   #36
PRH44
Senior Member
 
PRH44's Avatar
 
Join Date: Dec 2009
Location: Indiana
Posts: 549
Default Re: What size service conductors do commercial buildings use

Quote:
Originally Posted by Alchymist View Post
Some of the high power RF stuff I worked with used tubing for conductors - all the current was carried in the tube, the hollow inside would have carried very little current even if present. The higher the frequency, the less the core carries. Noticeable at 400 Hz also.
Hollow tubing is commonly used in substation structures, on different voltage levels, from medium at 15000 to high at 136000 60 HZ.
I wired an induction furnace were the phase conductors were actually hollow and water cooled! The voltage and hertz were variable, its been a while I can not remember the upper limit for the Hertz. That was pretty cool to see. I have some photos somewhere I will try to find them.
PRH44 is offline   Reply With Quote
Old 04-17-2012, 02:05 PM   #37
Stuart in MN
Senior Member
 
Stuart in MN's Avatar
 
Join Date: Sep 2005
Location: Minneapolis
Posts: 8,390
Default Re: What size service conductors do commercial buildings use

Quote:
Originally Posted by PRH44 View Post
I wired an induction furnace were the phase conductors were actually hollow and water cooled!
Water cooled conductors are pretty common for things like induction furnaces - I used some for a plasma arc torch design years ago, it was kind of hard to get used to the idea that you can run water through an electrical cable without getting shocked.
Stuart in MN is offline   Reply With Quote
Old 04-20-2012, 07:32 AM   #38
The Frisco Kid
Senior Member
 
The Frisco Kid's Avatar
 
Join Date: Apr 2012
Location: Texas
Posts: 555
Default Re: What size service conductors do commercial buildings use

In commercial installations, I always laugh at multiple runs of 500 when 750 would have been fine. Till I have to bend it into the generator MLCB, that is!!!!
The Frisco Kid is offline   Reply With Quote
Old 04-20-2012, 03:19 PM   #39
Delta74
Senior Member
 
Join Date: May 2011
Location: Peachland B.C. Canada
Posts: 307
Default Re: What size service conductors do commercial buildings use

largest to date for me, 8 runs per phase of 1000 MCM for feeds from the 13.8 Kv gen's and 6 gen sets on site. no pics sorry they wont even let us take our cell phones on site.
Delta74 is offline   Reply With Quote
Old 04-21-2012, 10:33 AM   #40
RPH
Senior Member
 
Join Date: Dec 2006
Location: Michigan Thumb
Posts: 1,040
Default Re: What size service conductors do commercial buildings use

Induction heating is the area of my job. We build heat treat, tube Welders, brazing units, bonding systems, and billet heaters. Anywhere from line frequency to 450 kHz. Water cooling of the "wires" is required. Without it copper melts. The systems I work on go from 6kW on the low end to 3 mW of power on the high end. All kinds of strange conductors utilized to insure efficient power transfer. But when it goes bang it's spectacular. Some of the neatest things on my desk are from the melted results.
RPH is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Sponsored Links (Register now to hide all advertisements)


All times are GMT -5. The time now is 10:38 PM.