100 amps to shop. What wire size?

xbanone

Well-known member
Joined
Aug 1, 2008
Messages
63
Location
West Virginia
I just had an electrician install a 200a service upgrade to my house. I would like to run a 100 amp feed to the new shop. I have a 100a panel in the shop and will have to go about 100-120 feet distance underground. What cable do I need to ask for at the electrical supply house? I will have 3 conductors and a ground. #3 THHN? What should I expect to pay for copper?
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
For a feeder the #2 Al is good to 90A not 100A. #2 Al used as service entrance carrying the whole load to a dwelling can be used at 100A. That chart is for 3 wire service entrance. You are doing a 4 wire branch/feeder circuit, which is a different chart/table. It's a NEC thing. If you can be happy with 90A use Mobile Home Feeder 2-2-2-4 or 2-2-4-6.

http://www.southwire.com/products/MobileHmFeeder.htm

The #2 is fine for the 120', it will be less than 3% at 90A @ 75C.
 
Last edited:

Gary S

Well-known member
Joined
Dec 27, 2008
Messages
2,972
Location
Bismarck, ND
I ran #2 copper to my garage. Menards didn't have #3 in stock and the other vendors in town wanted more for #3 than I paid for #2 at Menards. It handles the 100a breaker with room to spare.
 

mrjaw14

Well-known member
Joined
May 22, 2012
Messages
1,958
Location
Nashville, TN
I did a similar project earlier this year and was wanting #4 Cu thhn/thwn, but the cost of #2 Al XHHN was literally about half of what it was going to cost for Cu. I did the entire project for the cost of what #4 Cu would have been.

90A breaker > 4 cond AL to a subpanel in detached garage (on 100A "main disconnect")

I had a single 15A circuit prior to this but anything with a motor would heat up really quickly, voltage would drop to around 100 VAC, it was horrible. Things are much happier now that I have an actual sub panel setup. V-drop is next to nothing under the same loads I was putting on it before.
 

'04 Cummins

Well-known member
Joined
Jul 14, 2012
Messages
137
Location
MD
Just got a price from local electric supply. #2 copper is 1.37 per foot. Menards is 1.89.

Wire other than romex is where the supply houses have the box stores beat by a mile. Panels and breakers usually seem to be cheaper at HD, Lowes, etc. YMMV
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
Just got a price from local electric supply. #2 copper is 1.37 per foot. Menards is 1.89.

#2 AL mobile feeder is running about 1.80/ft. That's a 4 wire cable - not a single wire. It's what I used for mine - it was 1.47/ft when I bought it. I fused my 100A panel at 75A in the panel at the meter.

Error - 70A is what's in the can.
 
Last edited:

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
#2 AL mobile feeder is running about 1.80/ft. That's a 4 wire cable - not a single wire. It's what I used for mine - it was 1.47/ft when I bought it. I fused my 100A panel at 75A in the panel at the meter.

Where are you finding 75A fuses or circuit breakers? 75 is not a standard size, 70A is.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Most economical is 1/0 al SER.

That would be okay, except for the fact that SER can't be run under ground.


338.12 Uses Not Permitted.
(A) Service-Entrance Cable. Service-entrance cable (SE)
shall not be used under the following conditions or in the
following locations:
(1) Where subject to physical damage unless protected in
accordance with 230.50(B)
(2) Underground with or without a raceway
(3) For exterior branch circuits and feeder wiring unless
the installation complies with the provisions of Part I of
Article 225 and is supported in accordance with 334.30
or is used as messenger-supported wiring as permitted
in Part II of Article 396
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
Error - its a 70. 220,221 - whatever it takes ;)

It was in stock and plenty big enough IMHO. I worked out here all day yesterday, cut some stuff on the lathe, built a mobile stand for the handsaw- bet I didn't pull 10~15A peak all day.
 
Last edited:
To avoid these ads, REGISTER NOW!

fnsane

Active member
Joined
Jul 28, 2012
Messages
40
Location
Alabama
Ok, we have an inspector monitoring this thread. So, pipe it with 1 1/2" pvc, pull 3 1/0 al XHHW and 1 #6 XHHW and you are compliant.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
Ok, we have an inspector monitoring this thread. So, pipe it with 1 1/2" pvc, pull 3 1/0 al XHHW and 1 #6 XHHW and you are compliant.

No your not, when you upsize ungrounded conductors you run into the requirements of 250.122(B).

(B) Increased in Size. Where ungrounded conductors are
increased in size, equipment grounding conductors, where
installed, shall be increased in size proportionately according
to the circular mil area of the ungrounded conductors.

Copied from the 2011 NEC.

That section overrides the normal grounding conductor sizing table.
 

Dave Maxwell

Well-known member
Joined
Sep 21, 2011
Messages
865
Location
Kickapoo illinois
Supplier says #2 copper. My electrician says too small. Should be 1/0 atleast. Run 2/0 and be done. Om getting lost. 100 amp house to garage. Underground in conduit. 250 foot
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
The 250' is whats killing you. To get the full 100A at 3% or less voltage drop you do need at least 1/0 Cu or 3/0 Al.

Supplier says #2 copper. My electrician says too small. Should be 1/0 atleast. Run 2/0 and be done. Om getting lost. 100 amp house to garage. Underground in conduit. 250 foot
 

Dave Maxwell

Well-known member
Joined
Sep 21, 2011
Messages
865
Location
Kickapoo illinois
Dave, calculating the wire size is pretty basic, the challenge is fitting it into the existing lugs of the breaker in your house panel and the lugs of the breaker in the additional panel in your shop. We stock a 2/0- 3 conductor direct bury underground aluminum for this application. Cost is $2.55 per foot.
that is from another supplier.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Dave, I'd say drop your load amps to 90 and go with the 2/0 Al and use a 90A breaker in your main panel. Using 2/0 Al at 90A for 250' you should be right at a 3% volt drop. Also make sure you get 4 conductor (2 hots, 1 Neutral, 1 Ground). Such as 2/0-2/0-2/0-1 or 2/0-2/0-1-4. Otherwise you'll need to use 1/0 copper ($$$) to get it to fit the breaker at 100A. I believe a 100A breaker will take up to a 2/0 wire.
 
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
That will work. The 2/0 Al at 100A for 250' will give you a 3.33 % voltage drop which is not too bad. The supply house doesn't have any aluminum wire you could run for the ground? I'm surprised they don't have any 2/0 Quadruplex or 4 wire URD. They can't order it for you?

Edit: If you add your own ground to the three wire cable you will need to mark it as a ground by wrapping the ends where terminated with green tape.

Figures. Supply house has the 2/0 aluminum in a 3 wire. Then they have a #4 copper for ground. Sound good for my 100 amp run
 
Last edited:

forced induction

Active member
Joined
Aug 16, 2012
Messages
28
Location
NJ
I am running 3-#2 and 1-#8 THHN in 1-1/2" PVC conduit running 50' to a 100A sub panel in my detached garage. I didn't think you could use #4 and get away with 100A.
Hope to complete this project soon. Great thread guys and great site!!
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
If you're commenting to my post, the 4 wire URD is the number of conductors not the size. The size was 2/0. I was not very clear with the wording.

Also, are the #2's and #8 you used for 100A, copper? I also so assume the THHN you used also carries the THWN rating.

I am running 3-#2 and 1-#8 THHN in 1-1/2" PVC conduit running 50' to a 100A sub panel in my detached garage. I didn't think you could use #4 and get away with 100A.
Hope to complete this project soon. Great thread guys and great site!!
 

forced induction

Active member
Joined
Aug 16, 2012
Messages
28
Location
NJ
Yes all my conductors are copper. And yea accd to nec THHN and THWN have same rating. I don't have the cable yet but should arrive today. My #8 is actually gonna be XHHW. I wanted to try that wire type. I bought all my #2's color coded black, red, white. But only black and green was available in XHHW in 2ga size so I stuck with the THHN. At the 8 ga size they have all colors.

That's for explaining your post sorry on that I went back and reread it also.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
THHN and THWN are not the same ratings. THHN is for dry locations and THWN is for wet locations. Most if not all wiring today that is THHN also carries the THWN rating too. I asked just to make sure the wire you have was not just THHN only. There's no question about the XHHW being suitable for wet locations.

Yes all my conductors are copper. And yea accd to nec THHN and THWN have same rating. I don't have the cable yet but should arrive today. My #8 is actually gonna be XHHW. I wanted to try that wire type. I bought all my #2's color coded black, red, white. But only black and green was available in XHHW in 2ga size so I stuck with the THHN. At the 8 ga size they have all colors.

That's for explaining your post sorry on that I went back and reread it also.
 

forced induction

Active member
Joined
Aug 16, 2012
Messages
28
Location
NJ
The amapcity rating is the same (as far as I can tell). The application of each is different I agree completely. I just got my wire in today and it is THHN and THWN-2 approved. I also really like the jacket on the XHHW. Nice wire. I might start the install tomorrow but don't know if I will get to it. Thx again for all the help.
 
OP
X

xbanone

Well-known member
Joined
Aug 1, 2008
Messages
63
Location
West Virginia
For a feeder the #2 Al is good to 90A not 100A. #2 Al used as service entrance carrying the whole load to a dwelling can be used at 100A. That chart is for 3 wire service entrance. You are doing a 4 wire branch/feeder circuit, which is a different chart/table. It's a NEC thing. If you can be happy with 90A use Mobile Home Feeder 2-2-2-4 or 2-2-4-6.

http://www.southwire.com/products/MobileHmFeeder.htm

The #2 is fine for the 120', it will be less than 3% at 90A @ 75C.

So, mobile home feeder @ 2-2-2-4 or 6 with a 90A breaker should work fine for me. I would like to run it through conduit, what size would you suggest?
 