    Wiring for 9k btu mini split

    Yes, I was originally thinking of plugging in to the inside outlet for 6' then tying into the uf solid core (12-2 , I originally said 14-3 but counted the ground) at the point the rest of the 'stuff' goes thru the wall and down 25'. Got some good pointers from this forum and some info to chew on.
  2. F

    Wiring for 9k btu mini split

    good idea and less cable being run.
  3. F

    Wiring for 9k btu mini split

    Instead of the plug, I have been looking at white primed (paint to match) metal raceway channel & receptacle box where I would be able to run the #12/uf directly and wire it there, would look better than the plug and more permanent.
  4. F

    Wiring for 9k btu mini split

    Yes, it's a 20 amp circuit. I was thing of running a ground so was thinking of 14/3. There isn't anything on the circuit except for a small table lamp but will flip the breaker and double check that to be sure. We have a central vac so the plugs in the room are seldom used. Thanks for the input...
  5. F

    Wiring for 9k btu mini split

    Yes, these are small rooms, I currently use a 9kbtu window unit and that cools perfectly.
  6. F

    Wiring for 9k btu mini split

    Hello, I have combed the forums and did not see any similar questions- I am looking to wire a 9000btu minisplit that draws115v/7-8amps. It's a big house (3 levels, 6k square feet) so nothing is nearby in terms of the 2 electrical breaker boxes. My question is, rather than get a portable ac that...