Welcome to the The Garage Journal Board forums. You are currently viewing our boards as a guest which gives you limited access to view most discussions and access our other features. By joining our free community you will have access to post topics, communicate privately with other members (PM), respond to polls, upload content and access many other special features. Registration is fast, simple and absolutely free so please, join our community today! If you have any problems with the registration process or your account login, please contact contact us. |
|
|||||||
![]() |
|
Thread Tools | Display Modes |
|
|
#1 |
|
Senior Member
Join Date: Dec 2008
Location: Lafayette, LA
Posts: 1,409
|
Anything special about wiring smoke/fire detectors? I want to install 5 detectors and have them all go off if one detects an issue.
Do the detectors have to be on a separate circuit or can they get power from any circuit. I am assuming I must use 12/3 wire with the red wire being the interconnected wire between the units. Any thing else?
__________________
. . . . . _______________________________________ My garage and steel home build thread... http://garagejournal.com/forum/showthread.php?t=91518 |
|
|
|
|
|
#2 |
|
Senior Member
Join Date: Apr 2010
Location: somerset NJ
Posts: 343
|
my installed system is all wireless but i have a monitoring company along with a burglar alarm and i dont need to worry about it being heard thru out the house because the speaker screams lol you cant miss it ive set it off a few times by accident.
You should have it on a seperate circuit as matter of fact it may be code, i know in multi family dwellings in NJ you have to do it that way and also have a lock on the breaker so it cant be shut off. If we test an alarm in the basement we have to be able to hear it all thru the home. In a private dwelling new construction I believe its a requirement now as well. Last edited by Lawson4450; 03-11-2012 at 10:00 PM. |
|
|
|
|
|
#3 |
|
Senior Member
Join Date: May 2011
Location: Napa Valley, California
Posts: 1,643
|
I don't have much to add to your questions, but they are pretty easy to replace.
We needed a new one in our rental (The renter packed it and took it. Grrr. long story). I was dreading figuring out how to replace it, but it was a non-issue. there are $15 replacements for wired fire alarms at Home Depot. They seem to all have one or two standard power plugs (which come in the replacement detector). Just unscrew the old mounting ring, screw on the new mounting ring, plug the new detector in, and fit the detector into it's mounting ring. M_P
__________________
Rivets are the New Duct Tape. Very close to finishing up the first Fantastic Light Bracket in The Aerodrome Studio--my metalworking studio in a 2-car, attached garage, where I build artistic projects, inpired by aeroplanes - The Aerodrome Studio: http://www.garagejournal.com/forum/s...d.php?t=122188 - Solid Rivets 101: http://www.garagejournal.com/forum/s...d.php?t=172474 - Blog: http://TheAerodromeStudio.com/wordpress -Twitter @Machine_Punk |
|
|
|
|
|
#4 | |
|
Senior Member
Join Date: Oct 2010
Location: Oshkosh, WI
Posts: 2,326
|
Quote:
Nothing special... on the Kidde at least, the white/black are the standard AC wires and the red is connected between all of them. You can buy relays that connect to external alarm systems as well. I suggest installing them on a separate circuit, but the models you'll find are battery backup, so you could install them on something existing if necessary. |
|
|
|
|
|
|
#5 |
|
Senior Member
|
DO NOT INSTALL WIRED SMOKE DETECTORS ON THEIR OWN CIRCUIT!!!!!
Putting them on their own circuit facilitates turning the circuit off if there is a problem with one of the units. Putting them on a commonly used circuit will require fixing the problem correctly. Find a 15 amp circuit, and take a piece of 14-2 to the first detector, then take 14-3 to the rest. the red wire is for the interconnect. |
|
|
|
|
|
#6 | |
|
Senior Member
Join Date: Jan 2010
Location: The Bad Lands
Posts: 6,856
|
Something else to consider, is to install a EOLR (End Of Line Resistor) to the smoke / co detector. This assumes this system is being monitored as well.
The intent is to ensure a measure of safety and security at all times with respect to the integrity of the fire system. Should any of the units encounter a fault, bad wiring, etc. Using a EOL resistor will immediately detect such a fault. Not using a EOL resistor will reflect a false sense of security for the home owner. Teken . . .
__________________
Do or Die . . . No one gets left behind !! Quote:
|
|
|
|
|
|
|
#7 | |
|
Senior Member
Join Date: Mar 2009
Location: Central PA
Posts: 2,455
|
Quote:
|
|
|
|
|
|
|
#8 |
|
Senior Member
Join Date: May 2011
Location: Cleveland, Ohio
Posts: 5,525
|
What he said...
__________________
Jeff Moss Self-proclaimed President of the Harry Epstein Fan Club Feedback Thread |
|
|
|
|
|
#9 | ||
|
Senior Member
Join Date: Oct 2010
Location: Oshkosh, WI
Posts: 2,326
|
Quote:
The 14-3 should be run to an access point if you ever plan on integrating with an alarm system, as you need to connect to it. Quote:
|
||
|
|
|
|
|
#10 | ||
|
Senior Member
Join Date: Jan 2010
Location: The Bad Lands
Posts: 6,856
|
Quote:
I can't really envision why anyone would have an alarm system and not have the smoke / CO portion not monitored. But, many people do, so it is what it is . . . As it was also stated, employing a EOL resistor will enable fault detection. Not, deploying said device will give the user a false sense of security when there is not. This is why it is called a life and safety device . . . Teken . . .
__________________
Do or Die . . . No one gets left behind !! Quote:
Last edited by Teken; 03-12-2012 at 12:02 PM. |
||
|
|
|
|
|
#11 | ||
|
Senior Member
Join Date: Jan 2010
Location: The Bad Lands
Posts: 6,856
|
Quote:
Teken . . .
__________________
Do or Die . . . No one gets left behind !! Quote:
|
||
|
|
|
|
|
#12 |
|
Senior Member
Join Date: Oct 2010
Location: Oshkosh, WI
Posts: 2,326
|
I never mentioned wireless either, where did you get wireless from?
|
|
|
|
|
|
#13 |
|
Senior Member
Join Date: May 2011
Location: Cleveland, Ohio
Posts: 5,525
|
We have hardwired heat detectors and 2 hardwired smokes on our alarm system, with a couple battery operated ones as well.
__________________
Jeff Moss Self-proclaimed President of the Harry Epstein Fan Club Feedback Thread |
|
|
|
|
|
#14 | |||
|
Senior Member
Join Date: Jan 2010
Location: The Bad Lands
Posts: 6,856
|
Quote:
Quote:
Teken . . .
__________________
Do or Die . . . No one gets left behind !! Quote:
|
|||
|
|
|
|
|
#15 | |
|
Senior Member
Join Date: Oct 2010
Location: Oshkosh, WI
Posts: 2,326
|
Nope. RF refers to a particular portion of the frequency band which is often wireless, but not necessarily. In the consumer world it's often used to refer to wireless, but RF is no more always wireless than a tissue is always a Kleenex
![]() ![]() Kidde also makes a wireless system, though I have no experience with it. I just installed the complete hardwire system in my house. Quote:
When I install a security system, I have the alarm connected to a steel box before it goes into the load center... I'll just stick the two modules in and be good to go with two separate signals to identify whether it's smoke or CO by assigning a zone to each. Security system is low on the priority list. |
|
|
|
|
|
|
#16 |
|
Senior Member
Join Date: Dec 2008
Location: Lafayette, LA
Posts: 1,409
|
Thanks for all the information.
I will not have a monitored alarm system and no need for CO detection either. I live in the country and by the time the monitoring service gets the alarm signal and the fire department showing up, there will not be much left so no need to spend the 30 bucks per month. I had mentioned the 12/3 since that is what I used through out the entire house. I could etiher run a new dedicated circuit using 14/3 or tie into another circuit using 12/3. I did speak to an electrician this morning from my area in our area, it does not need to be a dedicated circuit but they mucy be interconnected. I saw wireless systems mentioned a couple of times in this thread. Anyone familiar with them? Reliable? Pros-Cons?
__________________
. . . . . _______________________________________ My garage and steel home build thread... http://garagejournal.com/forum/showthread.php?t=91518 |
|
|
|
|
|
#17 | ||
|
Senior Member
Join Date: Jan 2010
Location: The Bad Lands
Posts: 6,856
|
Quote:
Your missing my whole point. Lets stay on topic here for a moment shall we. I stated that ideally the OP should have is smoke / co monitored with his home security system. If it is great . . . Now, to bolster that system, is to install a EOL resister to the smoke / co interconnected system. This will ensure that if there is a fault no matter what it is. It will be detected, and be made aware to the user / monitoring station. With respect to RF, you will not hear anyone mistake a smoke / co detector with a frequency. It is always referred to as it being a wireless device. Teken . . .
__________________
Do or Die . . . No one gets left behind !! Quote:
Last edited by Teken; 03-12-2012 at 12:44 PM. |
||
|
|
|
|
|
#18 | ||
|
Senior Member
Join Date: Jan 2010
Location: The Bad Lands
Posts: 6,856
|
Quote:
1. Mixing RF devices with wired interconnected smoke devices allows you flexibility. Anywhere were there is NOT existing wiring or where it is hard to do so. Using a wireless module will allow you to deploy them anywhere. 2. Wireless devices will not be affected by a surge / spike condition. Rendering your device useless if and when you need to count on them. 3. They are all interconnected the same as wired devices. One sounds and they all sound. I use the First Alert One Link combination smoke / CO detectors. As stated above it provides you redundancy, scalability, and a isolated system. All the while it can be monitored via a alarm company. Regardless of monitoring this hybrid system will provide you the most robust system with out any weaknesses. Of course they are all battery operated and they also speak to indicate where the fire / CO is happening. Teken . . .
__________________
Do or Die . . . No one gets left behind !! Quote:
|
||
|
|
|
|
|
#19 | |
|
Senior Member
Join Date: Oct 2010
Location: Oshkosh, WI
Posts: 2,326
|
Quote:
These systems DO NOT wire directly to the security system, there is NO REASON for an EOL resistor because it's a different type of signal. They are not a normal security system add-on, they are designed #1 to interconnect with each other. The module I showed you a picture of converts things to a normal signal the security system can consume the signal. This is why you do not see an EOL in any of their diagrams, installation instructions, etc. etc. etc. |
|
|
|
|
|
|
#20 | ||
|
Senior Member
Join Date: Jan 2010
Location: The Bad Lands
Posts: 6,856
|
Quote:
![]() Monitoring your smokes is the same as monitoring the sump pump, low temp, water zone. The difference comes down to whether the user is deploying a low voltage 2 / 4 wire system. Now since this is a 120 VAC system the wiring is indeed different but the same principles still apply. Having the ability to monitor the the working status of a smoke / CO device is not just a nice to have. It is a measure of safety and knowing things are actually working! Teken . . .
__________________