You are currently viewing our boards as a guest which gives you limited access to view most discussions and access our other features. By joining our free community you will have access to post topics, communicate privately with other members (PM), respond to polls, upload content and access many other special features. Registration is fast, simple and absolutely free so please, join our community today!

If you have any problems with the registration process or your account login, please contact contact us.

Go Back   The Garage Journal Board > The Tools > General Tool Discussion

Sponsored Links (Register now to hide all advertisements)

Reply
 
Thread Tools Search this Thread Display Modes
Old 07-06-2009, 06:14 PM   #1
Blacknwhitepit
Senior Member
 
Blacknwhitepit's Avatar
 
Join Date: Feb 2005
Location: Central Ohio
Posts: 3,164
Default Why does my compressor keep tripping the circuit breaker?

I am getting a bit frustrated now. I have a 33 Gal Craftsman compressor. It is rated for 15 amps. Now I originally had in on a 15 Amp service outlet. It would get to about 90 psi then trip the breaker.

I installed a dedicated 20 amp line (I used the correct wire as well) on a 20 amp circuit breaker with an outlet rated for 20 amps.

Here is the kicker now. It charges air up until it automatically shuts off (125 psi). After it has turned itself off, within about 5 minutes I hear the circuit breaker trip (It was not even trying to pull a load). Mind you this circuit breaker has only 1 electric line going to the outlet. Why does it do this?

Could it be a weak/bad circuit breaker? or could my compressor be trying for more than 20 amps?

I use it on my 20 amp service in my house with an extension cord and it does just fine.



-BWP
__________________
Blacknwhitepit is offline   Reply With Quote
Old 07-06-2009, 06:21 PM   #2
fatfillup
Senior Member
 
Join Date: Jan 2009
Location: Finksburg, Md
Posts: 2,547
Default Re: Why does my compressor keep tripping the circuit breaker?

Can you amp test the compressor while its running to see what its pulling? Also, how far is the run from the breaker box to the oulet you are having the problem with? You may need to go to heavier wire due to distance. Could be a bad breaker. You could always switch the breaker that it runs on in the house ok to the breaker you are having problems with to test whether its a breaker problem or wire size?distance problem.

Seems odd to me that it trips with no load on. If its pulling the correct amount of amps while its running and your not getting a voltage drop while its running then breaker is suspect.
fatfillup is offline   Reply With Quote
Sponsored Links (Register now to hide all advertisements)
Old 07-06-2009, 06:40 PM   #3
volvo420coupe
Senior Member
 
volvo420coupe's Avatar
 
Join Date: Dec 2008
Location: central Michigan
Posts: 598
Default Re: Why does my compressor keep tripping the circuit breaker?

I've only had problems with my compressor tripping breakers in cold weather on startup. I am interested to hear what caused the problem when you find it.
volvo420coupe is offline   Reply With Quote
Old 07-06-2009, 07:09 PM   #4
walrus
Senior Member
 
walrus's Avatar
 
Join Date: Nov 2008
Location: Maine
Posts: 4,086
Default Re: Why does my compressor keep tripping the circuit breaker?

Quote:
Originally Posted by Blacknwhitepit View Post
After it has turned itself off, within about 5 minutes I hear the circuit breaker trip (
Its the only thing on the circuit and it trips when the compressor is not running?
walrus is offline   Reply With Quote
Old 07-06-2009, 07:24 PM   #5
Blacknwhitepit
Senior Member
 
Blacknwhitepit's Avatar
 
Join Date: Feb 2005
Location: Central Ohio
Posts: 3,164
Lightbulb Re: Why does my compressor keep tripping the circuit breaker?

Quote:
Originally Posted by fatfillup View Post
Can you amp test the compressor while its running to see what its pulling? Also, how far is the run from the breaker box to the oulet you are having the problem with? You may need to go to heavier wire due to distance. Could be a bad breaker. You could always switch the breaker that it runs on in the house ok to the breaker you are having problems with to test whether its a breaker problem or wire size?distance problem.

Seems odd to me that it trips with no load on. If its pulling the correct amount of amps while its running and your not getting a voltage drop while its running then breaker is suspect.
Good questions.

The wire is less than 15 feet in length from the circuit breaker box.

I ran #10 wire just for overkill.

I am thinking it is the breaker (chinese made box store type).

I also think it is weird it is tripping with no load.

I have a clamp on tester. I will try that... But like you say, why would it work with load, and then fail without one?

-BWP
__________________
Blacknwhitepit is offline   Reply With Quote
Old 07-06-2009, 07:25 PM   #6
Blacknwhitepit
Senior Member
 
Blacknwhitepit's Avatar
 
Join Date: Feb 2005
Location: Central Ohio
Posts: 3,164
Default Re: Why does my compressor keep tripping the circuit breaker?

Quote:
Originally Posted by walrus View Post
Its the only thing on the circuit and it trips when the compressor is not running?
Yes, it is a line I just ran for the compressor. It only trips about 5 minutes after the compressor has automatically shutoff...

-BWP
__________________
Blacknwhitepit is offline   Reply With Quote
Old 07-06-2009, 07:42 PM   #7
eric87
Senior Member
 
Join Date: Feb 2009
Posts: 169
Default Re: Why does my compressor keep tripping the circuit breaker?

you could have a bad plug or outlet
eric87 is offline   Reply With Quote
Old 07-06-2009, 07:45 PM   #8
Blacknwhitepit
Senior Member
 
Blacknwhitepit's Avatar
 
Join Date: Feb 2005
Location: Central Ohio
Posts: 3,164
Default Re: Why does my compressor keep tripping the circuit breaker?

Quote:
Originally Posted by eric87 View Post
you could have a bad plug or outlet
Bought the outlet from Lowe's a week ago... Tried a completely different (and new) one today. Both rated at 20 Amps. Both made in USA. BTW both are not GFCI.

The plug is barely used. In excellent condition. I bought this compressor new.

-BWP
__________________

Last edited by Blacknwhitepit; 07-06-2009 at 07:48 PM.
Blacknwhitepit is offline   Reply With Quote
Old 07-06-2009, 07:54 PM   #9
Bustawrench
Senior Member
 
Join Date: Dec 2008
Posts: 519
Default Re: Why does my compressor keep tripping the circuit breaker?

Put an ammeter on it and see what's going on.

Is the breaker warm/hot after it trips?

Try swapping the breaker out for another one in the panel, just to see what happens. If the new braker does the same thing, the problem is soomewhere else.
Bustawrench is offline   Reply With Quote
Old 07-06-2009, 08:00 PM   #10
Blacknwhitepit
Senior Member
 
Blacknwhitepit's Avatar
 
Join Date: Feb 2005
Location: Central Ohio
Posts: 3,164
Default Re: Why does my compressor keep tripping the circuit breaker?

Quote:
Originally Posted by Bustawrench View Post
Put an ammeter on it and see what's going on.

Is the breaker warm/hot after it trips?

Try swapping the breaker out for another one in the panel, just to see what happens. If the new braker does the same thing, the problem is soomewhere else.
The breaker is not hot. (Nor the wires )

For less than $4.00 I will go to Lowes and try another breaker. I only have two other breakers that are 20 Amp service which are a completely different brand than the one I bought for this line/service.

Thanks

-BWP
__________________

Last edited by Blacknwhitepit; 07-06-2009 at 08:02 PM.
Blacknwhitepit is offline   Reply With Quote
Old 07-06-2009, 08:10 PM   #11
Bustawrench
Senior Member
 
Join Date: Dec 2008
Posts: 519
Default Re: Why does my compressor keep tripping the circuit breaker?

Quote:
Originally Posted by Blacknwhitepit View Post
The breaker is not hot. (Nor the wires )

For less than $4.00 I will go to Lowes and try another breaker. I only have two other breakers that are 20 Amp service which are a completely different brand than the one I bought for this line/service.

Thanks

-BWP
Try to stay with the same brand of breaker as the panel itself.
Bustawrench is offline   Reply With Quote
Old 07-06-2009, 08:14 PM   #12
Blacknwhitepit
Senior Member
 
Blacknwhitepit's Avatar
 
Join Date: Feb 2005
Location: Central Ohio
Posts: 3,164
Default Re: Why does my compressor keep tripping the circuit breaker?

I unscrewed the outlet.





Here is a picture of the breaker box. The two breakers I have installed are the two bottom ones. Upon noticing this picture I saw that they were a different 'Type' from the others.

There are type QP and the ones I installed were HOM. Is there a difference?
Perhaps this is an issue?



-BWP
__________________
Blacknwhitepit is offline   Reply With Quote
Old 07-06-2009, 08:31 PM   #13
Bustawrench
Senior Member
 
Join Date: Dec 2008
Posts: 519
Default Re: Why does my compressor keep tripping the circuit breaker?

Looks like Square D breakers in a Seimens (?) box.........

doesn't look like they really fit to me.........

Only reason I can think of would be poor fit at the buss, causeing the breaker to heat up slowly and trip. Could be current leakage thru the compressor switch to ground, what happens if you unplug the compressor as soon as it shuts off? Does breaker still trip 5 minutes later?
Bustawrench is offline   Reply With Quote
Old 07-06-2009, 08:33 PM   #14
Blacknwhitepit
Senior Member
 
Blacknwhitepit's Avatar
 
Join Date: Feb 2005
Location: Central Ohio
Posts: 3,164
Default Re: Why does my compressor keep tripping the circuit breaker?

Quote:
Originally Posted by Bustawrench View Post
Looks like Square D breakers in a Seimens (?) box.........

doesn't look like they really fit to me.........

Only reason I can think of would be poor fit at the buss, causeing the breaker to heat up slowly and trip. Could be current leakage thru the compressor switch to ground, what happens if you unplug the compressor as soon as it shuts off? Does breaker still trip 5 minutes later?
They clip in and snap on just fine...... Fit like normal.....


I will try unplugging the compressor and see what happens.

Thanks

-BWP
__________________
Blacknwhitepit is offline   Reply With Quote
Old 07-06-2009, 08:43 PM   #15
Blacknwhitepit
Senior Member
 
Blacknwhitepit's Avatar
 
Join Date: Feb 2005
Location: Central Ohio
Posts: 3,164
Default Re: Why does my compressor keep tripping the circuit breaker?

Interesting... It has cooled off here now (ambient air temperature), and I cannot get it to trip..... Hmmmmm....


-BWP
__________________

Last edited by Blacknwhitepit; 07-06-2009 at 09:08 PM.
Blacknwhitepit is offline   Reply With Quote
Old 07-06-2009, 09:50 PM   #16
Charles (in GA)
Senior Member
 
Charles (in GA)'s Avatar
 
Join Date: Jan 2006
Location: 50 mi south of Atlanta
Posts: 11,051
Default Re: Why does my compressor keep tripping the circuit breaker?

Square D Homeline crap. Funny part is how much noise Square D makes about breakers of one brand not being legal to use in a panel of a different brand, even if they fit, yet they came out with the Homeline crap and made it the same as Siemens, Bryant, Murray, GE, etc so it would interchange. They have their own propriety line of panels and breakers, why they felt they needed to introduce the Homeline is beyond me.

Go out and buy a Siemens breaker, at least that is what the rest of yours are (easily spotted by the beveled surface where the ON and OFF lettering is.

Charles
Charles (in GA) is offline   Reply With Quote
Old 07-07-2009, 05:17 AM   #17
Fins/413
Senior Member
 
Join Date: Jan 2009
Posts: 161
Default Re: Why does my compressor keep tripping the circuit breaker?

Make sure your line voltage isn't too high, had that problem years ago and had 135 to 140 VAC. the power company relaced the transformer no more problem.
__________________
Eric Corse
Wake Forest, NC
1959 Chryler New Yorker
Fins/413 is offline   Reply With Quote
Old 07-07-2009, 07:29 AM   #18
rhandwor
Senior Member
 
Join Date: Oct 2008
Posts: 1,056
Default Re: Why does my compressor keep tripping the circuit breaker?

Check the fit of the plug sometimes non commercial plugs aren't tight enough. Buy a 20 amp plug if it still trips I would try another breaker.
You stated it runs on an extension cord from another 20 amp breaker.
My craftsman compressor can run on 110v or 220v I would suggest hooking it up to 220v
they run better.
rhandwor is offline   Reply With Quote
Old 07-07-2009, 08:17 AM   #19
sberry
Senior Member
 
sberry's Avatar
 
Join Date: Jun 2005
Location: Brethren, Michigan
Posts: 11,202
Default Re: Why does my compressor keep tripping the circuit breaker?

Quote:
They have their own propriety line of panels and breakers, why they felt they needed to introduce the Homeline is beyond me.
They wanted a line to compete with Challenger, Siemens, etc. It was a brilliant move by the right people, they became the original equipment in a lot of mobile and modular homes now. If you ever need a company turn around hire the guys that come up with that, now a standard stock in most box stores. Excellent business and marketing strategy.
sberry is offline   Reply With Quote
Old 07-07-2009, 08:28 AM   #20
Blacknwhitepit
Senior Member
 
Blacknwhitepit's Avatar
 
Join Date: Feb 2005
Location: Central Ohio
Posts: 3,164
Default Re: Why does my compressor keep tripping the circuit breaker?

Quote:
Originally Posted by rhandwor View Post
Check the fit of the plug sometimes non commercial plugs aren't tight enough. Buy a 20 amp plug if it still trips I would try another breaker.
You stated it runs on an extension cord from another 20 amp breaker.
My craftsman compressor can run on 110v or 220v I would suggest hooking it up to 220v
they run better.

I would like to run a 220 line. But, I am out of spaces in my box. I could run an additional panel, but given that I can't make a relatively simple circuit work, I am going to hold off on that.

Anyone know what a Pro costs to run an service panel?

-BWP
__________________

Last edited by Blacknwhitepit; 07-07-2009 at 08:43 AM.
Blacknwhitepit is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On

Forum Jump

Sponsored Links (Register now to hide all advertisements)


All times are GMT -5. The time now is 10:43 AM.