    Two double gangs side by side?

    Conduit ******?
  2. 2

    Surface mounted boxes/conduit for shop power?

    I'm in the middle of wiring my shop. I ran EMT from the panel up to 8', then ran MC cable to J-boxes. Dropped down with EMT to 4"square device boxes, at 52". Tried to avoid horizontal runs on the lower walls.
  3. 2

    PVC Conduit under deck

    Another question (forgot to ask inspector). Should I have rough-in before pulling wire in conduit? In case there's a problem with trench? I'd hate to have to move 2" conduit full of wire. Today's Sunday, last chance to get help with pull.
  4. 2

    PVC Conduit under deck

    Great ideas, thank you. I will bury conduit under deck. Deck is composite material, flaking and chipping. It'll be next project.
  5. 2

    PVC Conduit under deck

    I'm installing a subpanel in a detached garage. Individual conductors in 2" PVC conduit. The shortest path would be from main panel into crawl space, then exiting building through LB under a deck built on grade. My question is - Does conduit need to be buried while under the deck? If so,I...