Welcome to the The Garage Journal Board forums. You are currently viewing our boards as a guest which gives you limited access to view most discussions and access our other features. By joining our free community you will have access to post topics, communicate privately with other members (PM), respond to polls, upload content and access many other special features. Registration is fast, simple and absolutely free so please, join our community today! If you have any problems with the registration process or your account login, please contact contact us. |
|
|||||||
![]() |
|
Thread Tools | Display Modes |
|
|
#1 |
|
Senior Member
Join Date: Feb 2012
Location: Spokane, WA
Posts: 208
|
I live in climate zone 5 and am getting ready to install a 75K natural gas Big Maxx heater in the 800 sq ft attached garage with 9' ceilings. The walls and ceiling are already sheetrocked so I'll use blown-in insulation for both the walls and the attic above the ceiling. I know that there was no vapor barrier installed before the sheetrock, so my question is this: What does that mean in this situation? Will this cause serious problems for me or is it simply just a factor of not being done in the most energy efficient way?
Thanks, Paul |
|
|
|
|
|
#2 |
|
Senior Member
Join Date: Aug 2009
Location: Slate River, ON
Posts: 2,403
|
It will mean big inefficiencies.
A well sealed building does more than good insulation. Although they are part of a good package. The insulation slows the exchange of warm and cold while the VB stops the movement of air, speeding that exchange of heat and cold. Use an online heat loss calculator with and without VB and you will see the difference. If you heating intermittently you can just live with it but can run the risk of mold in the walls. Not a definite but a possibility.
__________________
"Success is when you reach a point in your life when you don't feel the need to go back and change things." Johnny S. www.LauraMyersPhotography.com Last edited by dirttracker18; 03-03-2012 at 06:29 PM. |
|
|
|
|
|
#3 | |
|
Senior Member
Join Date: Dec 2007
Location: Saskatoon, SK
Posts: 8,918
|
I think VB would be critical in an "attached" garage - especially if you're ever going to bring in a wet or snow-covered vehicle. As you likely know, the VB stops moisture from going though the wall to condensate on the insulation, or freeze against the siding in winter, only to melt later and affect the siding.
You're in luck though - some paints can act like a VB. Research them a bit and you'll find that by sealing and painting with the correct material, you can get almost the same barrier as with properly installed plastic. Make sure to seal around light fixtures and switches. Another help would be a fan running that pulls moist air out. I have a window fan running in my shop most of the year - it sucks heat\fumes from the cars out in summer and moisture at other times. Hope that helps - we'll see what the pro's say!
__________________
VISIT me at www.E-TekRestorations.com OR, read the blog: www.E-TekRestorations.blogspot.com Quote:
|
|
|
|
|
|
|
#4 |
|
Senior Member
Join Date: Oct 2010
Location: Delaware County, NYS
Posts: 493
|
Closed cell spray foam would be a solution although spendy. Closed cell acts as a VP when applied in thicknesses over 3". Around here, closed cell is selling for $.85 per sf per inch of thickness applied.
|
|
|
|
|
|
#5 | |
|
Senior Member
Join Date: Nov 2011
Posts: 217
|
Quote:
I would us it in the attic though |
|
|
|
|
|
|
#6 |
|
Senior Member
Join Date: Feb 2012
Location: Spokane, WA
Posts: 208
|
I understand the theory of VB and an airtight envelope preventing moisture movement into the wall/ceiling cavities, however, how practical is that in a typical garage? Wouldn't the articulated garage doors (even though each panel is insulated with foil-faced stryrofoam sheets) be the weak link that prevents the garage from being airtight? Wouldn't it be easier for any moisture in the garage to escape through the garage doors and their associated air gaps rather than penetrating through sheetrock into the walls and ceiling?
I didn't know there was such a thing as VB paint, but unless it's really cost prohibitive, I'll probably prime the walls and ceiling using such a product. What would be worse (i.e. from a moisture penetrating the walls/ceiling and freezing/melting/ruining insulation/causing mold standpoint), trying to keep the garage at a constant temp (say 55F) at all times, or just heating to 60-65F when I'm working and letting it go down to 35-40 when I'm not out there? Paul |
|
|
|
|
|
#7 |
|
Senior Member
Join Date: Jun 2008
Location: Virginia - USA
Posts: 3,759
|
$67 for 5 gal on Amazon
|
|
|
|
|
|
#8 |
|
Member
|
Oil based paints and primers can act as a form of a vapour barrier. This was commonly used in older houses without vapour barrier.
It would likely require 1-2 coats of oil based primer, and then a coat of oil based paint to be effective. I would recomend 2 primer and 2 coats of paint to completely make it a "true" vapour barrier. For the interior of houses I rarely use oil based stuff due to clean-up & possible health issues and it really isn't necessary as compared to modern latex blends for everyday finishes of walls and trim. I did use oil based recently for a used oil tank I bought for my garage. Due to modern insurance and oil inspectors obsession with surface rust on oil tanks (despite the fact it is less than 8 years old), I gave it a coat of oil based paint prior to installation. We have a 20 year limit on interior oil tanks in Ontario. The oil paint gave a nice finish on metal, and for future metal projects that require durability, I will be repeating. I just threw out the brushes when I was done, and anything I poured the paint into. When dealing with oil based paints, ensure you let whatever tools you will be disposing of air dry in the open before disposal. While I haven't heard of it, oily rags have caused fires when tossed in a can, and I treat oil based paints the same way even though I have no justification to. Just let your brushes/rollers/cans dry in the open before you toss them if your local area allows. At this stage, the oil based stuff is probably your only solution.... it will really seal in your drywall finish, and it will be a very durable finish. R |
|
|
|
|
|
#9 | |
|
Senior Member
Join Date: Oct 2011
Location: Western Washington
Posts: 1,013
|
Quote:
In our area new houses are built to have garage as a cold zone....its not a good idea to turn a cold zone into a warms zone like our houses.....thats why your point is correct the garage doors are a weak link because it was never intented to be a warm zone. Do you know what R-values you put or will be in the walls and Attic? In Spokane Valley, the minimum R-value in a basement is an R-21....I know the walls are close to that R-value so I am not sure you can get enough in the walls with blown it. Even if you get enough insulation in, you will still be wasting a ton of energy and dollars to heat a room all the time, given that it was never designed to be that. I would love that heater in my Shop (which is uninsulated) for when I am in there during the cold....it sounds awesome! |
|
|
|
|
|
|
#10 |
|
Senior Member
Join Date: Nov 2007
Location: Western NY
Posts: 1,157
|
Heat moves from places of high heat to places of low heat and water vapor moves from places of high water vapor to places of low water vapor.
Say your building is 60 degrees inside and it is 10 degrees outside. The inside of your insulation is warm and moist, the outside is cold and dry. Heat and water vapor try to escape through the insulation. At some point between inside and outside, the temp will reach the freezing point. That is where the water vapor will freeze in the insulation. Repeat the process a few times and you will have soaked insulation and all the problems that go with it. I would at least use a good vapor retarding paint.
__________________
Why a cool garage? Chicks dig 'em. Alcohol may intensify the effect. As John Belushi said in Animal House, "I suggest you drink and drink heavily." |
|
|
|
|
|
#11 |
|
Senior Member
Join Date: Aug 2011
Location: Minneapolis
Posts: 418
|
First, your heater is a least twice too big, likely 3x.
Next, 2"-2# foam can be injected in existing walls, and should be installed first over the finished ceiling with cellulose. |
|
|
|
|
|
#12 | |
|
Senior Member
Join Date: Mar 2012
Location: Grafton, Wisconsin
Posts: 758
|
Quote:
__________________
20x22 attached garage (Sears opener w/40w lite, one 75w ceiling lite on pull chain, no heat no running water no TV no AC, one GFCI outlet on main bath circuit in a lousy location), added 8 outlet (4 in each location w/GFCI), 10x20 detached garage (one outlet in wrong location & 75w ceiling light on pull chain), looking to build bigger garage. #90 Heilig-Meyers Ford Taurus-1996 Suburban 1500-24' enclosed trailer-lots of tools Wears sound warnings like a badge of honor |
|
|
|
|
|
|
#13 | |
|
Senior Member
Join Date: Feb 2012
Location: Spokane, WA
Posts: 208
|
Quote:
Paul |
|
|
|
|
|
|
#14 |
|
Senior Member
Join Date: Nov 2006
Posts: 301
|
Do we need VB here in the south-Ms? I don't have it in my house and do not see it in new construction here. I don't have any signs of mold.
|
|
|
|
|
|
#15 |
|
Senior Member
Join Date: Feb 2012
Location: Spokane, WA
Posts: 208
|
Kippieland,
Well, Hello to you too, neighbor! Without heat or insulation, my 3-1/2 car garage rarely got below freezing (at least the water stored out there has never frozen) but it certainly is too cold for extended work periods. I know it'll be hard to effectively insulate, but with the large heater, I think I can keep it comfortable while I am out there. With the blow-in Attic Cat insulation I got from HD, I can get R13 to R15 in the 2x4 walls and can get anywhere fro R19 to R49 in the ceiling depending on how deep I lay it. I installed 1" rigid foam in the garage doors which should only give me about R-5. With those constraints, I probably won't go more than R-25-30 in the garage attic. Definately will use a VB primer on the drywall before the finish coat. With the 75K heater and low temperature thermostat I have, I could lower the garage temp down to 35-40F when I'm not working and hopefully raise it rather quickly to 60-65 when I want to work comfortably. I'll just have to wait and see how it works... Paul Last edited by nwav8tor; 03-04-2012 at 11:49 PM. |
|
|
|
|
|
#16 |
|
Senior Member
Join Date: Feb 2011
Location: South Puget Sound
Posts: 1,057
|
Funny. In western WA, modern construction doesn't use plastic for the VB anywhere. The homes are built and then painted with the VB paint and/or enough latex paint to provide the barrier. This is a mold/water issue and not an efficiency issue.
As far as energy savings, if you have properly finished the sheetrock with taped joints then just where do you expect heated air to leak into the attic? The air sealing is done with the sheetrock. Your efficiency is only slightly better, if at all, with a plastic VB. |
|
|
|
|
|
#17 | |
|
Senior Member
Join Date: Oct 2011
Location: Western Washington
Posts: 1,013
|
Quote:
As long as your not trying to convert it into a warm zone from a cold then real goal would be to keep the heat from escaping as fast. Thats the goal of the thin pole building insulation. Plus, in the summer it will keep it a bit cooler as well. Sounds awesome to me and make sure you make a thread in the garage forum for use to droul over! |
|
|
|
|
|
|
#18 | |
|
Senior Member
Join Date: Oct 2011
Location: Western Washington
Posts: 1,013
|
Quote:
It is funny the differencies between the two areas. You can get away with a lot less because of the higher temps in the winter, where here we have to have higher R-values for both extremes....summer...keep the AC in and winter keep the heat in. Also, we heat more with Natural gas here because it is the most efficient at low temps....but I personally have an electric heat pump that turns off at 35 degrees. On the other hand, we don't do any of the things you guys do for water removal around the house. When we lived in Granite falls ALL our gutters where piped to the main waste line. Here they just dumb on the ground....but it doesn't rain anything like over there. I would say, Western WA is more advanced then use....we are ALWAYS 10 years behind! |
|
|
|
|
|
|
#19 | |
|
Senior Member
Join Date: Feb 2012
Location: Spokane, WA
Posts: 208
|
Quote:
Not sure if plastic VB is code here or not or when it started to be required. I do know I have it down in the basement, but not everywhere above ground... I'm planning to just use the VB paint primer in the garage since I hope that was also used on the rest of the house when it was built 16 years ago. Garage IS completely rocked, taped and mudded. I know the VB is for moisture control which retards mold, but it also prevents saturation of the insulation which would decrease the efficiency of the insulation. My main insulation inefficiency worries were/are only being able to get R-15 in the walls and only R-5 on the garage doors. Some serious potential for heat loss there, but better than no insulation at all! Paul Last edited by nwav8tor; 03-05-2012 at 04:59 PM. |
|
|
|
|
|
|
#20 | |
|
Senior Member
Join Date: Feb 2012
Location: Spokane, WA
Posts: 208
|
Quote:
Paul |
|
|
|
|
|
|
#21 |
|
Senior Member
Join Date: Mar 2011
Location: michigan
Posts: 129
|
Can someone with a home older than 15-20 years old please climb up in their attic and pull back some insulation and check for vapor barrier and mold, my bet is you won't find either. Truth is most homes built even today aren't built with vapor barrier. With that said I think a garage that is only heated part time will have higher moisture levels and that may cause an issue after awhile.
|
|
|
|
|
|
#22 | |
|
Senior Member
Join Date: Oct 2011
Location: Western Washington
Posts: 1,013
|
Quote:
|
|
|
|
|
|
|
#23 | |
|
Member
|
Quote:
A vapour barrier is part of the system, and I would always add it into a garage that was built from scratch. With an attached garage it will assist in stopping migration of fumes from a garage into a house (that and 5/8" drywall with min two coats of plaster finish). With any garage I built, I would still add vapour barrier unless closed cell spray foam is used. After the fact is just too late, or a downright pain to retrofit. Most of the pros who care about their job, even if they don't insulate the ceiling with blown in, if they finish the ceiling with drywall, they add vapour barrier before drywall. The cost is minimal, and is easily built into the estimate. R |
|
|
|
|
|
|
#24 |
|
Senior Member
Join Date: Nov 2008
Location: Maine
Posts: 3,653
|
|
|
|
|
|
|
#25 |
|
Senior Member
Join Date: Mar 2011
Location: Between Raleigh and Fayetteville, NC, USA
Posts: 264
|
A better name for a "vapor barrier" is a Class I Vapor Retarder.
In your climate zone, you do need to provide an interior vapor control layer, but unless the heater puts out as much moisture as a spa or pool, you neither need, nor should want, a Class I Vapor Retarder. References and more detail are included in this post.
__________________
Disclaimer: I'm not a building professional. |
|
|
|
|
|
#26 |
|
Senior Member
Join Date: Feb 2011
Location: South Puget Sound
Posts: 1,057
|
For the purposes of this thread....
A plastic sheet is a VB, enough of the right kind of paint is also a VB. I never said that homes aren't being built with a VB in western WA but that they do not use plastic for the VB. It's just way way cheaper to spray a coat of that VB paint on as a primer coat than to mess with plastic sheets. My home was built in 1963 and foil faced batts were used in the walls and attic so yes, a VB was used even 50 years ago. I prefer the sealing properties of the plastic sheet but I also recognize that by the time you screw 1000 holes into it with staples, lighting, and sheetrock screws it is not perfect. Still better than painted on and why not use plastic and the painted on stuff. Even regular latex paint acts to block vapors to some extent. Good point above about how an improper VB can lead to efficiency problems once enough water has soaked through to saturate the insulation. I was thinking more along the lines of actual heated air leakage which will be stopped with a complete layer of sheetrock. Vapors can still pass through though. |
|
|
|
|
|
#27 | |
|
Senior Member
Join Date: Mar 2011
Location: Between Raleigh and Fayetteville, NC, USA
Posts: 264
|
Quote:
To address those areas, the Airtight Drywall Approach uses gaskets, foam or caulk. Not all the place they specify are intuitively obvious to me, but I assume some of the places that they recommend measures beyond mudding and taping has to do with reliability of the joint. It doesn't apply in the OP's situation, but there are those who prefer an exterior air barrier.
__________________
Disclaimer: I'm not a building professional. |
|
|
|
|
|
|
#28 |
|
Senior Member
Join Date: Feb 2011
Location: South Puget Sound
Posts: 1,057
|
At the bottom plate? This is air sealing for the living space and if you seal everything above the floor then it is not unlike a bell or bowl in water. The air bubble is trapped. The floor level openings are least important. We are trying to avoid the chimney effect.
Rough openings are the same whether you depend on the sheetrock or on plastic, you still have a penetration to seal. |
|
|
|
![]() |