You are currently viewing our boards as a guest which gives you limited access to view most discussions and access our other features. By joining our free community you will have access to post topics, communicate privately with other members (PM), respond to polls, upload content and access many other special features. Registration is fast, simple and absolutely free so please, join our community today!

If you have any problems with the registration process or your account login, please contact contact us.

Go Back   The Garage Journal Board > The Garage > Lighting & Electrical

Sponsored Links (Register now to hide all advertisements)

Reply
 
Thread Tools Search this Thread Display Modes
Old 09-26-2009, 11:26 AM   #1
ebasista
Member
 
Join Date: Dec 2008
Posts: 42
Default 2-2-2-4 Mobile Home Feeder wire for Garage?

I decided to go with Mobile home feeder wire for my subpanel in the garage. Its going to be 2-2-2-4 AL wire, breakered in the main panel at 90A connected to a 100A main disconnect subpanel in the garage.

http://www.southwire.com/ProductCata...prodcatsheet15

I understand that I can direct bury this wire, and will use sch80 to go from the ground to the house and garage.

What do I have to do inside the house with this wire to protect it....is conduit required in the house for this, or can i run it thru the crawlspace to the panel without any additional shielding?
ebasista is offline   Reply With Quote
Old 09-26-2009, 11:33 AM   #2
mrb
Senior Member
 
mrb's Avatar
 
Join Date: Dec 2008
Posts: 3,735
Default Re: 2-2-2-4 Mobile Home Feeder wire for Garage?

make sure the cable you get has the RHH / RHW listing or it cant enter the structure. It would need to be in conduit inside the house since its individual wires and not a jacketed cable.

I wouldnt use the stuff. I would go conduit all the way and individual AL conductors.
mrb is offline   Reply With Quote
Sponsored Links (Register now to hide all advertisements)
Old 09-26-2009, 02:31 PM   #3
Charles (in GA)
Senior Member
 
Charles (in GA)'s Avatar
 
Join Date: Jan 2006
Location: 50 mi south of Atlanta
Posts: 11,004
Default Re: 2-2-2-4 Mobile Home Feeder wire for Garage?

Quote:
Originally Posted by mrb View Post
make sure the cable you get has the RHH / RHW listing or it cant enter the structure. It would need to be in conduit inside the house since its individual wires and not a jacketed cable.

I wouldnt use the stuff. I would go conduit all the way and individual AL conductors.
I have 150 ft of this same cable. I think the brochure he linked to says it all.

Southwire mobile home feeder consists of four quadruplexed type RHH or RHW-2 or USE-2 AlumaFlex TM AA-8000 series
aluminum alloy compacted conductors. The cable contains a triple extruded white striped neutral conductor and a green
grounding conductor to eliminate the need for field marking per the National Electrical Code. Insulation is sunlight resistant .


Indeed, the cable, consisting of four individual wires twisted together are marked with all the specs indicated in the brochure.

Charles
Charles (in GA) is offline   Reply With Quote
Old 09-26-2009, 02:42 PM   #4
bward76
Junior Member
 
Join Date: Jan 2009
Posts: 25
Default Re: 2-2-2-4 Mobile Home Feeder wire for Garage?

I agree to using conduit as well but If you insist on direct burial be very very certain that it is in a path that will never be near any trees or bushes. I had a service account a few years back that fed hundreds of mobile homes (built about 20 years ago) all in direct burial cable. Over the coarse of a couple years, I replaced probably 30 sets of their feeders that had been destroyed by roots over time. This involved trenching from the transformer to the unit on every one(very expensive). In this case a lot of t.v.'s and appliances were damaged when the problems occurred.
bward76 is offline   Reply With Quote
Old 09-26-2009, 05:52 PM   #5
ebasista
Member
 
Join Date: Dec 2008
Posts: 42
Default Re: 2-2-2-4 Mobile Home Feeder wire for Garage?

There will never be tree roots or shrubs to worry about in this location (too close to my house and never plan on putting stuff there).

Inside the house I take it I'm required to use conduit in the crawlspace up to the box (whats the minimum size for that)? I would like to avoid using conduit in the house because of the hassle, can I connect this to shielded cable inside the house?
ebasista is offline   Reply With Quote
Old 11-19-2009, 12:24 PM   #6
Iseman
Member
 
Iseman's Avatar
 
Join Date: Dec 2008
Location: Kerrville, TX
Posts: 48
Default Re: 2-2-2-4 Mobile Home Feeder wire for Garage?

I used the same wire and direct buried it like the manufacture approves. BIG BIG BIG mistake. Even with no trees or bushs nearby it can still come in contact with moisture or water. When I put in the new line 2 years later, the electrician said it happens all the time. There is a nick or crack in the insulation and now you have burn thru. Bury it in a conduit, be safe and not sorry. Cost me an additional $3000 to fix. Conduit less than $200. Just my oppinion. Maybe to late.
Iseman is offline   Reply With Quote
Old 11-19-2009, 02:22 PM   #7
bimmer1980
Senior Member
 
bimmer1980's Avatar
 
Join Date: Feb 2009
Location: York, PA
Posts: 787
Default Re: 2-2-2-4 Mobile Home Feeder wire for Garage?

2" PVC really isn't all that hard to run..... I just finished running some 2" PVC from my garage to the house (including under a driveway) and pulling 2# copper... not bad at all....
bimmer1980 is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Sponsored Links (Register now to hide all advertisements)


All times are GMT -5. The time now is 04:28 PM.