Recent content by Flexia

  1. F

    Radiant closed loop pressure shot up

    Hello all. Please help diagnose my closed loop system. I have a navien boiler and my pressure shoot up to over 35psi the other day and the relief valve opened. The boiler does have an auto fill valve that I am wondering if it is stuck open. Has anyone seen pressure shoot up? Usually it operates...
  2. F

    picts of your in-floor heat set ups.

    Most thermostat cannot handle the 120v load of the pump. So you need to taco controller to turn the 120v pump on. The thermostat calls for heat and tells the pump controller to turn the pump on. Basically the controller is a big relay to handle the pump on and off. Sent from my Pixel XL...
  3. F

    Lets see your workbench

    Doorfx I wouldn't screw it down either. It should stay just fine with some silicone caulk under it. Sent from my Pixel XL using Tapatalk
  4. F

    Lets see your workbench

    They are asking 1500. And the guy I talked to has them shipped in. It would be awesome if you could look closer at them one day. I was planning on doing a steve-o bench with 2 hb44 box's so by the time I get all the material il be close to the money of the China bench. Plus it saves me a lot...
  5. F

    Lets see your workbench

    http://www.haylite.com/en/product/Work/index.html That's who seems to be manufacturer. I found a few importers but Im in the same boat. I don't have space or time to deal with import. It would be cool if someone did a group buy that had the the time and space. And of course, close to me.
  6. F

    Lets see your workbench

    Has anyone ever seen or bought one of the 10ft workbench imported from China? They seem to be floating around on Craigslist. I'm considering one of them but they are over 2 hours away and would like to know the quality before I go out there. These are what I'm talking about
  7. F

    HF Toolboxes Workbench - Phase 3

    Hey Steevo, not sure if you mentioned this at all but do you have any issues with not having any support in the direct corner when placing heavier items in the corner? It seems the very corner is just supported by cantilever and am thinking about adding a support under it. Thoughts?
  8. F

    Help! Secondary pump isn't kicking on!

    Just to update you guys. I used the external power term on the navien to flip a small 120v relay that then will bridge the TT on the taco relay. It works for me but is an extra step. You could get a bigger 120v relay that will get triggered from the boiler to power the pump. But I already...
  9. F

    Help! Secondary pump isn't kicking on!

    Yes the navien remote can act like a thermostat. Has temp sensor and is programmable too
  10. F

    Help! Secondary pump isn't kicking on!

    When I got home today I put my multimeter on the cn26/ external power. It does throw 120v out when the primary pump in the navien in on. I'll prob make a relay that will flip from that 120 and then it will bridge the R&W when flipped.
  11. F

    Help! Secondary pump isn't kicking on!

    That's not the problem. I can bridge the R&W on the taco to start the pump. The problem is the boiler isn't telling the taco really when to turn on
  12. F

    picts of your in-floor heat set ups.

    Finally got mine mostly done. Still have to add drops for the T&P and condensate drain. Using the combi boiler with outdoor reset.
  13. F

    Help! Secondary pump isn't kicking on!

    There is a relay its just sealed on the board. Here is the ladder. I was thinking about making a relay to hook the the pump wire to trigger the taco relay
  14. F

    Help! Secondary pump isn't kicking on!

    Here is the diagram thats in the manual.
  15. F

    Help! Secondary pump isn't kicking on!

    I have tried that and the navien still doesn't send a trigger to the pump relay