Go Back   The Garage Journal Board > The Tools > General Tool Discussion
Reply
Thread Tools Display Modes
Old 04-10-2008, 02:47 PM   #1
Greg9504
Default Wiring magnetic (definite purpose) starters for compressor?
Hi,
I picked up a used 7.5 hp compressor (Snap-On, however it's actually an Eagle 7180V2-MS painted red with Snap-on logo). However it did not have a magnetic starter included. I purchased a magnetic starter from Princess Auto (think Harbor Freight but Canadian), that their catalog recommends for a 7.5 hp compressor. It is a D Square 8911 DPSO43 (1 or 3 phase, 3 pole), with a 9998 DA1VO2 coil (120v), and a B 40 thermal unit (to install in the starter, may be referred to as a "heater"). I haven't been able to find much in the way of documentation beyond the general specifications. So from surfing the web I think I have it figured out, but I would like to go over the wiring as there are a few terminals which I am unsure of their function (OL and COM).
Here's an over all picture. The thermal unit can be seen on the left.
The wiring diagram included in the cover:
The coil terminals (for those reading this trying to figure out the inside of their starter, the coil here is the two spade terminals, one has a red wire connected to it in the picture below. When the coil is energized (by the pressure switch turning on), this moves the magnet, completing the circuit starting the motor... I think ).
Mine are labeled A1 and A2, A1 has the red wire on it which goes to a terminal at the bottom labeled OL.
The terminal with the red wire attached is labeled OL, the one below it is labeled COM. Not sure what part of the starter this is or what function it serves, anyone?
OK so here is what I think I need to do:
main power comes in and one side goes to L1, one to L2. The thermal unit is installed at T1 to connect T1 to the upper part of the switch, a jumper wire is installed at T2. T1 and T2 then go to the motor. Now for the pressure switch. Run a wire from L1 to the switch, then from the switch to A2 (the free terminal on the coil). Does this sound right?
Thanks
Greg.
Greg9504 is offline   Reply With Quote
Old 04-10-2008, 04:46 PM   #2
s_ontario
Senior Member
s_ontario's Avatar
Default Re: Wiring magnetic (definite purpose) starters for compressor?
This is what i found Not 100% sure its correct but I'll post the picture and perhaps someone else can confirm it for you
I call my dealer and he talked me out of getting a Mag starter said he had 3 units in my area none with a mag starter and he knows ones been out for 20 years and never had a starter
s_ontario is offline   Reply With Quote
Old 04-21-2008, 08:22 AM   #3
Greg9504
Quote:
Thanks for the schematic...
If I remember correctly from your post in the air compressor thread you own a 5 hp unit, he probably recommended that to you because your pressure switch is rated for the amps for your motor. The motor on mine is 35.5 amps (SF of 40 Amps). The pressure switch is only rated for 20 amps. So I could find a pressure switch rated for 40 amps or spend the same money on a mag starter and get the added bonus of overload protection for the electric motor.
Once I got a hold of some industrial circuit symbol definitions all fell into place.
There are basically 3 parts to the "magnetic starter". The coil/magnet (this is terminal A1 and A2), the contactor (L1 and L2), and the overload protection (OL and COM terminals).
The coil can be either 120V or 240V. If your starter has a 120V coil you'll need to use a 3 wire (plus ground) supply cable, since you'll need the neutral for 120V.
So then, how to wire it.
Supply.
Bring in the supply, L1 and L2 get power (black and red wire), neutral (white) goes to "COM" terminal at the bottom (overload relay). I had to use an insulated twist connector to connect a 14 gauge wire to the supply neutral wire, then to the COM terminal. Since my supply was 8 gauge and the COM terminal was too small. And of course bare wire to ground.
Pressure switch.
You'll need a 2 wire cable (plus ground) to go to the pressure switch. For the starter to operate, the coil needs 120V. So a wire is run from L1 (Use one of the spade connectors at L1) to the "LINE" terminal on the pressure switch, then from "MOTOR" terminal on the switch back to A2 (other side of the coil).
Overload.
A1 on the coil is wired from the factory to the OL (Over Load) terminal on the overload part of the starter. If the overload relay trips, the connection between A1 and neutral (COM terminal) is broken and the motor wont start.
Overload relays (referred to as "heaters"), If your starter uses these you'll need one for a single phase motor, the documentation for the starter will give you details on which one to get (mine required a B50). You'll also need some jumpers, hopefully your starter will come with the jumpers. Mine is a polyphase unit (it can be used for a single or three phase motor), and didn't come with any jumpers. I couldn't find any jumpers so that's why you see three relays in the attached picture. The starter WILL NOT WORK without the jumpers. If you don't have the jumpers in, the overload protection appears tripped, and therefore no current across the coil.
Motor.
T1 and T2 on the starter go to the motor.
If you have a 240V coil L2 will connect to "COM" of the overload protection circuit and you can run a 2 conductor (plus ground) from your panel instead of a 3 conductor since you wont need a neutral for a 120V circuit. Otherwise you connections should be the same.
jumpers
Old 11-18-2008, 04:37 PM   #4
BradIXXI
Junior Member
Great image. What would it look like for three phase?
I have a Square D (part# 8536scg3v02s) and the diagrams are useless to me on how, or more spacific, where to connect my preausure switch.
Any help would be great.
Kind Regards,
Brad
BradIXXI is offline   Reply With Quote
Old 11-18-2008, 05:31 PM   #5
Greg9504
According to the specs (see here) the coil (V02S) on the starter is 120V from a separate source. So you'll need to bring in the 3 phase power for the motor and a separate 120v single phase source to go between the coil and the pressure switch... at least that's my GUESS without seeing the wiring diagram included with the starter.
Get the part number off the coil and do a search on it.
Old 11-18-2008, 06:21 PM   #6
Charles (in GA)
Senior Member
Charles (in GA)'s Avatar
Look at this thread for a pic of my Square D starter on a 7.5 hp Husky/C-H compressor. There is another post, with a better description of the wiring inside of the starter, I'm still looking for it.
http://www.garagejournal.com/forum/showthread.php?t=456
EDIT: found it......
http://www.garagejournal.com/forum/s...gnetic+starter
See my post #8 in the above thread, for my description of the wiring in my Square D starter. It is the des of the wiring in the starter pictured in the top thread link, my post #6.
Charles
Charles (in GA) is offline   Reply With Quote
Old 11-29-2009, 01:05 PM   #7
larbow
Junior Member
larbow's Avatar
The wire that needs to go to COM should I run that back to my breaker box and give it it's own source. That seems to be my only loose wire that needs to be connected to something I think.
It's connected to the COM and connected to nothing on the other.
larbow is offline   Reply With Quote
Old 11-29-2009, 09:34 PM   #8
Greg9504
I can only guess because you haven't provided enough information.
So I'm assuming single phase. Did you run a 3 conductor (plus ground) from the panel to the starter? Or a 2 conductor (plus ground)? Is your coil 120v? if it is:
neutral = COM
In my picture the large white supply wire is connected to COM (Neutral on the panel).
I'm guessing again that you ran a 2 wire cable so you have no neutral. Could your run another wire from your neutral tap on the panel to the starter? Probably wouldn't pass inspection.
Old 11-29-2009, 10:10 PM   #9
Thedroid
Senior Member
Thedroid's Avatar
3 phase will have L1, L2, and L3 coming in the top, T1, T2, and T3 going out to the motor. You will then hook up an additional wire to L1 and L2 and connect them to a control transformer that matches the voltage on the starter coil. Everything else is hooked up the same, making sure that all of the power going through the control circuit is coming from the secondary of the control transformer. Always run the neutral through the O/L also.
The one thing I hate about the Square D relays, is that red wire hooked up to A1 from O/L. Should be a white wire hooked up to A2 IMO. Electrically it doesn't matter, but it should be white.
Thedroid is offline   Reply With Quote
Old 12-06-2009, 12:23 PM   #10
larbow
Junior Member
larbow's Avatar
Yes I'm using single phase. It has a 120v coil.
I've got my power wires connected to L1 and L2 and a ground.
I have a 14 gauge wire going from L1 to the line terminal on the pressure switch and a wire coming off the pressure switch to 3 terminal which then goes to the coil. coming out the other side of the coil is another wire that goes to the OL.
I ran a seperate wire from my breaker box to the COM.
But I'm not sure if I'm connected to the right place in my breaker box.
When I turn the power on it trips the breaker instantly.
Old 12-06-2009, 07:34 PM   #11
Thedroid
Senior Member
Thedroid's Avatar
Where is the wire from the panel to common hooked up to? It should be hooked up with all the other white wires, and definitely not hooked up to a breaker. You might want to call an electrician to give you a hand hooking that up. You don't want the risk of a fire or electrocution in the future.
Old 12-06-2009, 08:16 PM   #12
JohnFreeman
Senior Member
JohnFreeman's Avatar
I'm pretty sure you can find the instruction sheet for all Square D stuff on their website.
JohnFreeman is offline   Reply With Quote
Old 12-06-2009, 10:37 PM   #13
larbow
Junior Member
larbow's Avatar
I have the COM connected with all the wires that are either white or bare copper in the breaker box. I found this web sight.
http://ecatalog.squared.com/pubs/Mot...0140CT9201.pdf
And looked up the mag starter that I have and followed the wiring diagram and it said to run the COM to L2
. And that instantly tripped the breaker also. I should have known that was'nt going to work
Old 12-12-2009, 07:19 PM   #14
Thedroid
Senior Member
Thedroid's Avatar
L2 is for your motor, and without re reading the post I remember this being a 240V motor. If this is the case, then I'm not surprised that the breaker is tripping. COM should be hooked up to A2 for the coil, definitely not L2.
Old 12-12-2009, 07:22 PM   #15
Thedroid
Senior Member
Thedroid's Avatar
After you sort that out, if the breaker is still tripping you can disconnect the neutral, and check the rest of the circuit to ground using your multimeter set to read resistance. You should not read anything to ground.
Remember, you are dealing with 2 different circuits here. One is the power circuit for the motor, the other is your control circuit.
Old 02-11-2011, 09:45 PM   #16
JohnJL
Senior Member
Greg, did you get everything running? I'm in the same boat...need to wire up my 220V 1-phase motor with a mag starter and pressure switch...
Do you have a diagram? That would be awesome.
John
JohnJL is offline   Reply With Quote
Old 02-11-2011, 10:31 PM   #17
Greg9504
Yes it's been running fine. I don't have a wiring diagram. Look on the inside of your starter, that should get you started. Then you need to know if you have 120v coil or a 220v one. Hopefully with my description above and the pictures (the wires are labeled in the picture) you should be able to sort it out.
Old 02-14-2011, 07:17 PM   #18
JohnJL
Senior Member
I actually have the exact same starter as you and a similar motor and switch.
I couldnt ascertain from your pics/description...
1. Is the heater necessary and where did you install it in the SquareD starter? Mine had no documentation with it.
2. I only see 2 white wires pigtailed together, and your pic refers to "com" as one of those. I dont see a "com" terminal in the starter, is it one of the clear terminals or somehting else?
3. Where did you get those jumpers? Im also in Toronto.
4. How many wires did your motor have? Mine has 2 heavy wires labelled "1" and "4" and 2 ligher gauge wires labelled "5" and "8." The motor wiring diagram only indicates to wire 1 and 5 together and 4 and 8 together. I emailled tech assist from Baldor but they gave me a lame "we didnt make the compressor so we dont know the wiring requirements" response, even though my question was very specific to their motor...
Old 02-14-2011, 09:16 PM   #19
Greg9504
Hi John,
Slow down and re-read, all your questions were already answered above. Press Ctrl and + keys at the same time to increase the size of the images.
1) As I said the "heater" is a relay. It is 100% absolutely necessary. Without it (if you just jumped all 3 terminals) you would have no overload protection. There is only one place the heaters can go. They are installed in the picture that has the wires labeled. They are not installed in the first picture of the starter. They must be sized to the motor you are running, I believe on the inside of the cover there should be a chart with the sizes. I don't have a picture, but in the one I attached to this post the chart would be to the left. Use the wrong size and you could have a fire, or always be tripping the breaker.
2) Look closer, the com terminal is one of the clear plastic ones at the bottom of the starter. It is labeled.
3) as I said in my post, I couldn't find anyone stocking the jumpers here in Ottawa. So I just used heaters instead for the terminals that didn't require a relay. I got them at Princess Auto.
4) I can't tell you that. I can only offer a guess... you have two heavy gauge wires (plus ground) leaving the starter... that leaves you with only one place for them to go on the motor...
Ultimately if you don't feel comfortable wiring the starter, hire an electrician.
Old 02-15-2011, 08:56 AM   #20
JohnJL
Senior Member
Thanks Greg. Since I've never held a heater in my hand I didnt recognize their "backsides" in the labelled picture.
Also, though we have the same model number starter unit, my COM terminal was not labelled. Your pic clarified that.
Reply
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Forum Jump