You are currently viewing our boards as a guest which gives you limited access to view most discussions and access our other features. By joining our free community you will have access to post topics, communicate privately with other members (PM), respond to polls, upload content and access many other special features. Registration is fast, simple and absolutely free so please, join our community today!

If you have any problems with the registration process or your account login, please contact contact us.

Go Back   The Garage Journal Board > The Garage > Heating and A/C

Sponsored Links (Register now to hide all advertisements)

Reply
 
Thread Tools Search this Thread Display Modes
Old 01-13-2013, 09:10 PM   #1
stealman
Member
 
Join Date: Mar 2011
Posts: 87
Default radiant floor heat not supplying enough heat

I just finished up my hydronic system about a week ago and the system does not supply enough heat. I am hoping that someone may be able to offer some advice. In all fairness the insulation is not 100% yet and we are having really cold weather, but I thought the system would perform better.

I paid a professional to do a heat loss calc. and design the system and I assembled the system. I have 1400 sq. feet and 12' plate height and 17' to the ridge.
3" ridged foam under 4" concrete, the pex is stapled to the foam at 12" centers. 4" ridged on stem walls with a 45* at the top and 8 inches of stem wall uninsulated above that. R 42 s.i.p. walls. R 30 fiberglass batts in the ceiling, I will add another 3" of ridged foam to the bottom of the truss, but have not done it yet. The building has no sheet rock yet.
The heat system is a 100,000 btu high efficiency condensing water heater with a Taco x pump block to control the system.
I have the thermostat set at 55* and the system runs all night none stop and the temp only gets to 53* {I cant imagine how much propane that uses}. As soon as the sun comes up the temp come up to 55 or higher and the heater does not run all day until about sunset ant the the system run all night again.
Night time lows are -5 to -10 normal is more like 10 to 15 and the highs are like 10 and normal is like high 30's.
Does anyone have any ideas? Is this normal or how I can improve the performance? How much difference will the 3" ridged on the ceiling make? The inside temps don't bother me much, but I am worried about how much it will cost to run. I have done every thing I could think of to build a efficient building and I am a bit bummed at the moment.
Thanks for listening.
stealman is offline   Reply With Quote
Old 01-13-2013, 09:19 PM   #2
socapots
Senior Member
 
Join Date: Jan 2011
Posts: 460
Default

Most of the heat loss is always through the roof.
Everything I've always seen had lots in the roof. And not as much in the walls.
So maybe more R in the roof will help.
socapots is offline   Reply With Quote
Sponsored Links (Register now to hide all advertisements)
Old 01-13-2013, 09:24 PM   #3
Randy in Maine
Senior Member
 
Join Date: Nov 2010
Location: The Beach
Posts: 440
Default Re: radiant floor heat not supplying enough heat

How hot is the water going to and coming back from the floor?

When it is cold and windy outside and you don't have adequate insulation, it will require some BTUs to heat up the slab and to keep it at 55.
Randy in Maine is offline   Reply With Quote
Old 01-13-2013, 09:33 PM   #4
stealman
Member
 
Join Date: Mar 2011
Posts: 87
Default Re: radiant floor heat not supplying enough heat

I am really hoping that the extra r20 in the ceiling in the will make the difference.
The supply temps are 105* and the return is 82*.
stealman is offline   Reply With Quote
Old 01-13-2013, 10:50 PM   #5
Dick in Wisconsin
Senior Member
 
Dick in Wisconsin's Avatar
 
Join Date: Mar 2012
Location: Grafton, Wisconsin
Posts: 1,145
Default Re: radiant floor heat not supplying enough heat

Are those the temps in the morning after its been running all night long? What is the surface temp of the concrete floor? (shoot it with an infrared gun) Do you have spots that are much colder than other? is there a "dead zone" in the tubing that isn't getting the hot water?

How many square feet of floor space? How many loops? How long are the loops? Are there any valves on the manifold that might not be completely open?

Do you know the temp of the water coming off each zone? Maybe a zone or two isn't working.
__________________
20x22 attached garage (Sears opener w/40w lite, one 75w ceiling lite on pull chain, no heat no running water no TV no AC, one GFCI outlet on main bath circuit in a lousy location), added 8 outlet (4 in each location w/GFCI), 10x20 detached garage (one outlet in wrong location & 75w ceiling light on pull chain), looking to build bigger garage.
#90 Heilig-Meyers Ford Taurus-1996 Suburban 1500-24' enclosed trailer-lots of tools
Wears sound warnings like a badge of honor

Last edited by Dick in Wisconsin; 01-14-2013 at 08:28 AM. Reason: more clarity of questions
Dick in Wisconsin is offline   Reply With Quote
Old 01-13-2013, 11:00 PM   #6
anthony666
Senior Member
 
anthony666's Avatar
 
Join Date: Dec 2007
Location: kirkfield ontario
Posts: 706
Default Re: radiant floor heat not supplying enough heat

lets see a picture of you near boiler piping
anthony666 is offline   Reply With Quote
Old 01-13-2013, 11:16 PM   #7
stealman
Member
 
Join Date: Mar 2011
Posts: 87
Default Re: radiant floor heat not supplying enough heat

The temps I listed are the temps at the time I posted. I dont think they are much different in the a.m. The valves on the manifold are all the way open. I have flow guages on the manifold and they are all the way open. Although the max flow that they are showing is about 2.75 L.P.M. I have 5 loops and 1400 sq.' The surface temp on the floor at the present is 55*. I can take pictures in the morning and try and post them. I have not posted pictures before so I might have trouble with that one.
Thanks for the interest. This is my first experience with hydronics so I know little about it.

Last edited by stealman; 01-13-2013 at 11:19 PM.
stealman is offline   Reply With Quote
Old 01-14-2013, 06:50 AM   #8
KenB
Senior Member
 
Join Date: Dec 2008
Location: Pittsburgh, PA
Posts: 200
Default Re: radiant floor heat not supplying enough heat

There are a lot of variables, but I think you need a higher delta-t, the difference between supply and return temps. Increasing your supply temp to around 120 degrees should help a lot. After that, restricting flow to decrease return temp to about 75 will squeeze much better efficiency from the system.

Ken
__________________
You can argue all day with a six-point socket, but it will never work with anything but a hex fastener.
KenB is offline   Reply With Quote
Old 01-14-2013, 07:26 AM   #9
Sureshot
Alliance Member
 
Sureshot's Avatar
 
Join Date: Jan 2011
Location: In the shop in Saskatchewan
Posts: 2,827
Default Re: radiant floor heat not supplying enough heat

First thing I would try is slowing the water down to give it time to drop its energy.
Sureshot is offline   Reply With Quote
Old 01-14-2013, 08:55 AM   #10
wedge40
Senior Member
 
Join Date: Oct 2009
Location: Bloomington, IN
Posts: 318
Default Re: radiant floor heat not supplying enough heat

Which pump are you using?
wedge40 is online now   Reply With Quote
Old 01-14-2013, 09:08 AM   #11
stealman
Member
 
Join Date: Mar 2011
Posts: 87
Default Re: radiant floor heat not supplying enough heat

I am using a Taco x pump block. It is a heat exchanger pump and mixing valve in one. I am using the outdoor reset mode, which calculates supply temp based on outside air temp. It also has a delta t mode which I dont really understand. I am not sure if I can manually adjust the supply temp.
I have been speeding up the flow through the loops thinking that it might hepl. So you think I should slow it down? How much drop in temp between supply and return should I be looking for?
stealman is offline   Reply With Quote
Old 01-14-2013, 09:11 AM   #12
theoldwizard1
Senior Member
 
Join Date: Feb 2011
Location: SE MI
Posts: 10,418
Default Re: radiant floor heat not supplying enough heat

Quote:
Originally Posted by stealman View Post
3" ridged foam under 4" concrete, the pex is stapled to the foam at 12" centers. 4" ridged on stem walls with a 45* at the top and 8 inches of stem wall uninsulated above that.
...
Night time lows are -5 to -10 normal is more like 10 to 15 ...
Too late now, but I would have gone with at least 4" under the concrete.

What is the temperature of the uninsulated stem wall and how do you plan on insulating it ?
theoldwizard1 is offline   Reply With Quote
Old 01-14-2013, 09:11 AM   #13
Blk88GT
Senior Member
 
Join Date: Mar 2009
Location: Manitoba
Posts: 529
Send a message via MSN to Blk88GT
Default Re: radiant floor heat not supplying enough heat

Quote:
Originally Posted by Sureshot View Post
First thing I would try is slowing the water down to give it time to drop its energy.
Agreed.
Blk88GT is offline   Reply With Quote
Old 01-14-2013, 09:36 AM   #14
ReneJK
Member
 
Join Date: Jan 2013
Location: aalsmeer , netherlands
Posts: 33
Default Re: radiant floor heat not supplying enough heat

Quote:
Originally Posted by stealman View Post
How much drop in temp between supply and return should I be looking for?
Where we are (Europe) delta T we're looking for should be at least 20 degrees but preferably 30-35 degrees

slowing the water flow (letting the pump run slower) ensures that the water gets time to release its energy and get cooler

you also said that the system has only been running for a week ? , might take 'a bit' longer than that for the slab to heat up. Typically we're being advised to up temp by 5 degrees per week to prevent problems with the concrete
ReneJK is offline   Reply With Quote
Old 01-14-2013, 10:02 AM   #15
stealman
Member
 
Join Date: Mar 2011
Posts: 87
Default Re: radiant floor heat not supplying enough heat

Quote:
Originally Posted by theoldwizard1 View Post
Too late now, but I would have gone with at least 4" under the concrete.

What is the temperature of the uninsulated stem wall and how do you plan on insulating it ?
I'm sure the 8" of exposed stem wall is very cold. I am not sure how I should go about insulating it. Seems like 2" of ridged on the exterior would be good, but I haven't seen a good detail. How do you keep the ants from eating it. The easier method seems like 1" on the inside. Thoughts?
Thats funny you say to put 4" under the slab. Seems like everyone goes with 2". I do 3" and still not enough.

I slowed down the flow at the floor loops and will monitor to see if it helps.
The system has only been running one week. The slab temp comes up all night long until the system turns off when the sun comes up and then the floor cools off all day and the cycle starts again in the evening
stealman is offline   Reply With Quote
Old 01-14-2013, 10:27 AM   #16
Blk88GT
Senior Member
 
Join Date: Mar 2009
Location: Manitoba
Posts: 529
Send a message via MSN to Blk88GT
Default Re: radiant floor heat not supplying enough heat

Where is your thermostat? Do you have a slab sensor?
Blk88GT is offline   Reply With Quote
Old 01-14-2013, 11:16 AM   #17
stealman
Member
 
Join Date: Mar 2011
Posts: 87
Default Re: radiant floor heat not supplying enough heat

Quote:
Originally Posted by Blk88GT View Post
Where is your thermostat? Do you have a slab sensor?
I don't have a slab sensor, but I am open to installing one. What is the benefit of it.

I have tried the thermostat in different locations. The exterior north wall seemed too cold. Right next to the heating controls stayed too warm. Presently it is on a interior wall at the north end. I think this is the best so far.
stealman is offline   Reply With Quote
Old 01-14-2013, 12:37 PM   #18
jlckmj
Senior Member
 
jlckmj's Avatar
 
Join Date: Dec 2009
Location: SE Wiscosin
Posts: 556
Default Re: radiant floor heat not supplying enough heat

I have 2 inch foam board on the outside of my slab and the slab is 5 to 10 degrees colder at the outside perimeter than the rest of the slab.

It looks like you are fighting the cold without it, I would bet that your slab is colder much farther in. Like suggested above, pick up an infrared thermometer and check the temp of the whole slab.

For your other question;
On the outside of my slab, I used aluminum flashing over the insulation to protect it where it is exposed, I actually went over the insulation down to a couple of inches under the ground, bent it over the top of the foam (exposed 2 inches), then went in and up a few inches under the siding.

Jim
jlckmj is offline   Reply With Quote
Old 01-14-2013, 01:15 PM   #19
custom1
Senior Member
 
custom1's Avatar
 
Join Date: Jan 2008
Location: Pa
Posts: 282
Default Re: radiant floor heat not supplying enough heat

I never hooked my floor up yet and I'm not a heating guy. These are just some questions that came to mind.

What is your heating source? Edit...Never mind this one. I must have missed that the first time through.

How does the outside reset thing work?

What is the outside temp during the day when it shuts down? Does it stay off all day?
I guess there is an outside sensor, if so where is it located? In the sun?

Where are you located?

I looked up that Taco pump.

Why the need for the heat exchanger as part of the pump? Why not just a pump. Are you running antifreeze in the floor and water in the heater or is there some other reason?

When you read the supply and return temp, is that on the heater or floor side of the exchanger?

If it is shutting down all day it probably never got up to operating temp yet. You might have to do away with the outside reset thing. It sounds like it is starting up for the first time everyday.

Just a guess. If you run it on the delta-T setting it probably adjusts it own speed to get that temp difference.

A couple of pics would probably help spot a problem.

Also I think you are loosing a lot of heat to the outside if your floor is not separated from the outside wall on the inside of the wall.

Last edited by custom1; 01-14-2013 at 01:56 PM.
custom1 is offline   Reply With Quote
Old 01-14-2013, 01:41 PM   #20
Highbeam
Senior Member
 
Join Date: Feb 2011
Location: South Puget Sound
Posts: 1,701
Default Re: radiant floor heat not supplying enough heat

Your insulation and construction methods are not your problem. Sure, you might have an improvement or two you could make but you have another issue. You will discover that you are not wasting energy. It is not that your system can't keep up, it is that your system thinks it is keeping up.

You have a mod/con boiler that is designed to use less energy but burn longer. The most efficient way to run a boiler is all the time at low output and that's what it is doing.

You set the stat for 55 and you are getting 53. That's prety close, within the standard variance of a stat. Try bumping the stat up to 60 and see what you get, I'm guessing you'll get 57.

Last edited by Highbeam; 01-14-2013 at 01:43 PM.
Highbeam is offline   Reply With Quote
Old 01-14-2013, 02:26 PM   #21
stealman
Member
 
Join Date: Mar 2011
Posts: 87
Default Re: radiant floor heat not supplying enough heat

I don't have a boiler. It is a water heater 50 gal. 100,000 btu. The way I see it is it is like a on demand with 50 gal. of storage.

Let me try and explain the situation as I see it and hopefully I can find answers to solve the issue. It is 11* outside right now and sunny. Unusually cold. The air in the shop is 58* the floor temp is 53*. The heater has not run since around 8:00 a.m. It is comfortable in here. When the sun sets The temps. drop fast outside and it takes a little while to cool off in the shop. The heater kicks on and runs non stop until 8:00 a.m. Mean while the temperature inside drops slowly all night until the sunrise.

Remember the system has only been running for a week. I ran the heat nonstop for 2 days until the slab and air temp got to 58*. And then set the thermostat to 58*. Thats when this cycle started of heat off all day and on all night. And a cooling of the building all night.

It seems like the slab is not getting enough heat. Or loosing too much. A combination of the two most likely. Or I still have not brought the mass of the floor fully up to temp. I thought That when I got the floor to 58* and the air was the same that things had equalized and I was good to go.
stealman is offline   Reply With Quote
Old 01-14-2013, 02:52 PM   #22
Highbeam
Senior Member
 
Join Date: Feb 2011
Location: South Puget Sound
Posts: 1,701
Default Re: radiant floor heat not supplying enough heat

A 100,000 btu water heater is the same as a 100,000 btu boiler as far as I'm concerned. Both make 100,000 btu for your floor.

You have a wall stat and are comparing that setting to the floor temps? How are you measuring floor temp? Is your wall stat programmable or do you leave it on one setting?

The operation you describe is exactly how I would expect floor heat to run. There is a huge lag between the time when the thermostat calls for heat and when the stat is satisfied. The floor temp is likely overshooting in the morning, shutting off, and then must recover in the evening. You will get temp swings with such a large thermal mass.

This is not a hot air furnace. That funky outdoor reset, mixing valve, scenario might also be making things worse.
Highbeam is offline   Reply With Quote
Sponsored Links (Register now to hide all advertisements)
Old 01-14-2013, 02:56 PM   #23
ejk52d
Junior Member
 
Join Date: Jan 2013
Posts: 16
Default Re: radiant floor heat not supplying enough heat

What type of perimeter slab insulation do you have? what model water heater do you have? I have heated 10000 sq ft with 145,000 btu in N IL somethings not right.
If your picking up a large amount of passive solar during the day then your outdoor reset should be compensating for the gain. where do you have the outdoor sensor? It should be on the north outside surface isolated from the building. You may also need to tweek the settings on the reset.
As far as flow if anything your to low with that high of delta t across the circuit. Low flow loops in europe are in series a slab is parallel and should have around 15* delta t or temp drop.
What appears to be happening is that it runs all night and overshoots by morning and shuts down. the sun then warms it all day allowing the slab to cool down.

Last edited by ejk52d; 01-14-2013 at 03:07 PM.
ejk52d is offline   Reply With Quote
Old 01-14-2013, 05:18 PM   #24
hidollartoys
Senior Member
 
hidollartoys's Avatar
 
Join Date: Jul 2008
Location: K. C. Metro area
Posts: 588
Default Re: radiant floor heat not supplying enough heat

Install a slab thermo sensor. Let it overide the air stat on call for heat.
__________________
"If your friends dont race you need new friends", Mad Mike

My shop:
http://www.garagejournal.com/forum/s...d.php?t=159993
hidollartoys is offline   Reply With Quote
Old 01-14-2013, 06:00 PM   #25
stealman
Member
 
Join Date: Mar 2011
Posts: 87
Default Re: radiant floor heat not supplying enough heat

Thanks for all the ideas and thoughts. I am kind of getting confused. Some are saying speed up flow others are saying slow down.

I have a programmable thermo, but I have been over riding the program and just setting a temp. For measuring slab temp I just have a thermo laying on the floor out of the sun. The out door reset thing I don't really understand. The sensor for that is on the exterior North wall. My cystem has a delta t mode as well. Should I try that? How does that work?

I kind of like the idea of a floor sensor. Would I just use a temp prop. drilled into the conc. connected to the thermo?

I bumped up the temp on the therm to 60* a couple of hrs. ago. The floor temp cam up quick from 54 to 61 and the indoor air temp rose to 60* for a bit, but now the indoor temp is falling the pump is circulating, the heater is turning on and off and the temp in the building is falling. It is down to 58* and the floor is 61.5. It seems like a case of just not enough insulation? What do you think? The thing is, is that the building is insulated very well except for the ceiling. And it is r30 which is not bad. Maybe the 3" ridged on the ceiling will make all the difference?
stealman is offline   Reply With Quote
Old 01-14-2013, 06:35 PM   #26
Highbeam
Senior Member
 
Join Date: Feb 2011
Location: South Puget Sound
Posts: 1,701
Default Re: radiant floor heat not supplying enough heat

Your "problem" is that your measured temperatures are not exactly the same as your stat setpoints, right? They are within a couple of degrees though. I would not try too hard to fix this problem. Don't you think that this is just the flywheel effect of a huge thermal mass heater?
Highbeam is offline   Reply With Quote
Old 01-14-2013, 06:36 PM   #27
Highbeam
Senior Member
 
Join Date: Feb 2011
Location: South Puget Sound
Posts: 1,701
Default Re: radiant floor heat not supplying enough heat

Quote:
Originally Posted by Highbeam View Post
Try bumping the stat up to 60 and see what you get, I'm guessing you'll get 57.
Do I get a prize? Pick what temperature you want and adjust accordingly.
Highbeam is offline   Reply With Quote
Old 01-14-2013, 06:51 PM   #28
Dick in Wisconsin
Senior Member
 
Dick in Wisconsin's Avatar
 
Join Date: Mar 2012
Location: Grafton, Wisconsin
Posts: 1,145
Default Re: radiant floor heat not supplying enough heat

is the inside of the building comfortable?

"but now the indoor temp is falling the pump " What is the outside temp? That is really, really important every time you talk about how your system and building are behaving.

When you had the heat calcs done, how many BTUs was the breaken between outside air temp and 100,000BTU water heater you have?

For example, if the building will leak 105,000 BTU at 18*F and you have a 100,000BTU water heater, as the outside temp goes below 18*F the water heater will run full blast, the pump will continuously circulate water, and the temp inside will slowly fall. The BTUs escaping are greater than the BTUs being put into the building, plain and simple. This is the assumption at night with NO help from any solar gain.

The day time on a sunny day might be different (a little bit better) with some solar gain.

As you add insulation (reduce the BTU leaking out the building) and reduce air infiltration, the performance of your heating system will improve.

Keep us posted.
__________________
20x22 attached garage (Sears opener w/40w lite, one 75w ceiling lite on pull chain, no heat no running water no TV no AC, one GFCI outlet on main bath circuit in a lousy location), added 8 outlet (4 in each location w/GFCI), 10x20 detached garage (one outlet in wrong location & 75w ceiling light on pull chain), looking to build bigger garage.
#90 Heilig-Meyers Ford Taurus-1996 Suburban 1500-24' enclosed trailer-lots of tools
Wears sound warnings like a badge of honor

Last edited by Dick in Wisconsin; 01-14-2013 at 06:53 PM.
Dick in Wisconsin is offline   Reply With Quote
Old 01-14-2013, 06:55 PM   #29
stealman
Member
 
Join Date: Mar 2011
Posts: 87
Default Re: radiant floor heat not supplying enough heat

The problem is I have the thermostat set to 60 and the temp came to that for a little while, but now it is getting colder and the temp in the building continues to drop. Is that the way this radiant works. I thought radiant floors where the most comfortable and at night it gets cold in here and wont warm up. If I could turn the thermostat to 60 and get 58 that would be great, but the temp just drops as the night goes And the heat system runs full tilt.

The heat loss calcs. show 38,000 btu. required, but that is with the 3" ridged foam yet to be installed. I would think that my 100,000 btu. heater would still do it.

Last edited by stealman; 01-14-2013 at 07:12 PM. Reason: add
stealman is offline   Reply With Quote
Old 01-14-2013, 07:17 PM   #30
Dick in Wisconsin
Senior Member
 
Dick in Wisconsin's Avatar
 
Join Date: Mar 2012
Location: Grafton, Wisconsin
Posts: 1,145
Default Re: radiant floor heat not supplying enough heat

When the sun goes down, turn the termo stat to 70 and see what happens. (I expect the water heater will run continuously, the pump will run continuously, and the temp will go down.)

I think your building is leaking at night, with the current outside temperatures, more than 100,000BTUs (the output of the water heater) per hour.

Regardless of the type of heater you have, if the building is leaking MORE heat (measured by BTUs) than your heat source puts in ... then the temp in the building will drop. I don't think it gets any simpler than that.

I live in Grafton, WI; about 25 miles north of Milwaukee. When I build my 1,000sf race shop in the spring I'll put radiant in the slab with what I expect (and hope) is enough insulation under the slab, in the walls, around the stub wall, in the ceiling and try my best to seal the building up. I have an unused, existing (no cost to me) residential natural gas water heater that will heat the water for the radiant heat. I have resigned myself to the fact that because of the limits of the water heater I will having the following limitations:

1. Moving the temp from say 40 to 60 will take a while.
2. Once the temp gets in the teens (maybe single digits if I'm lucky), I won't be able to hold 60 or 55. As the O/S temp goes down below zero I will be stuck in the 40's and maybe high 30's.

I hope that helps you understand what is going on with your building.

You could get an infrared camera to show you where your heat is leaking out of the building. Or you could use an infrared temp gun (I use a Sears one with the race car and am happy with it) to shoot the surfaces ... floors all over (especially around the outside perimeter), outside on the walls, door, windows, stub wall, etc. which will help you further understand where you're leaking the heat. Even a remote thermometer in the attic above the insulation with the master readout in the shop and/or house will allow you to compare the outside air (with a sensor outside) and the attic. The warmer the attic of the shop is compared to the outside air temp ... the more heat you have leaking from shop to the attic; hence insulation will help.

Believe it or not, I've had friends who have spent money on insulating attics or this or that and have seen ONLY marginal improvement ... all because the existing insullation was adequate and anything beyond was "diminishing returns".

Keep posting. You're making me think about my upcoming build.
__________________
20x22 attached garage (Sears opener w/40w lite, one 75w ceiling lite on pull chain, no heat no running water no TV no AC, one GFCI outlet on main bath circuit in a lousy location), added 8 outlet (4 in each location w/GFCI), 10x20 detached garage (one outlet in wrong location & 75w ceiling light on pull chain), looking to build bigger garage.
#90 Heilig-Meyers Ford Taurus-1996 Suburban 1500-24' enclosed trailer-lots of tools
Wears sound warnings like a badge of honor

Last edited by Dick in Wisconsin; 01-14-2013 at 07:20 PM.
Dick in Wisconsin is offline   Reply With Quote
Old 01-14-2013, 07:31 PM   #31
HoosierBuddy
Senior Member
 
HoosierBuddy's Avatar
 
Join Date: May 2006
Location: Southern Indiana
Posts: 1,139
Default Re: radiant floor heat not supplying enough heat

I agree with Dick from WI.

Forget about the delta T, etc. Your water heater is running flat out with 100,000 BTU/hour input and can't keep up. That means you are losing more heat than that.

Solution?

First check for drafts. If you're leaking air that will kill you. Drafts are much worse than just "under insulated".

Second, insulate what needs insulated. Sounds like you know what needs done, you just haven't gotten to it yet?

Your water heater will be burning through a bit more than a gallon an hour if the burner is on all the time. Figure what? 12 gallons a day? Is that about $10 per day at current prices?

Fix any drafts. Insulate.

Phil
HoosierBuddy is offline   Reply With Quote
Old 01-14-2013, 07:45 PM   #32
Fastback
Senior Member
 
Fastback's Avatar
 
Join Date: Oct 2010
Location: Indy
Posts: 516
Default Re: radiant floor heat not supplying enough heat

My .02
Stop dicking with it until your inside insulation and wall board is up and sealed.

Also, I cant tell from your initial post but did you provide a thermal break between the slab and the foundation walls?

Also, we dont know what your system pressure is yet, or if you have the air out of the system and we dont know how you are taking heated fluid from the tank and returning it etc... Post a pic.
Fastback is offline   Reply With Quote
Old 01-14-2013, 08:35 PM   #33
Sureshot
Alliance Member
 
Sureshot's Avatar
 
Join Date: Jan 2011
Location: In the shop in Saskatchewan
Posts: 2,827
Default Re: radiant floor heat not supplying enough heat

A temp gun is a necessity not an option if you use infloor heat. My mixing valve takes its cue from the return line. I found it to be much better that way.

I don't know how you are getting an air temp that is higher than the slab. It should be a few degrees less in winter and especially if you are losing heat as other suspect.

You may also be worrying too much. Set the indoor temp and give it 24 hrs to acclimate.
Sureshot is offline   Reply With Quote
Old 01-14-2013, 09:04 PM   #34
stealman
Member
 
Join Date: Mar 2011
Posts: 87
Default Re: radiant floor heat not supplying enough heat



Lets see if this works. Here is a picture.
stealman is offline   Reply With Quote
Old 01-14-2013, 11:04 PM   #35
jlckmj
Senior Member
 
jlckmj's Avatar
 
Join Date: Dec 2009
Location: SE Wiscosin
Posts: 556
Default Re: radiant floor heat not supplying enough heat

Stealman,
I am definitely not an expert, It looks like you have plenty of insulation, (other than possibly your stem walls) R30 in the ceiling is about what I have, so that is probably not your problem.

If you are worried about the cost, turn it down to 55* and let it be. In fact, I would be turning it down until I found a temp that it maintained with the heater running fairly equally both day and night, then work out the bugs. Like others have mentioned, it may very well be working the way it should be, but modulated down so it is not running full bore.

What are you going to do in the garage? I have mine set at 55* and I was in there working today with only a flannel shirt on and I was sweating. You normally do not need it as warm as a garage with forced air.

You seem to have tried everything other than the Delta T setting instead of the outdoor reset. I would read up on how that works with your system and try to get that working instead of the outdoor reset and see what happens.

Buy an infrared thermometer ($30) so you can check the floor for cold spots, and around doors and windows for air infiltration. In my garage, if the floor temp is 55*, then the air temp is about the same or a few degrees lower, and the inside of the walls and the underside of the ceiling is the same as the air temp, Everything is very close in temperature throughout the garage.

Jim
jlckmj is offline   Reply With Quote
Old 01-14-2013, 11:42 PM   #36
Shop Specialties
Senior Member
 
Join Date: Mar 2012
Location: Grass Range, MT
Posts: 204
Default Re: radiant floor heat not supplying enough heat

Are you sure you got all the air out ?
Shop Specialties is offline   Reply With Quote
Old 01-15-2013, 03:05 AM   #37
theoldwizard1
Senior Member
 
Join Date: Feb 2011
Location: SE MI
Posts: 10,418
Default Re: radiant floor heat not supplying enough heat

Quote:
Originally Posted by stealman View Post
Thanks for all the ideas and thoughts. I am kind of getting confused. Some are saying speed up flow others are saying slow down.
The only way you will really know which is correct is to install a thermometer at the outlet of the water heater and at the return from the floor.

Quote:
I bumped up the temp on the therm to 60* a couple of hrs. ago. The floor temp cam up quick from 54 to 61 and the indoor air temp rose to 60* for a bit, but now the indoor temp is falling the pump is circulating, the heater is turning on and off and the temp in the building is falling.
So why is the burner turning on and off while the pump is still running ?

This is why you are cold !

I am no expert, but there could be an overtemp in the water heater burner shutting it down. (I actually have that problem with my horizontal flow forced air furnace when it is extremely cold out; The burner can not run more than 10 minutes without tripping the overheat sensor)
theoldwizard1 is offline   Reply With Quote
Old 01-15-2013, 03:07 AM   #38
theoldwizard1
Senior Member
 
Join Date: Feb 2011
Location: SE MI
Posts: 10,418
Default Re: radiant floor heat not supplying enough heat

Quote:
Originally Posted by HoosierBuddy View Post
Forget about the delta T, etc. Your water heater is running flat out with 100,000 BTU/hour input and can't keep up.
It can't keep up because the OP stated that the burner was cycling. Got to figure that out first !
theoldwizard1 is offline   Reply With Quote
Old 01-15-2013, 04:24 AM   #39
bams50
Senior Member
 
bams50's Avatar
 
Join Date: Feb 2012
Location: Central NY State
Posts: 1,422
Default Re: radiant floor heat not supplying enough heat

No idea what the problem is, but I want to learn before I build mine. Keep at it, and keep us posted with what you do and the ultimate solution. I am subscribed!
bams50 is offline   Reply With Quote
Old 01-15-2013, 06:25 AM   #40
philjafo
Senior Member
 
Join Date: Aug 2012
Posts: 244
Default Re: radiant floor heat not supplying enough heat

Can't tell from the pics what direction is the water flowing in the system, supply coming from the hot side and return going into the cold side of the tank? Tank type heaters don't work very well if you try to run them backwards.
philjafo is offline   Reply With Quote
Old 01-15-2013, 07:15 AM   #41
Rhsty
Junior Member
 
Join Date: Jul 2012
Posts: 20
Default Re: radiant floor heat not supplying enough heat

Your never going to get the building temp up with a 60 some degree slab surface
Temperature. My garage is 900 sqft and the thermostat stays at 65 degrees the
Floor surface is usually around 78 degrees. There is 11 foot ceilings, 2 inch rigid
Blue styrofoam under slab,R21 walls,R30 ceiling heat loss was just under 20,000
Btuh I have a 80000 btu boiler which also heats the 1500 sqft house as well with
No problems with a -5 outdoor design temperature. The boiler size is not the problem you can only put so much btu's
Through your tubing at any givin temperature, with the newer systems the flame
Modulates as the delta t gets smaller, that being said you probably have to raise
Your water supply temp going into floor a little.
Rhsty is offline   Reply With Quote
Old 01-15-2013, 09:11 AM   #42
tdkkart
Senior Member
 
tdkkart's Avatar
 
Join Date: Jun 2006
Location: Eastern Iowa
Posts: 4,783
Default Re: radiant floor heat not supplying enough heat

Quote:
Originally Posted by Rhsty View Post
Your never going to get the building temp up with a 60 some degree slab surface Temperature. My garage is 900 sqft and the thermostat stays at 65 degrees the Floor surface is usually around 78 degrees.

If you need 78* slab temp in order to maintain 60* room air you've got a BIG leak somewhere.

1200sq/ft, 11.5ft ceiling, R23-ish walls, 2" underslab and perimeter, R40ish ceiling. My slab temp runs 3-5* above ambient depending on the outside temp, NEVER has it been anywhere close to 13 degrees above ambient.

The OP has an issue, but it's gonna be really hard to diagnose over this forum. I suspect the fancy water heater may be a modulating type?? If that's the case, it could be making 10,000btu or 100,000btu while it's burning, with no real way to tell the difference.
What does bother me is the wide swings he's seeing between turn off and turn on, something's not right there. You want the slab temp to be kept in a tight window or it will cost you a fortune to keep up with the swings.
__________________
"Why should I pay someone to screw up my stuff when I can do it myself for free.........."

Disclaimer: What I say is based on my knowledge and experience only. It's entirely possible I'm full of shit. You've been warned!!
tdkkart is offline   Reply With Quote
Sponsored Links (Register now to hide all advertisements)
Old 01-15-2013, 09:45 AM   #43
stealman
Member
 
Join Date: Mar 2011
Posts: 87
Default Re: radiant floor heat not supplying enough heat

How do I know if the air is out of the system? I purged it until I didn't hear any air coming from the air separator and no more air bubbles can be seen in the flow gauges at the manifold. The system pressure is at 15 psi. Is that good? I couldn't find any info on what the system pressure should be.

The x block pump calculates supply temperature based on outside temp. It is usually only supplying 96* water. which is what it is targeting. I don't know how to change that or if it is possible.

The large slab temp. swings are from solar gain during the day. The air inside warms from the sun and satisfies the thermo. Therefor the slab cools. Then the outside temp drops rapidly and the slab has to catch up, which it cant seem to do. I am not sure if my system is running correct or not and I don't know how to figure it out. I am thinking that a floor sensing thermo would be the way to go. Set the floor temp to a nice medium. The building would get a little warm during the day and cool at night. I have a wood burning stove so I can compensate for the night temps and the heating system can equalize.
stealman is offline   Reply With Quote
Old 01-15-2013, 10:55 AM   #44
philjafo
Senior Member
 
Join Date: Aug 2012
Posts: 244
Default Re: radiant floor heat not supplying enough heat

I would recommend having the guy who designed it for you come out to take a look at it, you should be able to change the target temp for the water. I would turn it up to 120 but it also sounds like your losing way to much heat at night.
philjafo is offline   Reply With Quote
Old 01-15-2013, 11:20 AM   #45
Fastback
Senior Member
 
Fastback's Avatar
 
Join Date: Oct 2010
Location: Indy
Posts: 516
Default Re: radiant floor heat not supplying enough heat

Quote:
Originally Posted by stealman View Post
4" ridged on stem walls with a 45* at the top and 8 inches of stem wall uninsulated above that. R 42 s.i.p. walls. R 30 fiberglass batts in the ceiling, I will add another 3" of ridged foam to the bottom of the truss, but have not done it yet. The building has no sheet rock yet.

So, you have an open ceiling and open walls??? If that's the case then you really dont have any insulation value yet if the insulation is exposed.

It's the air space that gives R value, if you dont trap that air space you really dont have the space finished yet.

Ill say it again, finish the ceiling and walls and stop messing with the heat system. I would turn it off.
Fastback is offline   Reply With Quote
Old 01-15-2013, 11:29 AM   #46
anthony666
Senior Member
 
anthony666's Avatar
 
Join Date: Dec 2007
Location: kirkfield ontario
Posts: 706
Default Re: radiant floor heat not supplying enough heat

Quote:
Originally Posted by stealman View Post


Lets see if this works. Here is a picture.
that mixing block is the problem sir .. you just need to set it up right for your application .. contact taco http://www.taco-hvac.com/ .. they'll walk you through it

one other thing, a bit nit picky sorry, those relief valves should not be piped together .. you can't tell which one is venting if it goes off, it's against code up here, probably where you are too
anthony666 is offline   Reply With Quote
Old 01-15-2013, 12:29 PM   #47
tdkkart
Senior Member
 
tdkkart's Avatar
 
Join Date: Jun 2006
Location: Eastern Iowa
Posts: 4,783
Default Re: radiant floor heat not supplying enough heat

Quote:
Originally Posted by stealman View Post
The large slab temp. swings are from solar gain during the day. The air inside warms from the sun and satisfies the thermo. Therefor the slab cools. Then the outside temp drops rapidly and the slab has to catch up, which it cant seem to do. I am not sure if my system is running correct or not and I don't know how to figure it out. I am thinking that a floor sensing thermo would be the way to go. Set the floor temp to a nice medium. The building would get a little warm during the day and cool at night.

I think this is a big part of the issue, and I see some of the same thing in my shop, especially if i spend extended periods of time in the building. My building is insulated well enough that I actually see the temp come up a couple degrees if I'm working in there, especially in the smaller of the 2 rooms. I've only got one window, which is on the north side so I get very little solar gain, but simply working in the shop will raise the temp, and the heat seldom runs while I'm working.
I think the floor sensor idea is indeed valid, and worth looking into.

And yes, if you don't have the walls/ceiling finished the insulation will not be working to it's full ability.
__________________
"Why should I pay someone to screw up my stuff when I can do it myself for free.........."

Disclaimer: What I say is based on my knowledge and experience only. It's entirely possible I'm full of shit. You've been warned!!
tdkkart is offline   Reply With Quote
Old 01-15-2013, 07:29 PM   #48
stealman
Member
 
Join Date: Mar 2011
Posts: 87
Default Re: radiant floor heat not supplying enough heat

"that mixing block is the problem sir .. you just need to set it up right for your application"
Can you elaborate on this? Are you familiar with the x block. I will call them, but I would like to hear your thoughts.

As far as the insulation goes. Yes the building is not finished yet. I can see your point about the ceiling and the air space and I think the 3" ridged that I am going to put on the ceiling will take care of that. But the wall are ridged foam. Do you think that the drywall will make much difference?

I took the thermostat off the wall and laid it on the floor with ridged foam over the top of it to mimic a floor sensor.
stealman is offline   Reply With Quote
Old 01-15-2013, 08:17 PM   #49
philjafo
Senior Member
 
Join Date: Aug 2012
Posts: 244
Default Re: radiant floor heat not supplying enough heat

Quote:
Originally Posted by stealman View Post
"that mixing block is the problem sir .. you just need to set it up right for your application"
Can you elaborate on this? Are you familiar with the x block. I will call them, but I would like to hear your thoughts.

As far as the insulation goes. Yes the building is not finished yet. I can see your point about the ceiling and the air space and I think the 3" ridged that I am going to put on the ceiling will take care of that. But the wall are ridged foam. Do you think that the drywall will make much difference?

I took the thermostat off the wall and laid it on the floor with ridged foam over the top of it to mimic a floor sensor.
It may be possibe the taco x block is not set correctly and the outdoor temp sensor is having an effect on the temp of the water, it changes the temp of the water based on outdoor temps. I know you said its on the north wall where it should be but could something be affecting the reading its giving. I'm not very familier with the x block but it operates similar to other systems I am familiar with. Get the book out for it and go through the setup instructions, maybe read it twice and if theres anything your not completely clear on just ask here.
philjafo is offline   Reply With Quote
Old 01-15-2013, 09:12 PM   #50
stealman
Member
 
Join Date: Mar 2011
Posts: 87
Default Re: radiant floor heat not supplying enough heat

I read the x block instructions and I cant see what could be wrong with the set up. Basically you just set parameters. The weird thing is as I lower the outside design temp the target temperature of the x block goes down. I would think it should be the opposite. I am going to study the delta t mode and try that.

I picked up a inferred temp gauge today. The gauges on the manifold read about 20* different from supply and return, but when I put the in fared on the individual floor loops I get 10* difference and one loop is at 5*
stealman is offline   Reply With Quote
Old 01-15-2013, 10:34 PM   #51
tdkkart
Senior Member
 
tdkkart's Avatar
 
Join Date: Jun 2006
Location: Eastern Iowa
Posts: 4,783
Default Re: radiant floor heat not supplying enough heat

Quote:
Originally Posted by stealman View Post
I picked up a inferred temp gauge today. The gauges on the manifold read about 20* different from supply and return, but when I put the in fared on the individual floor loops I get 10* difference and one loop is at 5*

Ok, so slow down the loops with the smallest drop till they equal the one with the largest drop. Start closing the valve on that loop while monitoring the return temp, you should see a change pretty quickly.

Be a careful with the temp gun, when checking the temp of a tube, the gun's "eye" may not be looking where you think it is. Sweep back and forth across each the tube till you get the highest temp.

What's your floor temp running compared to the room temp?? I'll bet the floor is colder in the area of that 5* loop.
__________________
"Why should I pay someone to screw up my stuff when I can do it myself for free.........."

Disclaimer: What I say is based on my knowledge and experience only. It's entirely possible I'm full of shit. You've been warned!!
tdkkart is offline   Reply With Quote
Old 01-15-2013, 11:20 PM   #52
anthony666
Senior Member
 
anthony666's Avatar
 
Join Date: Dec 2007
Location: kirkfield ontario
Posts: 706
Default Re: radiant floor heat not supplying enough heat

yea, it's like an injection mixing system/pumps/control unit all in one .. basically it sets your delivery temp and temp ramp up by mixing in some of the return water, it handles the pumping duties & turns on your boiler etc etc

i'm personally not a big fan of these things, i can buy a lot of parts for what they are selling for, i think my cost is about a grand, retail 16 hundredish .. and if they go south you're replacing another thousand dollar part, home owners are never happy about that kind of eventuality .. i'd use it maybe for a very small snowmelt application because you can adjust it to bring the slab temp up very slowly and not crack the hell out of the concrete, but the connections are only 3/4" so you don't get the volume of water for a driveway job

i see them for sale used all the time, because they're a pain to get the controller set up right

so, what sensors did you install and where did you put them ???

for your application i'd program it in 'setpoint' mode .. if you have the outdoor reset & warm weather shut off enabled i guess you're not in setpoint, yea ??? it's been a year or more since i did the training on these units though so i might be wrong

taco has the install files online in .pdf format .. or just call taco, they'll walk you through it .. then go see your supplier and kick him in the junk for selling you on it
anthony666 is offline   Reply With Quote
Old 01-16-2013, 12:15 AM   #53
philjafo
Senior Member
 
Join Date: Aug 2012
Posts: 244
Default Re: radiant floor heat not supplying enough heat

then go see your supplier and kick him in the junk for selling you on it

I knew there was a good reason I'm not very familiar with these taco x blocks
philjafo is offline   Reply With Quote
Old 01-16-2013, 11:31 AM   #54
custom1
Senior Member
 
custom1's Avatar
 
Join Date: Jan 2008
Location: Pa
Posts: 282
Default Re: radiant floor heat not supplying enough heat

Here is a link to the instructions for the X-block.
Seems way more complicated than it needs to be.

http://www.taco-hvac.com/uploads/Fil...ry/102-202.pdf

I think we would need more detailed pics to determine if everything is connected correctly. For example, where are your supply and return sensors attached? On the diagram in the instruction for outside reset mode it only has one return sensor on the primary loop, but when using set point with delta-T there is second return sensor on the secondary loop.

Also where is the Variable Speed Mixing Valve? The diagrams make it look like it is separate from the x-block, or is it internal? I don't see it in your pic.

Do you have a pic showing the manifolds?

Does the x-block actually control the burner or does the burner just maintain a set temp and the x-block mixes return water on the primary side to set the input temp?

When you say it runs full tilt all night, what part is running? The burner or the circulating pumps or all of it? At one point you said the burner kicks on and off. I think you need to know how long the burner is on and how much fuel it is using before passing judgement on if it is working correctly.

My brain hurts.
custom1 is offline   Reply With Quote
Old 01-16-2013, 01:06 PM   #55
jvitez
Senior Member
 
jvitez's Avatar
 
Join Date: Nov 2009
Location: Big Sky Country, Canada
Posts: 1,977
Default Re: radiant floor heat not supplying enough heat

[[[[[[[[]]]]]]]
Attached Images
File Type: jpg My Brain Hurts!.jpg (25.3 KB, 9 views)
__________________
After the reading of the rich man's last will and testament, the family was asked "How much did he leave?"

The answer: "All of it."
jvitez is offline   Reply With Quote
Old 01-16-2013, 04:54 PM   #56
brian thomas
Junior Member
 
Join Date: Apr 2007
Posts: 8
Default Re: radiant floor heat not supplying enough heat

What is the ceiling covered with? You said R30 and no drywall yet if I read correctly. Are you losing heat by not being sealed up?
brian thomas is offline   Reply With Quote
Old 01-16-2013, 11:40 PM   #57
stealman
Member
 
Join Date: Mar 2011
Posts: 87
Default Re: radiant floor heat not supplying enough heat

I think I am making progress. The super cold weather has passed and now we have cold weather. I think the floor has come up to temp. I have the thermo. on the floor to mimic a floor sensor. The floor stayed 60* all day long without the pump or heater turning on. The room was very comfortable. Tonight the pump and heater have only been running periodically.

While running in outdoor reset mode There are two sensors required One outside and one on the supply line. The mixing valve is part of the x block. You cant see it. The x block does not control the burner although It looks like it can. In my case the burner just runs until it comes up to temp. When i said the system runs full tilt. What I meant was the pump runs constantly and the heater fires until it comes up to full temp, then turns off for maybe 15-20 min. and then turns on again. I called Taco today and the tech said he thought outdoor reset mode would be more efficient. He said If I want hotter supply temps I should raise the design temp not lower it.

Thanks to everyone for posting there thoughts. I will continue to update.

Last edited by stealman; 01-16-2013 at 11:48 PM. Reason: add info
stealman is offline   Reply With Quote
Old 01-17-2013, 03:51 AM   #58
theoldwizard1
Senior Member
 
Join Date: Feb 2011
Location: SE MI
Posts: 10,418
Default Re: radiant floor heat not supplying enough heat

Quote:
Originally Posted by custom1 View Post
Here is a link to the instructions for the X-block.
Seems way more complicated than it needs to be.

http://www.taco-hvac.com/uploads/Fil...ry/102-202.pdf
From the above document.

Your picture does not clearly show the Supply and Return sensors.
Attached Images
File Type: jpg Capture.JPG (30.3 KB, 34 views)
theoldwizard1 is offline   Reply With Quote
Old 01-17-2013, 03:58 AM   #59
theoldwizard1
Senior Member
 
Join Date: Feb 2011
Location: SE MI
Posts: 10,418
Default Re: radiant floor heat not supplying enough heat

Quote:
Originally Posted by theoldwizard1 View Post
So why is the burner turning on and off while the pump is still running ?
You still have to answer this question !
theoldwizard1 is offline   Reply With Quote
Old 01-17-2013, 07:56 AM   #60
HoosierBuddy
Senior Member
 
HoosierBuddy's Avatar
 
Join Date: May 2006
Location: Southern Indiana
Posts: 1,139
Default Re: radiant floor heat not supplying enough heat

Quote:
Originally Posted by theoldwizard1 View Post
You still have to answer this question !
If it is a modulating burner, then the OP's statement that the water heater is running all the time DOES NOT mean it's running flat out at 100,000 BTU all the time...as another poster noted.

My infloor heat (modulating tankless boiler) often has the pumps running and the burner off. It happens when the system water temperature is up, but at least 1 t-stat is still generating a heat call. In the OP's case, he has a lot of water in that tank and once it gets up to temp, the pumps may be able to run for some minutes before the tank temperature will drop down and call for the burner to kick on.

If it is a modulating water heater, then it kicks on at a preset BTU input and throttles up or down based on the CPU's determination. The outdoor reset and any delta T feed into what it wants to do.

Now...my setup is completely different than the OP's, but I will say that my outdoor reset caused me nothing put trouble and I eventually disconnected it and just manually programmed my required water temperatures. Not recommended really as this decreases the system efficiency, but it did work for me.

As far as air in the lines...getting air out of the lines in the slab is no harder than what the OP posted. The only problem I've ever had with air in my lines is air in lines that are above the boiler (lines in the floor of the garage's second story). To bleed those lines took more effort.

Phil
HoosierBuddy is offline   Reply With Quote
Old 01-17-2013, 05:15 PM   #61
theoldwizard1
Senior Member
 
Join Date: Feb 2011
Location: SE MI
Posts: 10,418
Default Re: radiant floor heat not supplying enough heat

Quote:
Originally Posted by HoosierBuddy View Post
My infloor heat (modulating tankless boiler) often has the pumps running and the burner off. It happens when the system water temperature is up, but at least 1 t-stat is still generating a heat call. In the OP's case, he has a lot of water in that tank and once it gets up to temp, the pumps may be able to run for some minutes before the tank temperature will drop down and call for the burner to kick on.
Perfectly logical. However your floor and return temps are "adequate" !

Quote:
If it is a modulating water heater, then it kicks on at a preset BTU input and throttles up or down based on the CPU's determination. The outdoor reset and any delta T feed into what it wants to do.
From reading the Taco XPB documentation, the water heater burner control, be it electronic or "mechanical", is independent.
theoldwizard1 is offline   Reply With Quote
Old 01-17-2013, 06:47 PM   #62
anthony666
Senior Member
 
anthony666's Avatar
 
Join Date: Dec 2007
Location: kirkfield ontario
Posts: 706
Default Re: radiant floor heat not supplying enough heat

Stealman, sorry dude, I thought I remembered there being a dry contact to trigger the boiler on those things, like I said its been ages since I did that training

Glad you got it sorted
anthony666 is offline   Reply With Quote
Sponsored Links (Register now to hide all advertisements)
Old 01-17-2013, 09:30 PM   #63
zmaxmotorsports
Senior Member
 
zmaxmotorsports's Avatar
 
Join Date: Jan 2013
Location: South of omaha
Posts: 558
Default Re: radiant floor heat not supplying enough heat

More heat.
Restrict the returns a little with the ball valves to give it time to work,just watch the temps in the heater/boiler so it doesn't start kicking out on limit switches if it has any.
Insulate every inch of garage,heat does no good if you cant contain it
zmaxmotorsports is offline   Reply With Quote
Old 01-17-2013, 09:34 PM   #64
AmickRacing
Senior Member
 
Join Date: Apr 2006
Location: Rapid City, SD
Posts: 131
Default Re: radiant floor heat not supplying enough heat

Quote:
Originally Posted by the duude before him
So why is the burner turning on and off while the pump is still running ?
Quote:
Originally Posted by theoldwizard1 View Post
You still have to answer this question !

I wouldn't be the least bit alarmed by the pump running all the time. Generally once the temp gets cold enough you want heat, the pump should be running until the outside temp rises enough you don't want heat.

With the pump running, you'll maintain a more even temp all over. If it shut off, you'd slug the boiler (or water heater) with a lot of cool water, and it'd take a while to get caught back up, once the temp fell enough to kick the pump on and boiler on. Then it'd stop... and repeat. Not really the end of the world because a bit of a temp swing in a garage usually isn't the end of the world.
AmickRacing is offline   Reply With Quote
Old 02-06-2013, 07:42 PM   #65
Dick in Wisconsin
Senior Member
 
Dick in Wisconsin's Avatar
 
Join Date: Mar 2012
Location: Grafton, Wisconsin
Posts: 1,145
Default Re: radiant floor heat not supplying enough heat

Mr. Stealman ... did you get it running right? What did you end up doing?
Dick in Wisconsin is offline   Reply With Quote
Old 02-06-2013, 08:54 PM   #66
stealman
Member
 
Join Date: Mar 2011
Posts: 87
Default Re: radiant floor heat not supplying enough heat

I think the system is working fine. I haven't done anything to the hydronic system. the slab temp has equalized. The weather is much warmer. The lows have been in the high teens and low 20's and the highs have been mid to upper 30's. I got the ridged insulation installed in the ceiling and I will start on sheet rock next week.
I have the thermostat set to 56* and it is resting on the floor. Basically mimicking a floor sensor. I want to buy a thermo with a slab sensor. Does anyone have any suggestions?
The building has been comfortable and the hydronic system has only been running late at night and in the early morning. I am not sure about how much propane I have used in the month since the system has been on.
stealman is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Sponsored Links (Register now to hide all advertisements)


All times are GMT -5. The time now is 09:33 AM.