I am building a garage and since it is less than five feet from my property line, I am required to have a one hour fire rating for applicable walls. I was told by my local planning office that even if I built it with brick walls that I would still need to have 1/2" Gypsum board on the exterior and 1/2" Gypsum board on the interior. The brick has the required one hour fire rating by itself so I am not sure why I still need to have the gypsum board. Anyone have any info on this or experience with it? My county uses the 2012 international building code.
clemsonee is offline   Reply With Quote
Old 12-19-2013, 12:18 PM   #2
Higgins
Senior Member
Higgins's Avatar
Default Re: One hour fire rating
It's the ole saying, if the local code requires it, your going to have to do it!
It may be worth while to stop by their office and go over their requirements.....
Higgins is offline   Reply With Quote
Old 12-19-2013, 12:25 PM   #3
Zeke
Senior Member
Zeke's Avatar
Location: Senior Member—in more ways than one in Long Beach CA
Damn. You could put 5/8ths rock on both sides plus the brick and probably call it a 4 hour wall. But he's right, you do what they tell you. 1/2 drywall is cheap and you only have to fire tape the outside which means you don't even have to spot fill the attachments.
__________________
Quote:
Originally Posted by 383 240z View Post
And just what in the heck were you searching for to find that? Keith
Quote:
Originally Posted by happymachinist View Post
This can't be a real question
Zeke is offline   Reply With Quote
Old 12-19-2013, 12:25 PM   #4
readhead
Senior Member
I would suggest that you go to the office and go over the one hour assembley options with the code official. There may be some options. Don't get sideways with building department. They will usually treat you well if you work with them. The '12 code is pretty restrictive in some areas and you may have found one of those areas.
I know that here brick has never met the 1hr. requirement. We usually install 5/8 X-board behind the brick.
readhead is offline   Reply With Quote
Old 12-19-2013, 12:29 PM   #5
Thumper68
Senior Member
Thumper68's Avatar
Quote:
I have never heard this before, I work with a lot of commercial fire rated walls and What I would normaly see in this situation would be 2 layers of 5/8 drywall on the inside or 1 layer with rockwool in the stud bays.
I would go talk it over with them, what I think is a misunderstanding, That sounds like a interior wall fire rateing not exterior.
__________________
The shop is both my salvation and sanity!
Of course the garage is bigger than the house, People live in houses, Trucks live in garages!
my shop redo/give me hell
https://www.youtube.com/c/WoodNMetalWorkshop?gvnc=1[/URL
Thumper68 is offline   Reply With Quote
Old 12-19-2013, 12:57 PM   #6
woodrail
Senior Member
woodrail's Avatar
It all about the assembly, not the individual materials. Tell them you want to use a UL-356 construction. This gives you 1-hour.
"U356: 5/8" (15.9 mm) Fire-Shield Gypsum Board applied vertically to interior side of 2x4 wood studs 16" o.c. with 6d coated nails, 1-7/8" long, 1/4" heads, 7" o.c. 3-1/2" insulation installed in stud cavity. 7/16" wood panels applied horizontally or vertically to exterior side with 6d coated box nails 6" o.c. Exterior to be finished with vinyl siding, particle board siding, wood structural panel (lap siding), cementitious stucco, brick veneer, exterior insulation and finish system (EIFS), steel/aluminum siding, fiber cement siding."
You are probably close to this construction already. Pray they don't make you rate your roof construction.
__________________
- DanB
Garage Gallery - The Rocket Shop
woodrail is offline   Reply With Quote
Old 12-19-2013, 02:11 PM   #7
Senior Member
theoldwizard1's Avatar
Quote:
Originally Posted by Thumper68 View Post
... What I would normaly see in this situation would be 2 layers of 5/8 drywall on the inside or 1 layer (5/8) with rockwool in the stud bays.
This is a good solution because you getting insulation also.
Check on ceiling requirements as well as use of any "special" joint compounds/tape.
If you are hiring it out, make sure the contract states, in writing, "installed to be compliant with local code." Also in writing, state you are going to hold back at least 1/3 of the payment until it is inspected and approved.
theoldwizard1 is offline   Reply With Quote
Old 12-19-2013, 02:13 PM   #8
clemsonee
Junior Member
Thanks for the input. I will just schedule a meeting with them.
Old 12-19-2013, 02:19 PM   #9
clemsonee
Junior Member
It is 5/8 gypsum on the interior and exterior, one layer, with brick veneer.
Old 12-19-2013, 06:24 PM   #10
6768rogues
Senior Member
Since it is a property line issue, I assume that the fire rating has to be to protect an adjacent property from your building fire. The brick will be attached to the framed wall. If your building fire levels that framed wall, the brick will go down, too.
Any engineer/architect friend or perhaps the local library, or the local code enforcement office should have a copy of the Underwriters Laboratory (UL), Gypsum Association (GA) and/or Factory Mutual (FM) books that described listed fire rated systems. Any system in those books that meets your construction limitations and the fire rating requirements is acceptable under building codes. There are hundreds of them. Check the books, pick a system, then submit the system number to the code office. It should be acceptable to them; that is what architects and engineers do. Then you have to build it exactly as it is listed.
__________________
Why a cool garage? Chicks dig 'em. Alcohol may intensify the effect. As John Belushi said in Animal House, "I suggest you drink and drink heavily."
6768rogues is offline   Reply With Quote
Old 12-19-2013, 07:44 PM   #11
Architorture
Senior Member
http://publicecodes.cyberregs.com/ic...2_7_par338.htm
Read up
Architorture is offline   Reply With Quote
Old 12-19-2013, 09:26 PM   #12
woodrail
Senior Member
woodrail's Avatar
uhm, I just gave him this info a couple of posts up. Unless he runs up against a hardass, this should get him through.
__________________
- DanB
Old 12-20-2013, 07:18 AM   #13
KELLHAMMER
Senior Member
KELLHAMMER's Avatar
Wall assemblies are given an hourly rating based on UL testing. UL assemblies can vary in materials, so you could look at the UL tests for alternatives to achieve a 1 hour PARTY wall.
Be prepared to show the UL info to the building official since there are thousands and they will want the published info
KELLHAMMER is offline   Reply With Quote
Old 12-20-2013, 07:48 AM   #14
Senior Member
So that was after the "meeting" ?
Old 12-20-2013, 11:07 AM   #15
rancherbill
Senior Member
rancherbill's Avatar
This is a case of DEFINITELY finding out all about it before you proceed.
Around here they have the similar regulations. The builders don't use regular drywall, it is pink colored on residential walls on the side exposed to neighbors. On commercial they use yellow colored drywall on the whole exterior of the building. It is not regular drywall.
Every year there are stories of a house burning down and also burning down the houses on either sides.
__________________
General Warning
I couldn't repair your brakes, so I made your horn louder.
rancherbill is offline   Reply With Quote
Old 12-20-2013, 11:08 AM   #16
clemsonee
Junior Member
Quote:
The only thing different than original is 5/8 vs 1/2. No meeting yet, just clarified it with the builder.
Old 12-20-2013, 07:31 PM   #17
Senior Member
Has your builder dealt with this building inspection department ?
Old 12-20-2013, 10:17 PM   #18
CNGsaves
Senior Member
CNGsaves's Avatar
Question Re: One hour fire rating
What . . . COUNTRY . . . . . STATE . . . . . CITY ????
CNGsaves is offline   Reply With Quote
Reply
Thread Tools
Display Modes
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Forum Jump