You are currently viewing our boards as a guest which gives you limited access to view most discussions and access our other features. By joining our free community you will have access to post topics, communicate privately with other members (PM), respond to polls, upload content and access many other special features. Registration is fast, simple and absolutely free so please, join our community today!

If you have any problems with the registration process or your account login, please contact contact us.

Go Back   The Garage Journal Board > The Garage > Lighting & Electrical

Sponsored Links (Register now to hide all advertisements)

Reply
 
Thread Tools Search this Thread Display Modes
Old 02-20-2012, 12:07 PM   #1
blackdart66
Member
 
Join Date: Jun 2011
Posts: 45
Default wire size for electric furnace

Hi all...

Little confused on what size wire to run for a 10KW electric furnace I am installing in the shop.

I have a 200 amp service in the shop.

HVAC guys who is doing the install said he needed a 60 amp breaker and #8 wire with 2 conductors and a ground. When I went to Home Depot, I see that wire is only rated for like 55 amps. Or maybe it was 50. anyway I know it was less than 60. I see I can get the THHN and it was like 65 amps. I would have to run conduit for the THHN which is easy to do as the interor is not finished yet but the romex style is a lot easier.

Advice ?
blackdart66 is offline   Reply With Quote
Old 02-20-2012, 12:15 PM   #2
50cal
Member
 
50cal's Avatar
 
Join Date: Sep 2009
Posts: 84
Default Re: wire size for electric furnace

An HVAC guy is not a Electrician. I have seen them clamp a meter on a conductor and it only reads X draw so wire is big enough. Use the proper size wire for the rating of the unit your insurance company will appreciate it.
50cal is offline   Reply With Quote
Sponsored Links (Register now to hide all advertisements)
Old 02-20-2012, 12:33 PM   #3
50cal
Member
 
50cal's Avatar
 
Join Date: Sep 2009
Posts: 84
Default Re: wire size for electric furnace

Here are a couple of links.
http://ecmweb.com/mag/electric_comme..._calculations/
http://www.rowand.net/Shop/Tech/WireCapacityChart.htm
http://www.altestore.com/howto/Solar...ur-System/a62/
50cal is offline   Reply With Quote
Old 02-20-2012, 12:37 PM   #4
PRH44
Senior Member
 
PRH44's Avatar
 
Join Date: Dec 2009
Location: Indiana
Posts: 545
Default Re: wire size for electric furnace

A 10 KW load at 240 volt will result in 41.67 amp load.
Your wire and breaker should be sized at 1.25% of 41.67A = 52A .
This would require a 60 amp breaker.
The following is based on copper conductors only.
this would require #6 wire, #8 is not large enough.
You could use a # 6 romex or SE cable this will net you 55 amps at 60 degree C.
Code allows you to round up to the next standard size breaker in this instance, which would be a 60 Amp.
A #6 THHN single conductors in a conduit will be 65 amps at 75 degree C.
Bottom line is you need # 6 wire on a 60 amp breaker.
PRH44 is offline   Reply With Quote
Old 02-20-2012, 12:38 PM   #5
50cal
Member
 
50cal's Avatar
 
Join Date: Sep 2009
Posts: 84
Default Re: wire size for electric furnace

When I did my electric heat I went to a local electric supply house to get my wire. They will have colors Red, Blue, Black, Green. Helps to avoid the confusion.
50cal is offline   Reply With Quote
Old 02-20-2012, 12:50 PM   #6
PRH44
Senior Member
 
PRH44's Avatar
 
Join Date: Dec 2009
Location: Indiana
Posts: 545
Default Re: wire size for electric furnace

Blackdart66. I based my information a 240 volt single phase feed. Is what you have?
PRH44 is offline   Reply With Quote
Old 02-20-2012, 03:33 PM   #7
blackdart66
Member
 
Join Date: Jun 2011
Posts: 45
Default Re: wire size for electric furnace

yes....240 volt single phase.........

Thanks for the info !
blackdart66 is offline   Reply With Quote
Old 02-20-2012, 05:21 PM   #8
Aceman
Senior Member
 
Join Date: Jan 2007
Location: Eastern Oregon
Posts: 1,868
Default Re: wire size for electric furnace

What I do is look for a plate on the side of the unit that says:

MCA(minimum circuit ampacity=wire size)
MOCP(maximum overcurrent protective device=breaker size)

If for some reason I can't find that plate, then I'll use the breaker size in the unit to determine wire ampacity and breaker size.
Aceman is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Sponsored Links (Register now to hide all advertisements)


All times are GMT -5. The time now is 06:10 AM.