The CHP50 charger has a configuration for "208/240V AC 60Hz single phase @ 16A, 24A, 32A, 40A, 48A, 50A".
Based on what you guys are saying 48Amp config will work well with 60Amp breaker.
This is in the charger which is at the other termination point. It states to use 90C copper conductors. Does this mean termination point is rated at 90C? Obviously the 60Amp circuit breaker in the box is rated at that as well.
I'm finding different answers talking to different electricians and doing my own research reading code books so I'm positing here.
I have 110 feet of 6/2 Metal Clad wire running to my garage (wire is routed completely indoors). The wire is hardwired into a Chargepoint charger CHP50 installed...