You are currently viewing our boards as a guest which gives you limited access to view most discussions and access our other features. By joining our free community you will have access to post topics, communicate privately with other members (PM), respond to polls, upload content and access many other special features. Registration is fast, simple and absolutely free so please, join our community today!

If you have any problems with the registration process or your account login, please contact contact us.

Go Back   The Garage Journal Board > The Garage > Lighting & Electrical

Sponsored Links (Register now to hide all advertisements)

Reply
 
Thread Tools Search this Thread Display Modes
Old 09-24-2012, 09:30 AM   #1
mod600
Member
 
Join Date: Apr 2012
Posts: 64
Default Cutler Hammer CH vs BR

Shortly I'm going to be working getting a service panel hooked up in my shop. I'm planning on running 100 amp service out there. In my house I have a Cutler Hammer CH service panel. My Dad recommended getting the same thing for the shop. It looks like the biggest 100 amp CH panel only comes with 20-22 spaces. Dad has the BR 100 amp box with 30-32 spaces in it. He went with that style box cause that's what his house had. He said the CH is a better box, the box and breakers are priced higher than the BR ones.

I think the standard 20-22 space CH box would be fine, I kinda was hoping for extra spaces for the future. But when that time comes I can always add another panel too I guess. But was curious as to what the difference was between the two styles...
Thanks in advance!
mod60
mod600 is offline   Reply With Quote
Old 09-24-2012, 09:50 AM   #2
Charles (in GA)
Senior Member
 
Charles (in GA)'s Avatar
 
Join Date: Jan 2006
Location: 50 mi south of Atlanta
Posts: 10,799
Default Re: Cutler Hammer CH vs BR

CH breakers and panels were originally designed by CH and are non-interchangable with other brands in any way shape or form. They are a propriety design in the way the breakers connect to the bus bar and mount. Many people consider them a superior design of breaker (the internals of them)

BR breakers and panels are a design that Eaton/Cutler-Hammer acquired with the purchase of the Bryant Electrical Company. The BR series is a quality product, but there is really nothing special about it.The breakers are physically interchangeable with Homeline, GE, Siemens, Westinghouse, and Murray (a Siemens division), and possibly others. Being physically interchangeable does not mean that it is legal or legitimate per code or UL listing to do so, however.

If you want more breaker spaces than the 100 amp CH panels provide, just go to a 150 or 200 amp CH panel with more breaker positions. It is not necessary to use a breaker panel rated the same as the feeder circuit is designed for, it can be a larger panel as long as the circuit is properly protected in your main panel.

Charles

Best deal going... Eaton/CH 200 amp main breaker panel with 42 spaces and includes branch breakers (starter pack) $149

Last edited by Charles (in GA); 09-24-2012 at 09:58 AM.
Charles (in GA) is online now   Reply With Quote
Sponsored Links (Register now to hide all advertisements)
Old 09-24-2012, 09:51 AM   #3
pattenp
Senior Member
 
pattenp's Avatar
 
Join Date: Jun 2008
Location: Virginia - USA
Posts: 5,696
Default Re: Cutler Hammer CH vs BR

The CH is just a better quality box and breaker than the BR. I have the CH in my home and added the CH in my attached garage because I moved some breakers from the main to the sub-panel in the garage, so that’s the reason I got a CH for the garage. I wouldn’t use the CH in your shop just because it’s what’s in the house if that’s the only reason. In my detached shop I used the Square-D Homeline because it was cheaper and more readily available.
pattenp is online now   Reply With Quote
Old 09-24-2012, 10:13 AM   #4
Gary S
Senior Member
 
Join Date: Dec 2008
Location: Bismarck, ND
Posts: 2,973
Default Re: Cutler Hammer CH vs BR

Charles explained it perfectly. Both are UL approved and both work, but the CH is the higher line.
I have a CH main panel in my house, and a BR subpanel. In my garage I have a BR subpanel. All I can say about all 3 boxes is that they have never given me any issues of any kind.

I've worked with a lot of different brands and models of electrical panels in my years on the jobs I worked. The only box I would never consider using is the Westinghouse panels they made around 1980. They were pure junk in my opinion. The breakers flopped around loosely in the box.
Gary S is offline   Reply With Quote
Old 09-24-2012, 11:51 AM   #5
mod600
Member
 
Join Date: Apr 2012
Posts: 64
Default Re: Cutler Hammer CH vs BR

Another thing I thought of...

Could I get a 200 amp panel and only run 100 amp service to it? I can get a 200 amp CH box with 30 spaces in it, just not a 100 amp one. I have a sub panel on the pole that used to feed an old shed via over head wires, a tree fell down and took the wires with it, the panel is there doing nothing and wire are no longer there, that shed will be coming down next summer…If I put in a 100 amp breaker in the box on the pole and feed the 200 amp panel in the shop, it’d still be protected at 100 amps right? Would that be another option?
mod600 is offline   Reply With Quote
Old 09-24-2012, 01:05 PM   #6
pattenp
Senior Member
 
pattenp's Avatar
 
Join Date: Jun 2008
Location: Virginia - USA
Posts: 5,696
Default Re: Cutler Hammer CH vs BR

Quote:
Originally Posted by mod600 View Post
Another thing I thought of...

Could I get a 200 amp panel and only run 100 amp service to it? I can get a 200 amp CH box with 30 spaces in it, just not a 100 amp one. I have a sub panel on the pole that used to feed an old shed via over head wires, a tree fell down and took the wires with it, the panel is there doing nothing and wire are no longer there, that shed will be coming down next summer…If I put in a 100 amp breaker in the box on the pole and feed the 200 amp panel in the shop, it’d still be protected at 100 amps right? Would that be another option?
That's correct. But be mindful of what amp feed is to that sub-panel on the pole.
pattenp is online now   Reply With Quote
Old 09-24-2012, 07:03 PM   #7
Norcal
Senior Member
 
Join Date: Mar 2008
Posts: 3,743
Default Re: Cutler Hammer CH vs BR

Eaton /Cutler-Hammer was advertising the BR line as "Engineered Value", translation: CHEAP. The BR line, SQ D homoline,& GE, are all bottom of the barrel makes but since Zinsco is gone, the trunk slammers have to have a choice of some crappy panels to use....
Norcal is offline   Reply With Quote
Old 09-24-2012, 07:57 PM   #8
Charles (in GA)
Senior Member
 
Charles (in GA)'s Avatar
 
Join Date: Jan 2006
Location: 50 mi south of Atlanta
Posts: 10,799
Default Re: Cutler Hammer CH vs BR

Quote:
Originally Posted by mod600 View Post
Another thing I thought of...

Could I get a 200 amp panel and only run 100 amp service to it? I can get a 200 amp CH box with 30 spaces in it, just not a 100 amp one. I have a sub panel on the pole that used to feed an old shed via over head wires, a tree fell down and took the wires with it, the panel is there doing nothing and wire are no longer there, that shed will be coming down next summer…If I put in a 100 amp breaker in the box on the pole and feed the 200 amp panel in the shop, it’d still be protected at 100 amps right? Would that be another option?
Quote:
Originally Posted by Charles (in GA) View Post
If you want more breaker spaces than the 100 amp CH panels provide, just go to a 150 or 200 amp CH panel with more breaker positions. It is not necessary to use a breaker panel rated the same as the feeder circuit is designed for, it can be a larger panel as long as the circuit is properly protected in your main panel.
As previously noted, yes.

Charles
Charles (in GA) is online now   Reply With Quote
Old 09-24-2012, 08:00 PM   #9
mrb
Senior Member
 
mrb's Avatar
 
Join Date: Dec 2008
Posts: 3,735
Default Re: Cutler Hammer CH vs BR

i just installed a BR panel. Its a piece of crap, but does the job and once installed its functioning perfectly. The construction is flimsy, both the sheet metal and the plastic. I do like being able to get the breakers for <4.00 a pole.....
mrb is offline   Reply With Quote
Old 09-24-2012, 09:32 PM   #10
wyliesdiesels
Senior Member
 
wyliesdiesels's Avatar
 
Join Date: Aug 2012
Location: Modesto, CA
Posts: 1,885
Default Re: Cutler Hammer CH vs BR

Quote:
Originally Posted by Gary S View Post
....I've worked with a lot of different brands and models of electrical panels in my years on the jobs I worked. The only box I would never consider using is the Westinghouse panels they made around 1980. They were pure junk in my opinion. The breakers flopped around loosely in the box.
Yeah, those Westinghouse panels were crap. And IMO, Zinscos are junk, too! And don't forget about the FPE panels that had the fraudulent UL stickers on them and caused many house fires!
wyliesdiesels is offline   Reply With Quote
Old 09-27-2012, 01:19 AM   #11
Shocker
Senior Member
 
Join Date: Nov 2008
Location: Olympia, WA
Posts: 1,289
Default Re: Cutler Hammer CH vs BR

I would go with the CH series panel. I am going to redo my home panels and will use the CH series panel. It is a bit more more money, but you get the copper backplane in it as well as a superior breaker.

The panel I am replacing is a CH panel from 1955. Still works just fine, but I just need to redistribute the loads to a more modern design.
Shocker is offline   Reply With Quote
Old 09-27-2012, 06:20 AM   #12
matt151617
Senior Member
 
Join Date: Dec 2011
Location: Plattsburgh, NY
Posts: 360
Default Re: Cutler Hammer CH vs BR

Same here, I put in a BR. At the time I didn't think there was a difference so I went with the cheaper option. Now, I probably would have gone with the CH. But, the BR works fine, breakers are very cheap and available anywhere. Anything beats the old FPE I had.
matt151617 is offline   Reply With Quote
Old 09-27-2012, 03:40 PM   #13
Speedy Petey
Senior Member
 
Join Date: Apr 2012
Location: NY State
Posts: 952
Default Re: Cutler Hammer CH vs BR

You guys calling BR junk and crap don't know what you're talking about.
BR series is FINE! The panels are not as finished as the painted CH boxes, but the quality is just as good as GE, HOM, Siemens, or any other 1" BR style breaker panel.
These are typically less expensive lines but they are far from junk.

Personally I like Siemens, but my main supply house does not carry them and I'm not driving across town to get them.
CH is great, but much more expensive by the time you fill up a panel.
QO has a nice fit and finish but the small, staggered neutral/ground bar layout is a JOKE.
Speedy Petey is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes