Recent content by billsr4

  1. B

    Garage door dilemma (new construction)

    use a roll up door instead of an overhead type.
  2. B

    Anyone have a Dual Ramp (4 car) 4 post lift

    I have the gemini called a common column. you can raise and lower each car seperately. You can reach Sam at 800-235-6932. They delivered and installed my lift.
  3. B

    Air line question

    you can use 3/4 pvc rated a 350 psi and its a lot easier to work and a lot cheaper.
  4. B

    Question for a lineman...

    Most of your 167.5 kva and some 100 kva transformers will have 4 secondary bushings . You can make up your taps on the outside with jumper wires and have a delta 120/240 volt or a 120/208 volt secondary. A 120 / 208 volt secondary is going to give you the full kva rating from each tansformer at...
  5. B

    Question for a lineman...

    The winding in a standard 12/240 volt tranformer are as follows: 2 sets of windings A------ B C--------D 120/240 VOLT A= 120V B&C TIE(CENTER BUSHING) NEUTRAL D =120 VOLT 120/208 VOLT A&C TIE 120 VOLT B&D TIE NEUTRAL YOU WILL END UP WITH 1 BUSHING NOT USED AND THIS...
  6. B

    Adding a Switch to the "Street" Lamp in my Backyard

    ask them to replace the shade with a metal one ,this will make the light shine down and in a 360 degree pattern. Photo cell catches the light from the side not the top.
  7. B

    Info on lifts

    Gemini lifts are American made in Texas. Great people to deal with.
  8. B

    Chinese fingers question

    If the line has tension on it you will need an automatic tension splice. The H tap will work if u don't tension on it.
  9. B

    Torque Spec

    You may want to use a pin connector ,just crimp it on the aluminum and install it in the lug . it will solve any loose connection issues. BURNDY HYPLUG AYPO4/0 Made for alum wire to be connected to a mechanical lug.
  10. B

    Busted my Grandads Elora Rachet.....

    http://www.bloomertool.com/Ratchets.html This web site shows a repair kit for an elora ratchet
  11. B

    Uses for 4AWG AL from OH drop?

    sounds like #4 triplex ,used by the power co. for service drop .
  12. B

    Running Low Voltage in conduit?

    You can pull cat 6 outside plant cable and use it in place of your telephone and coax cable. There is a connector to go from cat 6 to coax. I can get the name if you can't find it . I run my cameras mounted on the garage the the house with these.
  13. B

    Frustrated with Fluorescent!

    Try cleaning the tubes with a damp rag and dry them before reinstalling them. Sometimes the dust and dirt will keep them from lighting.
  14. B

    Electrical and cable lines?

    If they are in a designated right of way or servitude you may not be able to move them. Once the utilities have a right of way it hard to get them to release it. If the lines are only feeding your house and not going anywhere else they will probably move them without any problem.
  15. B

    PG&E service upgrade?

    The power co around here will use #4 triplex for a 100 amp service and a 1/0 for 200 amp. The triplex is aluminum conductors and is in free air so the rating is higher. I have a 3200 sq ft house and 2 garages with a total of 11 tons of a/c and the rest of the house is total electric . The...