Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,164
Location
Minneapolis
400/240 isn't a voltage combination used in the US, plus residential three phase here is uncommon, but the principles of three phase power are going to be the same regardless of voltage so I think your knowledge would be welcome.
 

RPH

Well-known member
Joined
Dec 17, 2006
Messages
4,190
Location
Michigan Thumb
Go with MB. The math maybe complex but the principles are the same. I personally enjoy reading about It, keeps the mind sharp.
Plus if you go to Canada you may find uncommon voltages in the same plant. Depends where it’s fed from.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,052
Location
NJ
240X1.732 is actually 415, why is it called 400?
110, 115, 117, 120,........220, 221!, 230, 240..........standards morphing over time. And of course, technically "loose" speak. Just like 440, 460, 480v is used in US.

In 1995, the prevalence was 220/385V for equipment I was installing in EU. I believe the working range is 385 - 415v today.
 
Last edited:

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,052
Location
NJ
Line - Line voltage will alway be 1.732x the Line -neutral voltage or visa-versa using 1/1.732 for the simpler case of WYE systems.
 
Last edited:

Steve from Socal

Well-known member
Joined
Jan 27, 2009
Messages
3,510
Location
Hutchinson Ks.
I am looking at setting up some machinery in South America where 230/380 is still listed as power. Getting more info on the European 50 cycle network would be useful. A number of my machines use VFD's that are able to use 380/50Hz as well as some DC drives.
 

Snapped-off

Well-known member
Joined
Feb 22, 2012
Messages
4,812
Location
Indiana
400/240 isn't a voltage combination used in the US, plus residential three phase here is uncommon, but the principles of three phase power are going to be the same regardless of voltage so I think your knowledge would be welcome.
Yeah as stated, 415/240 can be commonly found in data centers. Trips people up when you talk about 240v with 1 hot and 1 neutral.
 

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,992
Location
Peace Valley,mo
St. Louis area in commercial buildings and industrial
208 3 ph
230 3 ph center tap grounded and ungrounded
240 3 ph
277 3 ph
480 3 ph both wye and delta can have 277 to ground or 480v leg to leg
4160 3 ph If you like to screw with your help 500 ton chiller pulls 65 amps fla a 480 v 100 hp pump might be 125 amps and ask them why.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,071
Location
Modesto, CA
St. Louis area in commercial buildings and industrial
208 3 ph
230 3 ph center tap grounded and ungrounded
240 3 ph
277 3 ph

480 3 ph both wye and delta can have 277 to ground or 480v leg to leg
4160 3 ph If you like to screw with your help 500 ton chiller pulls 65 amps fla a 480 v 100 hp pump might be 125 amps and ask them why.
why would you have both 230v and 240v 3Ø delta? thats just odd

also are you saying you have 3Ø 277v line to line?
 

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,313
Location
Dutzow Missouri
why would you have both 230v and 240v 3Ø delta? thats just odd

also are you saying you have 3Ø 277v line to line?
I do not think Fitter30 is saying you will find them in the same building but if you visit a few dozen old industrial building you are likely to find all the flavors mentioned.

The only difference between 230 and 240 with a grounded corners is if the transformer on the pole was manufactured before or after 1965 or so.

A lot of 277V finds its way into industrial lighting circuits as part of the 480 V 3P .

Walt
 

Attachments

  • 2024-05-03_19-23-34.jpg
    2024-05-03_19-23-34.jpg
    20.6 KB · Views: 5
Last edited:
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,071
Location
Modesto, CA
I do not think Fitter30 is saying you will find them in the same building but if you visit a few dozen old industrial building you are likely to find all the flavors mentioned.

The only difference between 230 and 240 with a grounded corners is if the transformer on the pole was manufactured before or after 1965 or so.

A lot of 277V finds its way into industrial lighting circuits as part of the 480 V 3P .

Walt

he listed the 277v as if it was a separate service. thats the point i was making

yes i know you get 277v line to neutral on a 480Y/277v service. Ive never seen or heard of a service that is strictly 277v

corner grounded delta is a rare beast. we have a few here in town.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,052
Location
NJ
The OP, who's listed location is Sweden, offers a thread about 3 phase 400/240 service.

20 posts in and we're already bickering about 400/240 isn't a US voltage, and what voltages are available in St. Louis
You expected anything less :lol_hitti

BTW, Alfred started it back in post 6!! :twak:
 
Last edited:

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,052
Location
NJ
If people can look past the voltages mentioned :)argue:) and ignore the 50Hz, many "split-phase only people" can learn something new. The wiring methods and hardware alone will be an eye-opener for some.
 
OP
M

MBfreak

MEMBER EMERITUS
Joined
Dec 10, 2010
Messages
2,301
Location
Linkoping , Sweden
Hello to all.
I have zero professional knowledge of many inputs above, that relates to US voltage levels and also a rather peculiar way to connect a delta winding.
Please understand my shortcomings.
What I do know are most theoretical and technical aspects of European and Asian electrical power systems from the largest nuclear power stations to installation practice in a small flat.
I will restrict all my input to three phase power systems from 24 kV and below.

The three pase technology actually was mainly invented by Nikolas Tesla, US citize, together with maybe 4 other people in Russia and Europe,
Mr Tesla gave his patent rights to Westinghouse, saving that company from bankcrupcy.

Ola
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,881
Location
Richmond, VA
Hello to all.
I have zero professional knowledge of many inputs above, that relates to US voltage levels and also a rather peculiar way to connect a delta winding.
Please understand my shortcomings.
What I do know are most theoretical and technical aspects of European and Asian electrical power systems from the largest nuclear power stations to installation practice in a small flat.
I will restrict all my input to three phase power systems from 24 kV and below.

The three pase technology actually was mainly invented by Nikolas Tesla, US citize, together with maybe 4 other people in Russia and Europe,
Mr Tesla gave his patent rights to Westinghouse, saving that company from bankcrupcy.

Ola
Ola, you owe no one any apologies. Your input here has always been valuable and interesting. Please do share, we'd love to hear it
 

Racer_X

Well-known member
Joined
Jun 25, 2007
Messages
367
Location
MI
I'd find a thread about six phase more entertaining and educational than three phase.
 

cannuck

Well-known member
Joined
Nov 30, 2021
Messages
4,656
Location
Rural SK
Plus if you go to Canada you may find uncommon voltages in the same plant. Depends where it’s fed from.
The only voltage at the consumption level you will find here different from USA is 575/600 - common to some industrial use in EU IIRC. 480 is still very common in older buildings and very common in the oil patch since so much of our equipment is from USA and it was once "normal" industrial here. Walk into my storage shelter and you will find some 415 - once again from "outside" equipment from EU (I have such a transformer to run one mill and lathe) but you would have to do it the same way in US (i.e. transform voltage).

Where it gets a fair bit different is in transmission voltages. We used to be 72Kv in rural SK, while next door in MB they were 69Kv. Some places are the even multiple 138, others are 130. Longer regional AC is often 230Kv so tying to US where 345 is more common requires a conversion link. We do 460Kv and 500Kv DC - and you can see THEY don't even match up. I think Quebec has some 1Gv DC. I couldn't even BEGIN to list the distribution voltages I have seen across North America. We are now all 60Hz (I think the last 50Hz system out of Niagara Falls NY closed a while back, but NYC subways ran some 25Hz until 20 years ago). In other words: while consumers here see almost exclusively 120/240 single phase AC buying industrial stuff at the end of the wire can be 208/230/460/575 so not too bad, but the medium and high voltage stuff is a nightmare of incompatability.

So please don't hesitate to tell us what voltages, phases and frequencies you use in ANY other place. Fascinating subject.
 

cannuck

Well-known member
Joined
Nov 30, 2021
Messages
4,656
Location
Rural SK
You mean megavolt, correct? I can find some references to >1,000Kv distribution online but not >1,000,000Kv.
Oooops, what's a 1,000 x error between friends? Yes, MV. I am the HV mechanical guy, not one of the sparkies.
BTW: my good friend/former JV partner in that business saw the 1.1MV unit in China that is I think the highest voltage transformer EVER built. At that voltage the bushings (insulators that take power into the tank) are beyond belief. The limit for building most stuff at such extremes is having a test facility that can vaildate bushing and lightning arrestor designs. I assume China has such a facility - one huge advantage of not relying on legacy facilities and equipment to move forward.
 
Last edited:

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,881
Location
Richmond, VA
Oooops, what's a 1,000 x error between friends? Yes, MV. I am the HV mechanical guy, not one of the sparkies.
BTW: my good friend/former JV partner in that business saw the 1.1MV unit in China that is I think the highest voltage transformer EVER built. At that voltage the bushings (insulators that take power into the tank) are beyond belief. The limit for building most stuff at such extremes is having a test facility that can vaildate bushing and lightning arrestor designs. I assume China has such a facility - one huge advantage of not relying on legacy facilities and equipment to move forward.
All good. 1Mv is still mind blowing
 

cannuck

Well-known member
Joined
Nov 30, 2021
Messages
4,656
Location
Rural SK
All good. 1Mv is still mind blowing
I have worked on a fair bit of 460 and a bit of 500. Primary bushings for the latter arrive one per semi and you really don't want to drop or chip one (I am, er WAS usually the person doing the rigging - mostly retired now....as I sit here printing out the PO for a job next week).
 