You are currently viewing our boards as a guest which gives you limited access to view most discussions and access our other features. By joining our free community you will have access to post topics, communicate privately with other members (PM), respond to polls, upload content and access many other special features. Registration is fast, simple and absolutely free so please, join our community today!

If you have any problems with the registration process or your account login, please contact contact us.

Go Back   The Garage Journal Board > The Garage > General Garage Discussion

Sponsored Links (Register now to hide all advertisements)

Reply
 
Thread Tools Search this Thread Display Modes
Old 01-13-2006, 06:33 PM   #1
DynoDave
Senior Member
 
DynoDave's Avatar
 
Join Date: Mar 2005
Location: Michigan
Posts: 1,192
Default Running natural gas to a garage

Hey guys. Just wondering if anyone ran their own gas pipe to their shop. I don't know what's involved. Black iron was always the standard when I was helping my Dad, but a friend at work said a lot of that is done with rolls of plastic today. My application will be a run from the house, across the yard, to a detached garage. Any thoughts?
__________________
DynoDave
WPC #12304
1970 Plymouth Duster
1972 Dodge Charger Rallye
1977 Chrysler Cordoba
1988 Pontiac Firebird TransAm
DynoDave is offline   Reply With Quote
Old 01-13-2006, 07:50 PM   #2
drbill
Senior Member
 
Join Date: Jan 2006
Location: Detroit
Posts: 118
Default

Hey Dave hows it going.
To answer your question when I did mine I ran soft copper, flaired it on both ends and put a fitting that changes it over to black pipe. Of course I don't have it done inside the garage yet but I have a 3 day weekend to get it done along with installing the heater.
drbill is offline   Reply With Quote
Sponsored Links (Register now to hide all advertisements)
Old 01-13-2006, 08:11 PM   #3
rockwithjason
Union Wireman
 
rockwithjason's Avatar
 
Join Date: Jan 2006
Location: Las Vegas
Posts: 1,502
Default

in most places you have to run black pipe to meet code. plastic is used underground.
rockwithjason is offline   Reply With Quote
Old 01-13-2006, 08:29 PM   #4
chrgdrt
Junior Member
 
Join Date: Jan 2005
Location: Mi.
Posts: 12
Default

Dave,
If the run is less than 50' I think copper wouldlbe the way to go. it's difficult to get copper in legnths over 50'. I had a 130' run so I used 1" plastic.

Gary.
chrgdrt is offline   Reply With Quote
Old 01-13-2006, 09:38 PM   #5
fireman
Senior Member
 
Join Date: Dec 2005
Posts: 129
Default

Plastic for the underground and either black iron or type "L" or "K" copper for the rest would be fine. Do not connect copper directly to black iron.
fireman is offline   Reply With Quote
Old 01-13-2006, 09:56 PM   #6
REFLEXX
Senior Member
 
REFLEXX's Avatar
 
Join Date: Aug 2005
Location: Riverside, CA
Posts: 913
Default

I used black pipe for propane line (90 ft) and thread-sealed it with yellow teflon tape. The you wrap the outside of the fittings with some vynil tape. Our county codes say 18" deep

I'd stay away from plastic or copper, one good shovel strike and you've got a leak.

after you connect the whole thing, check for pressure (15 lbs) for 24 hrs. It will vary with temps but should not loose any.

my 2.5c
__________________
REFLEXX
My Garage Mahal: http://www.garagejournal.com/forum/s...ead.php?t=1253
My Garage Mahal (dream workshop) for EVERYONE! http://vocademy.com/
REFLEXX is offline   Reply With Quote
Old 01-14-2006, 09:25 AM   #7
spud
Junior Member
 
Join Date: Jan 2005
Location: Alberta
Posts: 19
Default

My last garage had Plastic pipe with steal risers, the local gas co-op had built it. but it was underground. It is my understanding that if you use black pipe undergound it must have welded connections not threaded. threre is also a fleaxxable steel line called "Gastite" (they have a website" that is run in new house construction, but I dont know if it can used outside. I just finished my garage furnace in my new house, and I bought black pipe and rented a threader and cutter and did all my own for Natual gas.ut none of it was under ground.

remeber if you do have a riser comming out of the ground that will have cement around it, you should put a plastic colloar around the riser so the cement cant put any weight on your line if it shifts
spud is offline   Reply With Quote
Old 01-15-2006, 07:08 AM   #8
DynoDave
Senior Member
 
DynoDave's Avatar
 
Join Date: Mar 2005
Location: Michigan
Posts: 1,192
Default

Hey Dr. Bill! Didn't know you were hanging around here now. Is this some of Jonís handwork? LOL
Copper sure sounds a LOT easier to work with than iron. Is your run over 50 feet? Chrgdrt (posted below yours) mentioned it's difficult to get copper over 50 feet in length.

Jason...I'll be running a fair distance underground. Say 30 feet if I build in one location, or a 70 feet if I build in another.

Chrgdrt...that's what I was thinking. Ease of install around bends, and just unrolling into a trench sounds pretty good to me! Just wasn't sure about code in Michigan for depth, or material type.

Fireman, thatís what I'm hoping to do.

Reflexx...I can appreciate (& share) your concern about durability. I could see copper getting damaged by a hand shovel. The plastic I've had described to locally sounds plenty tough to withstand it.

Spud...I'm not really familiar with gas pipe at all. What are risers? Are you saying they ran plastic underground, and then teed in iron when ever it was coming up to the surface? It's funny you mentioned that the co-op do the work, as I was wondering if I would have to hire the local gas company here (Consumers Energy) to do the work. I hope not. After a horrendous experience working with our local electric provider 2 years ago, I very much believe that the LESS interaction I have with a large utility the better off I am.

Thanks to everyone for replying so far. Any other thoughts? Sounds like the next step is to find out if there are any local code restrictions about trench depth, and pipe type.
__________________
DynoDave
WPC #12304
1970 Plymouth Duster
1972 Dodge Charger Rallye
1977 Chrysler Cordoba
1988 Pontiac Firebird TransAm
DynoDave is offline   Reply With Quote
Old 01-15-2006, 08:57 AM   #9
Bill K
Senior Member
 
Join Date: Oct 2005
Location: Thomasville NC
Posts: 100
Default

I strongly suggest you get a gas contractor or your local gas supplier to run your line.
This is for liability reasons. If you should happen to have a leak and a fire your home owners insurance will not cover the damage if they find you did the work.
If you run the line yourself you need to check with your supplier to see what type system you have ,ie 1/2 pound or higher pressure. Thiss make a differance as to pipe sixe and regulators to use.
There is a specific type of plastic pipe used for underground gas make sure you use that.
There is also a flex type, ribbed metal covered with a yellow sheath. It is used above ground and in walls etc.
If you do the work yourself have it inspected, then God forbid there is a problem you will be covered by your insurance.
Check your local building codes and with your inspector.
I work with natural and propane gas fireplaces, hope this helps
Bill.
Bill K is offline   Reply With Quote
Old 01-15-2006, 09:21 AM   #10
krooser
Senior Member
 
krooser's Avatar
 
Join Date: Jun 2005
Location: Waupaca, Wisconsin
Posts: 2,378
Default

FYI.....Virtually ALL underground gas pipe used in North America today is plastic....I'm in and out of those pipe yards every month....I haul miles of it going to gas and pipeline companies in the south and midwest.
krooser is offline   Reply With Quote
Old 01-15-2006, 09:36 AM   #11
bmwpower
Super Moderator
 
bmwpower's Avatar
 
Join Date: Apr 2005
Location: NJ
Posts: 12,500
Send a message via AIM to bmwpower Send a message via Yahoo to bmwpower
Default

My plumber used CSST (corrugated stainess steel tubing) with the yellow jacket inside a PVC sleeve. My run is quite curved, which would have meant more joints with black pipe (potentially more leaks).

Black pipe was used before the line exited the home as well as once the CSST entered the garage.
__________________
bmwcca 147895 | 99 m3 | 90 535i | 89 325is | 04 sienna le awd | 88 f250 4x4
my garage build | my wanted list
bmwpower is offline   Reply With Quote
Old 01-15-2006, 11:47 AM   #12
drbill
Senior Member
 
Join Date: Jan 2006
Location: Detroit
Posts: 118
Default

Well Dave I just kind of wander over here.
I ran my gas line in the same trench as my electric lines. They are in seperate plastic conduits roughly 24" down(depth of the trencher I rented). If I remember electric line only need to be 18". I think in total because of the 90į bend to get to the garage it's 37' plus what ever it going down and coming back up the trench. Well with in what you can buy. One thing I did learn is that 1/2" copper and 1/2" black pipe are not the same inside diameter. Copper being 0.500 and pipe being 0.622. So if you have a long run and a large furnace you might have to step up to a larger size pipe for the underground run.
drbill is offline   Reply With Quote
Old 01-15-2006, 05:47 PM   #13
Tim240Z
Senior Member
 
Tim240Z's Avatar
 
Join Date: Jul 2005
Location: LAX area, So Cal
Posts: 180
Default

http://www.garagejunkies.net/showthread.php?t=1540
Tim240Z is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On

Forum Jump

Similar Threads
Thread Thread Starter Forum Replies Last Post
New Guys garage DaveL. Garage Gallery 26 06-06-2008 10:33 AM
Running air line to semi-detached garage.... chrisexv6 General Garage Discussion 13 01-13-2006 10:07 PM
Running Natural Gas to Garage RoadRunner General Garage Discussion 30 11-22-2005 03:39 PM
Running electric to finish off my Garage loosegroove General Garage Discussion 12 04-12-2005 02:52 PM
My Garage plans... SANDOVAL General Garage Discussion 2 03-21-2005 08:44 AM

Sponsored Links (Register now to hide all advertisements)


All times are GMT -5. The time now is 02:02 AM.