Welcome to the The Garage Journal Board forums. You are currently viewing our boards as a guest which gives you limited access to view most discussions and access our other features. By joining our free community you will have access to post topics, communicate privately with other members (PM), respond to polls, upload content and access many other special features. Registration is fast, simple and absolutely free so please, join our community today! If you have any problems with the registration process or your account login, please contact contact us. |
|
|||||||
![]() |
|
Thread Tools | Display Modes |
|
|
#1 |
|
Senior Member
Join Date: May 2006
Location: St. Louis, MO
Posts: 505
|
Can somebody do sanity check on my plan?
I have attached garage and I will be installing 100A subpanel. Wire will be run in a basement from main panel and then through the wall to garage. 1. I'm planning on using 3-3-3-2 NM wire with no conduit. Does it sound right? Length of run will be about 50-60 feet, main panel in opposite corner ![]() 2. With preparation for welder I will install 240v 50A outlet using 8 gauge wire. 3. Other stuff all will be on 12 gauge wire. Outlets, lights, etc.
__________________
BMW 540i/6 97', Mazda Rx-7 94' |
|
|
|
|
|
#2 | |
|
Senior Member
Join Date: Mar 2008
Posts: 2,580
|
Quote:
For #3 is this NM cable (Romex®)? If this is the case 8 AWG is 40 amperes max, if in conduit w/ the more common THHN/THWN insulation then your OK. NM cable per NEC article 334.80 is sized in the 60º column, SE type cables in areas that have adopted the 2008 NEC is also sized in the 60º column, if using the 2005 or earlier then the 75º column is OK to use to size them. Last edited by Norcal; 01-18-2010 at 09:07 AM. Reason: Remove erroneous info. |
|
|
|
|
|
|
#3 |
|
Senior Member
Join Date: May 2006
Location: St. Louis, MO
Posts: 505
|
#1 - Yes, copper. Our county won't let me touch aluminum. Nor I really want to. Thinner wire, negligible savings over AL.
#2 - Yes, I meant THHN - common one that's sells. Didn't know there is important differences ![]() Our county uses NEC 2005. Looks like i'm on a good track. Will see what inspector says about my plan. One more Q. With feeder wire when I move it out from basement - there will be bend and tight space coming into the wall that's shared between garage and basement. Should I put metal elbow or something like that to protect wire?
__________________
BMW 540i/6 97', Mazda Rx-7 94' |
|
|
|
|
|
#4 |
|
Senior Member
Join Date: May 2006
Location: St. Louis, MO
Posts: 505
|
So, which "standard" cable would I use? 2-2-2-3?
__________________
BMW 540i/6 97', Mazda Rx-7 94' |
|
|
|
|
|
#5 |
|
Senior Member
Join Date: Mar 2008
Posts: 2,580
|
#2 AWG is fine for 100A as long as your load does not exceed 95A, if your area is on the 2005 NEC & the cable is not a type NM but is a SER type, then your original plan is good to go. Read the cable jacket to see what type it is.
|
|
|
|
|
|
#6 |
|
Senior Member
Join Date: May 2006
Location: St. Louis, MO
Posts: 505
|
I don't have a cable, I'm going to get it. Should I ask for SER 2-2-2-3 then?
__________________
BMW 540i/6 97', Mazda Rx-7 94' |
|
|
|
|
|
#7 |
|
Member
Join Date: Aug 2009
Location: Northern Virginia
Posts: 68
|
Currently doing similar project myself. My thoughts are:
1. Inspector said, if using aluminum SER, go with #1 (1-1-1-3) for 100A subpanel. 2. 8/2 is acceptable for 50A welder-only circuit, depending on welder duty cycle. Mine would be light duty residential, so 8/2 it will be. 3. Convenience outlets on 12/2 20A; T8 lighting and garage door opener circuits will be 14/2 15A. No worries using aluminum when connections are properly torqued and no-ox paste is used. Aluminum is more flexible than copper and there will be 11 bends in my 44' run. Again, just my thoughts. |
|
|
|
|
|
#8 | |
|
Senior Member
Join Date: Mar 2008
Posts: 2,580
|
Quote:
|
|
|
|
|
|
|
#9 |
|
Senior Member
Join Date: May 2006
Location: St. Louis, MO
Posts: 505
|
What about 6/2. Is it good enough for welder? I don't care about wire cost right now, just want to make sure I can get any kind of welder and be able to use it..
__________________
BMW 540i/6 97', Mazda Rx-7 94' |
|
|
|
|
|
#10 |
|
Senior Member
Join Date: Mar 2008
Posts: 2,580
|
|
|
|
|
|
|
#11 |
|
Senior Member
Join Date: May 2006
Location: St. Louis, MO
Posts: 505
|
What about grounding? There is 2 hot wires for 240, 1 common and 1 ground, no? Shouldn't it be 6/3?
__________________
BMW 540i/6 97', Mazda Rx-7 94' |
|
|
|
|
|
#12 |
|
Senior Member
Join Date: Mar 2008
Posts: 2,580
|
|
|
|
|
|
|
#13 |
|
Senior Member
Join Date: May 2006
Location: St. Louis, MO
Posts: 505
|
Seems like I need to do Aluminum SER. Difference in price huge. I have 110ft run and al is at $2/ft vs $6/ft for copper.
__________________
BMW 540i/6 97', Mazda Rx-7 94' |
|
|
|
|
|
#14 |
|
Member
Join Date: Jan 2010
Location: N. Utah
Posts: 54
|
6 gauge for the welding recep. and Id make sure you pull a nuetral out too. 2 hots, neutral, and ground.
|
|
|
|
|
|
#15 |
|
Member
Join Date: Jan 2010
Location: N. Utah
Posts: 54
|
and you may have to upsize your alum wire for the amperage too. Copper will hold more amps than aluminum
|
|
|
|
|
|
#16 |
|
Senior Member
Join Date: May 2006
Location: St. Louis, MO
Posts: 505
|
Yep. Thats what inspector told me today.
__________________
BMW 540i/6 97', Mazda Rx-7 94' |
|
|
|
|
|
#17 | |
|
Senior Member
Join Date: May 2006
Location: St. Louis, MO
Posts: 505
|
Quote:
I also planned to run 12/3 along wall for split recepticles, but seems like it won't work with GFCI
__________________
BMW 540i/6 97', Mazda Rx-7 94' |
|
|
|
|
|
|
#18 |
|
Senior Member
Join Date: Sep 2005
Location: Santa Barbara, CA
Posts: 1,663
|
why run a neutral for a welder ? I can see it for a something like a dryer but not a welder ?
It does not matter as the original poster said the inspector told him to so he has to, but I was wondering why ? I did not run 6-3 for my welders, I did for the dryer and oven in the kitchen but in the garage its straight 6-2. |
|
|
|
|
|
#19 | ||
|
Senior Member
Join Date: Jan 2007
Location: Eastern Oregon
Posts: 1,601
|
Quote:
Quote:
Why? Are they making welders now that require a neutral? |
||
|
|
|
|
|
#20 |
|
Senior Member
Join Date: May 2006
Location: St. Louis, MO
Posts: 505
|
Aceman, my friend told me about aluminum. Today inspector didn't say anything - I will double-check tomorrow. I hope aluminum allowed.
For 6-3 welder it's what I was told. I will double-check tomorrow.