    LED Light Fixtures & Garage Door Interference

    I have 2 8’ LED strip lights and 4 feit double tube hanging LED and there is no issue. I did have an issue when I put the LED in the opener itself. The range of interference is small so generally I’ve only experienced and seen people report issues when an LED is screwed into the light socket on...
  2. J

    conduit size?

    At 125 amps you’d normally use 1 gauge THHN which can carry 130 amps but based on distance you’re going to go up a size to minimize voltage loss so that is 1/0 THHN. Cross referencing the pvc conduit fill chart the first size that will carry at least 2 1/0 gauge conductors plus ground is 1 1/4”...
  3. J

    How many electrical outlets do you have

    I have two room/areas in my shop. Dual outlets, each on a separate 20 amp circuit, indicated by different colored outlets every 4’ both high and low (18” & 4’)I didn’t know where different machines were going to end up. This also kept me at the 10 outlet max per the NEC. Dual circuits are for...