You are currently viewing our boards as a guest which gives you limited access to view most discussions and access our other features. By joining our free community you will have access to post topics, communicate privately with other members (PM), respond to polls, upload content and access many other special features. Registration is fast, simple and absolutely free so please, join our community today!

If you have any problems with the registration process or your account login, please contact contact us.

Go Back   The Garage Journal Board > The Garage > Lighting & Electrical

Sponsored Links (Register now to hide all advertisements)

Reply
 
Thread Tools Search this Thread Display Modes
Old 09-18-2010, 09:40 PM   #1
juicegoose
Member
 
Join Date: Aug 2008
Posts: 32
Default Whats the average amp draw from a small welder?

Guys I was going to run some wire to two 220v circuits tomorrow and for right now I'm just going to run double pole 20A duplex receptacles at each one for use with my woodworking machinery. I do want to kind of future proof myself to some extent not possible needs for a small mig welder. Would 10-3 on a 30amp breaker be enough for a good sized mig welder or not? Also a medium sized plasma cutter. I've got one that I can use at any time.
juicegoose is offline   Reply With Quote
Old 09-18-2010, 09:46 PM   #2
terabyte
Senior Member
 
terabyte's Avatar
 
Join Date: Apr 2006
Location: Southwest Ranches, Florida
Posts: 690
Default Re: Whats the average amp draw from a small welder?

my 185 amp tig and 175 amp mig both only need 30 amp each.
i believe 10-3 is good enough as long as its a reasonable run and copper
terabyte is offline   Reply With Quote
Sponsored Links (Register now to hide all advertisements)
Old 09-18-2010, 10:06 PM   #3
Norcal
Senior Member
 
Join Date: Mar 2008
Posts: 3,708
Default Re: Whats the average amp draw from a small welder?

Quote:
Originally Posted by terabyte View Post
my 185 amp tig and 175 amp mig both only need 30 amp each.
i believe 10-3 is good enough as long as its a reasonable run and copper
Why spend the dough for a extra wire? It's a 240V load & welders do not require a neutral.
Norcal is offline   Reply With Quote
Old 09-18-2010, 10:08 PM   #4
terabyte
Senior Member
 
terabyte's Avatar
 
Join Date: Apr 2006
Location: Southwest Ranches, Florida
Posts: 690
Default Re: Whats the average amp draw from a small welder?

Quote:
Originally Posted by Norcal View Post
Why spend the dough for a extra wire? It's a 240V load & welders do not require a neutral.
you need a white a black and the neutral\ground don't you?
terabyte is offline   Reply With Quote
Old 09-18-2010, 10:15 PM   #5
Norcal
Senior Member
 
Join Date: Mar 2008
Posts: 3,708
Default Re: Whats the average amp draw from a small welder?

Quote:
Originally Posted by terabyte View Post
you need a white a black and the neutral\ground don't you?
Ground & a neutral are two different things. A 2 conductor w/ ground NM cable is fine, just have to reidentify the white conductor as a hot...
Norcal is offline   Reply With Quote
Old 09-18-2010, 10:18 PM   #6
terabyte
Senior Member
 
terabyte's Avatar
 
Join Date: Apr 2006
Location: Southwest Ranches, Florida
Posts: 690
Default Re: Whats the average amp draw from a small welder?

Quote:
Originally Posted by Norcal View Post
Ground & a neutral are two different things. A 2 conductor w/ ground NM cable is fine, just have to reidentify the white conductor as a hot...
i really need to fully learn this stuff.
thank you for the heads up.
sorry to the OP for steering you wrong
terabyte is offline   Reply With Quote
Old 09-18-2010, 10:19 PM   #7
terabyte
Senior Member
 
terabyte's Avatar
 
Join Date: Apr 2006
Location: Southwest Ranches, Florida
Posts: 690
Default Re: Whats the average amp draw from a small welder?

just for the record. for a 240 welder you do need a 3 conductor wire ?
and the 3rd conductor can be slightly smaller than the other two?
terabyte is offline   Reply With Quote
Old 09-19-2010, 12:02 AM   #8
AMCguy
Senior Member
 
AMCguy's Avatar
 
Join Date: Dec 2009
Location: Sunshine Coast, BC Canada
Posts: 671
Default Re: Whats the average amp draw from a small welder?

You do not need a three conductor wire. You need a two conductor wire. The ground which is included with either, is not a conductor.

A 10-2 will have the two conductors you need and a ground. In the breaker box and in the outlet, they must be identified as black and red regardless of what color they are actually.

For very little extra. about what you would have paid for 10-3, you could upgrade to 8-2 and then you are set for a 40 amp breaker.
AMCguy is offline   Reply With Quote
Old 09-19-2010, 12:45 AM   #9
Norcal
Senior Member
 
Join Date: Mar 2008
Posts: 3,708
Default Re: Whats the average amp draw from a small welder?

Quote:
Originally Posted by AMCguy View Post
You do not need a three conductor wire. You need a two conductor wire. The ground which is included with either, is not a conductor.

A 10-2 will have the two conductors you need and a ground. In the breaker box and in the outlet, they must be identified as black and red regardless of what color they are actually.

For very little extra. about what you would have paid for 10-3, you could upgrade to 8-2 and then you are set for a 40 amp breaker.
There no code requirement that one has to identify a white being used as a "hot" red, it just cannot be white or green.

Oversizing a wire kicks in another code requirement in 250.122( B ) NEC 2008 edition.

(B) Increased in Size. Where ungrounded conductors are
increased in size, equipment grounding conductors, where
installed, shall be increased in size proportionately according
to the circular mil area of the ungrounded conductors.

The 10 AWG grounding conductor in a 8/2 NM cable will not comply with that code section.
Norcal is offline   Reply With Quote
Old 09-19-2010, 09:01 AM   #10
Boyd Who
Senior Member
 
Boyd Who's Avatar
 
Join Date: Oct 2007
Location: Manitoba
Posts: 1,081
Default Re: Whats the average amp draw from a small welder?

My electrician wired up my 3 welder plugs with 10-2 wire on individual 30A breakers.
__________________
Al Gingles
Livin' the quiet life in rural Manitoba
12 x 20 garage
20 x 22 new build!
'27 Essex pickup
Boyd Who is offline   Reply With Quote
Old 09-19-2010, 09:41 AM   #11
george4
Senior Member
 
Join Date: Feb 2006
Location: N California
Posts: 576
Default Re: Whats the average amp draw from a small welder?

My Hobart 187 mig runs fine on 30 amps. But when I picked up 225 stick I had to upgrade to 50 amps. As long as you are starting fresh, you may want to consider 50 amps. I think most welders in this range use the same plug. 6-50?
george4 is offline   Reply With Quote
Old 09-19-2010, 10:53 PM   #12
fflintstone
Senior Member
 
fflintstone's Avatar
 
Join Date: Jul 2010
Location: MOFnowhere Mi.
Posts: 2,723
Default Re: Whats the average amp draw from a small welder?

Most welders and plasma cutter, use a 50A plug. Just go with 6-2 cable and the 50A plug NOW, and you are ready for any potential upgrades
fflintstone is offline   Reply With Quote
Old 09-21-2010, 11:32 AM   #13
alecmcmahon
Senior Member
 
alecmcmahon's Avatar
 
Join Date: May 2010
Location: Woodbridge NJ
Posts: 195
Default Re: Whats the average amp draw from a small welder?

Just thought I throw this in the mix, I emailed Hobart about what they recommend for running their Hobart 210 Welder and they replied.

Quote:
The recommended circuit size is a 40 amp breaker with #8 wire for an Ironman 210 or the Handler 210.

Regards,

Keith McQuown
Manager, Technical Support

Hobart Welding Products An ITW Company
600 W. Main St.
Troy, OH 45373 USA
1-800-332-3281 Office
1-937-332-4804 Fax
keith.mcquown@hobartwelders.com
www.hobartwelders.com
Please consider the environment before printing this email.





-----Original Message-----
From: xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx
Sent: Monday, September 20, 2010 5:12 PM
To: INFO-Hobartwelders
Subject:
---------------------
What size breaker and wire is required off a garage sub panel to safely run the Hobart 210 Welder?
alecmcmahon is online now   Reply With Quote
Old 09-22-2010, 12:13 PM   #14
mefarri
Member
 
Join Date: Jun 2009
Posts: 55
Default Re: Whats the average amp draw from a small welder?

I checked my Lincoln 180MIG and Miller Econotig and the lincoln calls for a 40amp and the Miller for an 80.
mefarri is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Sponsored Links (Register now to hide all advertisements)


All times are GMT -5. The time now is 07:39 AM.