Welcome to the The Garage Journal Board forums. You are currently viewing our boards as a guest which gives you limited access to view most discussions and access our other features. By joining our free community you will have access to post topics, communicate privately with other members (PM), respond to polls, upload content and access many other special features. Registration is fast, simple and absolutely free so please, join our community today! If you have any problems with the registration process or your account login, please contact contact us. |
|
|||||||
![]() |
|
Thread Tools | Display Modes |
|
|
#1 |
|
Junior Member
Join Date: Jan 2012
Posts: 4
|
I may have made a big mistake. I installed a new 100 amp sub-panel in my detached garage. I have already ran the conduit and cable from the house to the garage. It's buried and has several 90 degree turns in it. The box is in place and all the switches and receptacles are wired. Sheetrock has been hung. The sub-panel has not been connected to the box in the house yet. The wire is just hanging there right now. The wire is two hot and one neutral.
Question is: Do I have to have a ground wire running from the house box to the box in the detached garage? Can I run a copper wire from the sub-panel in the detached garage to a grounding rod just outside the garage? Do I need to do that? |
|
|
|
|
|
#2 |
|
Senior Member
Join Date: Oct 2011
Location: Portland Oregon
Posts: 1,425
|
When I did mine I was told to ground the box in the garage to a grounding rod, box in house has its own and so does the one in the garage.
That's here, your area may be different.
__________________
Making the World a Better Place, One Engine at a Time! |
|
|
|
|
|
#3 |
|
Senior Member
Join Date: Jun 2009
Location: Merkel, TX
Posts: 7,302
|
Current code requires 4 wires to the sub and the neutral bus at the sub to be held insulated from the panel. However, for many years three wires to a detached building with a ground at the building was standard procedure. You see it in farm buildings a lot. My old shop was two hots, neutral with an 8' rod at the shop. The power came right off the meter can, not out of the house panel. The install was blessed by a master. YMMV. If you are coming out of the house panel on a breaker, I'm thinking you're missing a wire.
__________________
Chris - Merkel, TX http://raceabilene.com/kelly/hotrod GJ Build thread :http://www.garagejournal.com/forum/s...d.php?t=100482 Last edited by Falcon67; 03-08-2012 at 11:31 AM. |
|
|
|
|
|
#4 |
|
Senior Member
Join Date: Jan 2006
Location: 50 mi south of Atlanta
Posts: 8,825
|
Current code, and I think the past couple of code cycles, has required FOUR wires between a main panel and a sub panel. Two hots, a neutral, and a ground. At the sub panel, the neutral and ground must be kept separated and the neutral has to be insulated from the panel's housing.
Conduit rules allow no more than 360° of bends between pull points, that would be four 90° bends. When you say "several 90 degree turns in it" it sounds as if you have exceeded the 360° rule, which makes it very difficult to pull new wire in the conduit. Charles |
|
|
|
|
|
#5 |
|
Senior Member
Join Date: Jun 2008
Location: Virginia - USA
Posts: 3,754
|
Yep.. as you are hearing you need an equipment ground wire that runs from main panel to sub-panel. Also at the detached garage you need to run a ground wire from the sub-panel to two 8' ground rods driven into the earth at least 6' apart for each other.
|
|
|
|
|
|
#6 |
|
Senior Member
Join Date: Jun 2008
Location: Virginia - USA
Posts: 3,754
|
What size conduit and wire did you use? You mentioned cable, was it a 3 conductor sheathed cable or 3 individual wires? If it's a cable then you aren't allowed to pull a separate wire for the ground. If you have three individual wires then you can pull the forth wire for your ground. Try using a shop vac to suck through a string with a small piece of cloth tied to it to use to get a pull rope through to pull a ground wire.
Last edited by pattenp; 03-08-2012 at 02:06 PM. |
|
|
|
|
|
#7 |
|
Senior Member
Join Date: Nov 2007
Location: Western NY
Posts: 1,157
|
One of the posts talks about having both an equipment ground from the main panel to the subpanel and ground rods at the subpanel. I may be mistaken, but I thought that grounding at the main panel and grounding at the subpanel being connected was to be avoided. The reason is that if the grounding potential at the main panel and the subpanel are different, the interconnected grounding wire could become a current carrying conductor. Electrical gurus, please set me straight.
__________________
Why a cool garage? Chicks dig 'em. Alcohol may intensify the effect. As John Belushi said in Animal House, "I suggest you drink and drink heavily." |
|
|
|
|
|
#8 | |
|
Senior Member
Join Date: Jan 2007
Location: Eastern Oregon
Posts: 1,601
|
Quote:
If anyone tells you otherwise, it's a pretty good indicator they aren't an electrician. So take it with a grain of salt.... |
|
|
|
|
|
|
#9 |
|
Senior Member
Join Date: Jun 2005
Location: Brethren, Michigan
Posts: 6,661
|
Pull wires out, add another one, fix it, no way around.
__________________
www.urkafarms.com |
|
|
|
|
|
#10 |
|
Senior Member
Join Date: Jun 2009
Location: Merkel, TX
Posts: 7,302
|
X2 - glad that was added. Or a UFER, if available.
__________________
Chris - Merkel, TX http://raceabilene.com/kelly/hotrod GJ Build thread :http://www.garagejournal.com/forum/s...d.php?t=100482 |
|
|
|
|
|
#11 |
|
Senior Member
Join Date: Mar 2008
Posts: 2,580
|
|
|
|
|
|
|
#12 | |
|
Senior Member
Join Date: Jun 2008
Location: Virginia - USA
Posts: 3,754
|
You may be getting confused with the requirement that the neutral and ground are not to be bonded at the sub-panel vs at the main panel the neutral and ground are bonded.
Quote:
|
|
|
|
|
|
|
#13 |
|
Junior Member
Join Date: Nov 2006
Location: Providence RI
Posts: 6
|
UFER?
I'll be doing this myself to my garage; I've already run the four individual #6 wires through the conduit, in preparation for the subpanel, so this is good information. What is the standard way to run the ground-wires out through the wall to the grounding-rods? More small-diameter PVC conduit from the subpanel box, through the outer wall to carry the THHN wire, and then just have a short run of the wire out in the open to the clamp on the ground-rod? The wire in my basement from the box to the grounding-rod in the hole where my water-meter sits is just uninsulated stranded copper with no special protection, but then again, it doesn't see any weather. |
|
|
|
|
|
#14 |
|
Senior Member
Join Date: Jan 2006
Location: 50 mi south of Atlanta
Posts: 8,825
|
Use a solid #6 copper for the ground, and you don't need to give it any protection beyond not installing it where it can get damaged. Drill a tiny hole in the wall out thru the wall and down to the ground rod. Anything smaller than #6 or not solid, and you have to have it protected with conduit, etc.
Charles |
|
|
|
|
|
#15 | |
|
Senior Member
Join Date: Feb 2011
Location: South Puget Sound
Posts: 1,049
|
Quote:
Passed inspections fine. Is that solid wire thing a preference or a requirement? |
|
|
|
|
|
|
#16 |
|
Senior Member
Join Date: Feb 2008
Posts: 261
|
I bet the solid wire corrodes more slowly and is probably cheaper. Vote preference.
|
|
|
|
|
|
#17 |
|
Senior Member
Join Date: Jun 2008
Location: Virginia - USA
Posts: 3,754
|
Code only specifies that the ground conductor is to be #6 or larger to not be in conduit and not subject to physical damage. Can be solid or stranded.
|
|
|
|
|
|
#18 |
|
Junior Member
Join Date: Mar 2012
Posts: 1
|
so do you run 2 grounding wires out of the box, one to each grounding rod; or do you run 1 grounding wire out of the box and split it outside to go to the 2 rods? I've never seen 2 grounding rods being used. is this new? what is the point?
|
|
|
|
|
|
#19 |
|
Senior Member
Join Date: Jun 2008
Location: Virginia - USA
Posts: 3,754
|
You use one continuous wire running from the panel to the first rod and then on to second rod. The two rod suggestion is because you need to reach a certain level of resistance to earth of 25 ohms or less. If you can meet that resistance level using one rod then only one rod is needed. To test the fact that one rod meets this requirement is a pain so it’s easier to just add the supplemental rod as allow by code. 2011 NEC 250.53
|
|
|
|
|
|
#20 |
|
Senior Member
Join Date: Jun 2009
Location: Merkel, TX
Posts: 7,302
|
"New" since 2008 if I recall right. Another reason why a UFER is common practice and an easier deal if done during construction.
__________________
Chris - Merkel, TX http://raceabilene.com/kelly/hotrod GJ Build thread :http://www.garagejournal.com/forum/s...d.php?t=100482 |
|
|
|
![]() |