Copy that! And yes, yes I am. I’m considering whether the run is short enough to hand bang it out, or if I should just rent a trencher. My brother my have access to one, but we’re waiting to see if it’s cool.
Understood. Thanks so very, very much for all your help!!! I’m super stressed about getting this done, and getting it done on our very limited budget. At the end of the day it absolutely has to be done right, but I always try to do it without going broke!!!
You guys are awesome!!! Can I do a single ground rod at the outbuilding, or does nec say I need two? I’m reading two different interpretations. Im also assuming 4 conductor wire back to the disconnect and leaving the sub unbonded.
I’m powering several led lamps, multiple fans and their controllers and a small radiant heater. There’s not THAT much draw when the heaters not running, and not much more when it is. Honestly, a 60A would be more than enough, I just didn’t know if it was safe to go from the bottom lugs on the...
Ha! Yes, it’s an indoor grow room, as opposed to a greenhouse. I’m up here in Montana where we need to start our garden when it’s 10’ of snow outside. Most years I have herbs and veggies year round, but I start flowers in there as well. However, and back to the point at hand, I’m currently...
Hello all! New here, so thank you for having me. I need to install a sub panel on my property to power a grow building. My Main service disconnect has a 200A breaker with nothing in the bottom lugs. I’d like to tap those lugs to supply the sub panel. There’s no real reason to have a 100A service...