Banjorear
Well-known member
Curious how many high output T-8's I can daisy chain together on the same 15A run?
You need to get the amp draw off the label of the ballast. The total amps should be no more than 12 amps for a 15 amp circuit. That's 80%. Example, if the fixtures pull 1 amp each then 12 fixtures is max on a 15A circuit.

OK, makes sense. I know just enough about electricity to get myself into trouble.![]()
I use the formula Volts x Amps = Watts or 120V x 15A = 1800Watts. If you want to run at 80% capacity that would be 1440 watts.
So it would support 14 100 watt fixtures, or 24 60 watt fixtures. I believe this is the same logic pattenp is using, just stated a little differently. In his example I assume the .7 amp lamps consume 84 watts to arrive at the 17 fixture capacity.
One thing I have wondered with this formula is with the new LED and CFL lamps it seems you can run quite a few more fixtures than with incandescent. As long as you are not switching back to higher wattage lamps you should be okay?
I use the formula Volts x Amps = Watts or 120V x 15A = 1800Watts. If you want to run at 80% capacity that would be 1440 watts.
One thing I have wondered with this formula is with the new LED and CFL lamps it seems you can run quite a few more fixtures than with incandescent. As long as you are not switching back to higher wattage lamps you should be okay?
Thanks pattenp, I did not know that about fluorescent ballasts. I suppose in general it's a good idea to measure circuit load in amps since watts is more of light bulb measurement and does not apply readily to other devices like garage door openers.
In my case my lights are on the same circuit as the garage door opener so assuming a 3/4 hp opener draws 5 amps (not sure what it draws) I only have 10 left over and just 7 with 20% cushion factor. Thanks again!
Thanks for the clarifications 2ManyProjects.
The info on the opener says 5 amps so that's what I'm using in my load calcs for this circuit.
It would be nice to have a separate circuit but that's not happening any time soon. Our box is in a weird spot in a finished area, I think it would cost quite a bit to add circuits. Maybe if I really need more power I could look into adding a subpanel or something some day but for now the opener will need to share a 15amp circuit with lights.
I'm not debating the photographic evidence; but SOMETHING is not adding up there. I strongly suspect that either Sears is fibbing about the "3/4 HP" figure, or that the "5.0 AMPS" figure refers only to constant running load, as opposed to start-up load and/or LRA, or both.
Why are you saying Sears is fibbing about the 3/4HP?
Unless I'm having brain freeze 3/4HP is 4.66A @ 120V. 1HP = 746W.
I'm sure it's just running load.


Well first, I did say "suspect" and "either/or", as I'm really not sure what is going on with that particular device. But as for why I suspect the figures may be bogus (or at least not telling the whole story)...
Purely in terms of unit-conversion, sure. But when was the last time you saw a 100%-efficient electric motor? And of course, there remains the issue of the start-up/LRA load, which would presumably be several times that.
That would be more plausible. But if so, I remain a little surprised that this would be the ONLY current rating on the data plate. Then too, putting "3/4 HP" on the data plate is also a little puzzling. If it were just a matter of some flashy "advertising" label, I would be quicker to dismiss it. OTOH, if that data plate were for the motor itself (as opposed to the unit as a whole), I'd take it a bit more seriously. As it stands, its "credibility" is somewhere between those two extremes. And overarching ALL of this would be my reluctance to underestimate the power of the Sears marketing department, particularly in the context of their dealings with a "captive" OEM vendor (who could presumably be rather easily strong-armed into putting whatever numbers on that plate that Sears told them to put on that plate).
Bottom line: