You are currently viewing our boards as a guest which gives you limited access to view most discussions and access our other features. By joining our free community you will have access to post topics, communicate privately with other members (PM), respond to polls, upload content and access many other special features. Registration is fast, simple and absolutely free so please, join our community today!

If you have any problems with the registration process or your account login, please contact contact us.

Go Back   The Garage Journal Board > The Garage > Lighting & Electrical

Sponsored Links (Register now to hide all advertisements)

Reply
 
Thread Tools Search this Thread Display Modes
Old 05-28-2009, 05:33 PM   #1
Phuckin' Jim
Senior Member
 
Join Date: May 2009
Location: North of the Peg
Posts: 129
Default ACWU 90 vs. TECK 90.

I am planning to run a 100 amp service out to a garage.
I was thinking of using either 2 guage aluminum teck, or aluminum ACWU wire.
Can I use either one?
Is there usually a big cost difference?
Also, do I need to use an "LB" connector where it enters the building?
I will be doing this in Manitoba.
Thanks for any info.
Phuckin' Jim is offline   Reply With Quote
Old 05-28-2009, 07:52 PM   #2
mrb
Senior Member
 
mrb's Avatar
 
Join Date: Dec 2008
Posts: 3,735
Default Re: ACWU 90 vs. TECK 90.

as long as its rated for direct burial....

does canada require an armored cable? Or can you get some other direct burial cable that is cheaper?
mrb is offline   Reply With Quote
Sponsored Links (Register now to hide all advertisements)
Old 05-28-2009, 08:11 PM   #3
Phuckin' Jim
Senior Member
 
Join Date: May 2009
Location: North of the Peg
Posts: 129
Default Re: ACWU 90 vs. TECK 90.

Quote:
Originally Posted by mrb View Post
as long as its rated for direct burial....

does canada require an armored cable? Or can you get some other direct burial cable that is cheaper?
Canada doesn't require armoured cable underground. The local inspector happened to be in the Hydro office and I got to talk to him briefly, he told me I could use this stuff:

http://www.nexans.com/eservice/Canad...600_V.html#top
Also I would need a #6 copper ground wire, 2 ground rods or a 2'x2' ground plate, buried 3' deep.

I forgot to ask him if it needed to be in conduit where in runs in the garage and the house. He did mention needing the conduit where it enters/exits the ground to the building.

I'm trying to figure out if using aluminum armoured cable would be much more $$$ than the triplexed wire, conduit, fittings the ground plate and wire...
Phuckin' Jim is offline   Reply With Quote
Old 05-28-2009, 08:49 PM   #4
nate379
Banned
 
Join Date: Feb 2009
Location: Palmer, AK
Posts: 7,297
Default Re: ACWU 90 vs. TECK 90.

My house has 125amp service and it's 4 guage aluminum wiring. They came out and buried it today actually.
nate379 is offline   Reply With Quote
Old 05-29-2009, 08:43 PM   #5
Phuckin' Jim
Senior Member
 
Join Date: May 2009
Location: North of the Peg
Posts: 129
Default Re: ACWU 90 vs. TECK 90.

Quote:
Originally Posted by nate379 View Post
My house has 125amp service and it's 4 guage aluminum wiring. They came out and buried it today actually.
They let you #4 wire for 125 amp?
Here they want #3 copper, or # 2 aluminum for 100 amp service.


I dug deeper into the 'net regarding the differences between "Teck" and "ACWU" wire, and found this page:
http://www.nexans.ca/egy/equip/ProdP...blesCSA_E.html

It looks like the TECK is a tougher cable, but it is more $$$.

If the cost difference between the 2 is huge, I will go with the ACWU.

I will keep you guys posted.
Phuckin' Jim is offline   Reply With Quote
Old 05-29-2009, 09:55 PM   #6
tfi racing
Senior Member
 
tfi racing's Avatar
 
Join Date: Apr 2008
Location: Cedar,BC
Posts: 1,260
Default Re: ACWU 90 vs. TECK 90.

What's the distance,that will be the big deciding factor between Al or Cu.I have direct buried ACWU on many projects,including my own,it does need to be "protected" where it comes out of the ground,not a big deal.I'm not sure why the inspector mentioned ground rods and/or a plate,a no-no on this side of the border unless its a barn for livestock,perhaps they have more barns than shops in your area.
tfi racing is offline   Reply With Quote
Old 05-29-2009, 10:07 PM   #7
nate379
Banned
 
Join Date: Feb 2009
Location: Palmer, AK
Posts: 7,297
Default Re: ACWU 90 vs. TECK 90.

I was told #4 is good for 65 amps per leg, so 130amps. Dunno, I didn't do the work, the power company did.

Quote:
Originally Posted by Phuckin' Jim View Post
They let you #4 wire for 125 amp?
Here they want #3 copper, or # 2 aluminum for 100 amp service.


I dug deeper into the 'net regarding the differences between "Teck" and "ACWU" wire, and found this page:
http://www.nexans.ca/egy/equip/ProdP...blesCSA_E.html

It looks like the TECK is a tougher cable, but it is more $$$.

If the cost difference between the 2 is huge, I will go with the ACWU.

I will keep you guys posted.
nate379 is offline   Reply With Quote
Old 05-29-2009, 10:13 PM   #8
Phuckin' Jim
Senior Member
 
Join Date: May 2009
Location: North of the Peg
Posts: 129
Question Re: ACWU 90 vs. TECK 90.

The garage is going to be 25' from the house, and the breaker panel in the house is on the wall closest to the garage. The garage panel is going to be on the wall closest to the house. I estimate the total length of the cable to be ~ 45 feet.

I think the inspector mentioned ground rods/plate electrode because I was asking about using the non-armored triplex wire (USEI 90) that is lacking a ground wire.
http://www.nexans.ca/egy/power/under..._secondary.htm

When you say ACWU needs protection where it comes out of the ground, do you mean 1-1/2" conduit and an "LB" fitting?
Did you choose ACWU because it was a lot cheaper than TECK?
Thanks for the info, it's coming in handy.

Last edited by Phuckin' Jim; 05-29-2009 at 10:17 PM.
Phuckin' Jim is offline   Reply With Quote
Old 05-30-2009, 10:51 AM   #9
tfi racing
Senior Member
 
tfi racing's Avatar
 
Join Date: Apr 2008
Location: Cedar,BC
Posts: 1,260
Default Re: ACWU 90 vs. TECK 90.

I would use the ACWU,however some are leary of aluminum and prefer copper,I see no real reason to spend the extra money,don't forget the anti-ox on the terminations.You will want to use 2" pvc and lb's,it just makes it easier to stuff the cable through.
tfi racing is offline   Reply With Quote
Old 05-30-2009, 08:56 PM   #10
Phuckin' Jim
Senior Member
 
Join Date: May 2009
Location: North of the Peg
Posts: 129
Default Re: ACWU 90 vs. TECK 90.

Thanks. That's probably the route I'll be taking.
Another idea I'm kicking around is to pass the cable thru the cinder block basement wall, 24" below the ground level. Once inside the un-finished basement, I would head up and toward the panel.
Is that allowed? is it a bad idea?
I have lots of time to plan this, the garage isn't built yet....
Phuckin' Jim is offline   Reply With Quote
Old 06-01-2009, 01:11 PM   #11
dodgeram2500
Member
 
dodgeram2500's Avatar
 
Join Date: Oct 2008
Location: Thunder Bay, ON
Posts: 48
Default Re: ACWU 90 vs. TECK 90.

Not sure about what the rules are, but I wouldn't want a hole in the ground below grade.....good place for water/critters to come in.
__________________
- Pat Elliott - 24x30x10 - 2x6 construction -
http://www.garagejournal.com/forum/s...ad.php?t=28771
dodgeram2500 is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Sponsored Links (Register now to hide all advertisements)


All times are GMT -5. The time now is 09:34 PM.