Welcome to the The Garage Journal Board forums. You are currently viewing our boards as a guest which gives you limited access to view most discussions and access our other features. By joining our free community you will have access to post topics, communicate privately with other members (PM), respond to polls, upload content and access many other special features. Registration is fast, simple and absolutely free so please, join our community today! If you have any problems with the registration process or your account login, please contact contact us. |
|
|||||||
![]() |
|
Thread Tools | Display Modes |
|
|
#1 |
|
Junior Member
Join Date: Dec 2008
Location: Canada
Posts: 4
|
How much electric baseboards do i need for my new garage
I have (2) 3X5 windows 1 regular 36" door (1) overhead garage door 12x7 R-16 walls R-20 roof R-31 size of garage is 22x26 with 9 foot walls and vaulted ceilings up to 12 feet want to heat all winter at 16-17°C thanks |
|
|
|
|
|
#2 |
|
Junior Member
Join Date: Sep 2009
Location: British Columbia, Canada
Posts: 15
|
When figuring this out accurately it's also helpful to know which direction your doors and windows are facing, North, south, east, or west. I do heating and cooling for a living so I might be able to help. This might also help to. My shop is roughly the same size and construction, except no windows, and I have three baseboards. If they were all on at the same time it would cook you right out. I usually have two on. I live in Canada also, and where I live we range in temp. anywhere from zero to minus 25 in the winter.
|
|
|
|
|
|
#3 |
|
Senior Member
Join Date: Aug 2009
Posts: 196
|
1000 watts / 100 sq ft. I would round up if necessary since it's a garage.
|
|
|
|
|
|
#4 |
|
Junior Member
Join Date: Dec 2008
Location: Canada
Posts: 4
|
thanks guys,
I have quite alot of trees in my yard so sunlight doesn't really reach the windows |
|
|
|
|
|
#5 | |
|
Junior Member
Join Date: Dec 2008
Location: Canada
Posts: 4
|
Quote:
|
|
|
|
|
|
|
#6 |
|
Junior Member
Join Date: Dec 2008
Location: Canada
Posts: 4
|
|
|
|
|
|
|
#7 |
|
Member
Join Date: Jun 2009
Posts: 47
|
How much in elec costs would Baseboard be like compared to Gas. Would always think be too much.
|
|
|
|
|
|
#8 |
|
Senior Member
Join Date: May 2009
Location: North of the Peg
Posts: 123
|
What part of Canada are you in?
Saskatoon,SK and Victoria, BC would have very different needs. Just north of Winnipeg, in my 24x24 garage w/10 ft. walls, I'll be installing 2 2500 watt baseboard heaters. I'll keep you posted on how well this works for a Manitoba winter. |
|
|
|
|
|
#9 |
|
Senior Member
Join Date: Oct 2009
Location: On a planet with alot of really Stupid people
Posts: 222
|
You would need a bare minimum of 22.88' of electric baseboard heat.
Electric baseboard heat is 250 watts per foot. you need a bare minimum of 5720 watts of heat The equation as I learned it years ago from my father (master electriction) when he would calculate the required baseboard for a job, is as follows. Take the room in question (your garage) 22x26 = 572 x 10 = 5720 divided by 250 = 22.88 This is based on a normal 8' ceiling. Now factoring in your high ceiling I would probably want to increase the footage of heat by 30% +/- or another 6' - 8' of baseboard Also if it helps. You can run 16' of electric baseboard heat on a 20 amp breaker, 220 volt circut. 16' of heat = 4000 watts So, roughly 30' of baseboard heat and 2- 20 amp / 220 volt circuts |
|
|
|
|
|
#10 |
|
Senior Member
Join Date: May 2006
Location: St. Louis, MO
Posts: 505
|
I'm having same dilemma especially that we just got ad on craigslist:
brand new Emerson baseboard heaters for sale. These are to be hard wired not the plug in type! 240 volt 940 watts 3208 btu. $ 35 each I'm in a process of "electryfying" garage and wondered if it makes sense to install those. I was planning on mini-split but imagine that baseboards will work better. I have 21x21 garage. Do I need more then 3 of those baseboards? How is electricity use, does it make sense to install them? I know electricity is cheap in STL in a winter, like 4c so it makes sense to use it over gas. Are they safe? Ideally I would keep one on all the time because we enter house via garage. And garage will be insulated.
__________________
BMW 540i/6 97', Mazda Rx-7 94' |
|
|
|
|
|
#11 |
|
Senior Member
Join Date: Nov 2009
Location: Big Sky Country, Canada
Posts: 1,725
|
Where in Canada are you? Fill out your sig please. I really helps us help you.
In my previous house, 22 x 24 ft attached garage, R12 walls and R40 ceiling, insulated steel garage door, a 4800 W construction heater would heat it up as warm as I wanted it, but it did take a while at -20C or colder. That was for intermittent heating. I only turned in on to thaw the cars or if I was doing a project. That works out to 9 W per sq. ft. 10 W/ft2 is the rule of thumb used successfully for years in colder climates for residential construction. Again, you might want a bit more to have faster recovery after the garage door is opened. One thought is 10 W/ft2 of baseboard heat, and add a couple of cheap fan forced 1500W electric heaters if you have enough circuit capacity. Keep the thermostat settings low enough that they don't come on when your garage is at the temp you want. This way after you cool off the garage from opening a door, the baseboard heaters will turn on, but convection heat takes a while to recover. The fan forced heat will circulate warm air faster, so more comfort. No extra operating cost either, as the baseboards will just shut off faster once the design temp is reached.
__________________
After the reading of the rich man's last will and testament, the family was asked "How much did he leave?" The answer: "All of it." |
|
|
|
|
|
#12 |
|
Senior Member
Join Date: May 2009
Location: North of the Peg
Posts: 123
|
Well, now that we've been through part of a winter, I can honestly say I'm satisfied with the way the 2 10 foot 2500 watt baseboard heaters heat the garage. I have to plan a couple of hrs. ahead if I want it warm enough to work in.
I usually leave the heat off unless I plan to work in there. |
|
|
|
|
|
#13 | |
|
Senior Member
Join Date: Jan 2010
Location: The Bad Lands
Posts: 6,851
|
Would you mind taking a temp reading for me? I wouldnt mind seeing how hot it gets in there with our winters being as they are. Glad you followed up with this thread, as I was eyeing it for sometime.
![]() Regards EVIL Teken . . .
__________________
Do or Die . . . No one gets left behind !! Quote:
|
|
|
|
|
|
|
#14 | |
|
Senior Member
Join Date: May 2009
Location: North of the Peg
Posts: 123
|
Quote:
The warmest I've had it so far was 17 C, but I'm sure it would have gotten warmer had I left the thermostats turned up. Mind you, it was only -25C that day, so it wasn't that cold.
|
|
|
|
|
|
|
#15 | ||
|
Senior Member
Join Date: Jan 2010
Location: The Bad Lands
Posts: 6,851
|
Quote:
It's it too funny that when its only -25'C here we equate that it's not that cold?? ![]() Do you recall last year when we had three weeks of -56'C with the wind chill?![]() ![]() ![]() That was a day to just keep your aszz at home, too bad I didn't, had to be in the field working like dumb SOB . . ![]() ![]() Thanks for taking the temps for me, much appreciated. This will give me some reference if and when I ever get this garage down. Regards EVIL Teken . . .
__________________
Do or Die . . . No one gets left behind !! Quote:
|
||
|
|
|
|
|
#16 |
|
Senior Member
Join Date: Jan 2006
Location: 50 mi south of Atlanta
Posts: 8,837
|
Problem with baseboard heaters (and I had them in one house I owned) is that you have to keep the wall space clear. In a garage you want workbenches, etc on the walls. They just don't look to me like they would be real practical for a garage.
Charles |
|
|
|
|
|
#17 | |
|
Senior Member
Join Date: Jan 2010
Location: The Bad Lands
Posts: 6,851
|
I know, that is the problem I am wrestling with. I might bite the bullet when finances are better to go all the way and pay someone to plumb in a NG line and install one of those over head units.
I have lived part of my life with *that's good enough* for some random things. In this latter stage of my life *good enough* ins't cutting it. So, more than likely I will *do it once, and properly* then to waste my time, energy, and hard earned dollars. Many thanks for your follow up & insight.
__________________
Do or Die . . . No one gets left behind !! Quote:
|
|
|
|
|
|
|
#18 |
|
Senior Member
Join Date: Jan 2007
Location: Central Ohio
Posts: 243
|
I belive NEC requires outlets in the garage to be at least 24" above finished floor. I don't know code on baseboard heaters in a garage, but something just doesn't sound right about it.
__________________
visit the nest ... www.roadrunnernest.com my garage build http://garagejournal.com/forum/showthread.php?t=7600 |
|
|
|
|
|
#19 | |
|
Senior Member
Join Date: Jan 2006
Location: 50 mi south of Atlanta
Posts: 8,837
|
Quote:
You can get stupid with this however, things like my fridge have a defrost timer down in the bottom of it, this timer has electrical contacts that most likely spark when it cycles, so I guess I should elevate my fridge above 18 inches. Then there is the thermostat for my 2 gal under counter water heater, and on it goes. Of course this is why the fire marshal requires that we use twist lock electrical connectors at work on extension cords, flo lights, etc, to prevent sparking from accidental disconnects with cords laying on the floor. (commercial aircraft hangar, Class I, Division 2 up to 18 inches off the floor and surrounding all wings and powerplants). Charles |
|
|
|
|
|
|
#20 |
|
Senior Member
Join Date: May 2009
Location: North of the Peg
Posts: 123
|
A few more numbers:
Last night I switched the heat on @ 6:45 Temp was -2C in the garage and -14C outside. At 7:45, I went in there to start working, and the temp was 7C At 8:15 the temp was 11C. At that point I was just about done the tire rotate, brake & front end inspection, so I shut the heat off again. At about 6:30 this morning, the thermometers read -2 again. The overnight low last night was -16C. It's nice to have this warm weather. ![]() As far as mounting the baseboards a certain minimum distance from the floor, I mounted them ~ 8" from the floor, and they passed electrical inspection.
|
|
|
|
![]() |