Jake, surprised to see you on here... build is coming along very nicely. Can't wait to see it come to fruition.
Hope you are going to have a garage/house warming party when its all done!!!
^ yes, I did confirm it was wired for max output.
I went to Lowes today and picked up a 5kw/ 17k btu heater for $198. Its made in the USA by a company called KING, lol. Its a good bit smaller and lighter than the Fahrenheat unit, but I just wanted something to test and see the output...
contacted Blain's farm & fleet where I purchased the unit and they were very quick to offer a pre-paid return shipping lable. I'll be sending it back this weekend and hopefully getting another one.
thanks to everyone for the input.
just switched the two white and black wires but felt no change in heat output.
I checked the voltage at the breaker and at the heater terminals while the unit was on/off. no change... reads 238-239v.
I don't have a red wire, unless you mean the red from the 6/3 I have coming into the sub panel. I'm running 10/2 from my sub panel/breaker to the heater. The black wire of the 10/2 goes to one leg of the heater and the white wire goes to the other. the cooper wire is to ground...
maybe I'm...
thanks for the replys.
Colardotrailrider, I was thinking of another heater I bought and returned when i typed the 13k btu, this one is 17k btu.
I measured the voltage at the unit this morning and it is seeing 120v on each leg/240v total. next step is to get a thermo and see what the temp...
Based on much research from this forum I went with a Fahrenheat 5kw/13k BTU heater to heat my 300sf half insulated detached garage (walls are insulated and covered with 3/8" paneling, but 8' ceiling is not insulated). I read many threads from people with much larger garages than mine having...