    Radiant in floor heat system help

    Just checked on the shop, its still -1 but holding with the water heater constantly on. Not bad I suppose, considering it was -15c overnight. I noticed the pressure on the system is 0psi. I believe when the system was off it was at 12PSI which is what I precharged it to at the start of the year...
  2. D

    Radiant in floor heat system help

    Alright just took the water heater timer off. I confirmed that both elements are not running simultaneously, I can’t run both with my breaker and wiring unfortunately. Also noticed each loop is running 0.4 gpm and the temp coming out of the heater is 16c and coming back is 14c.
  3. D

    Radiant in floor heat system help

    I was looking at the navien, rinnai or IBC combo units (I also have a 20 gallon DHW heater I’d like to get rid of), in the 120-150k BTU range. As you mention they modulate down, it’s my understanding it won’t be a waste of energy and it has capacity if I want to crank it up for a day to heat the...
  4. D

    Radiant in floor heat system help

    Hi guys, We moved into a new place a little while ago and the shop in floor heat does not heat the shop up past 4ish Celsius when it’s -10 to -15 c outside. The shop is 48’x28’ interior, 12’ ceilings, gambrel roof with upstairs, 6” roxol in the walls downstairs, 4” fiberglass in the gambrel...