What do you mean "no more than 360 degrees of bend"?
I should just be able to run from the gable on the house with a terminal adapter? straight to the side of the garage to another terminal adapter, using 2" PVC. My original question was, is it ok to do that, or does code specify a certain...
Ok, sounding better :) I'm aware of the ground rods and I've ordered the breaker to convert the main lug to a main breaker panel. Also, the intention is to 'attach' the roofs together at some stage. The real question is about running the cable between the house and the garage. Is there any...
Wait, what?? I thought the whole idea of SER cable was to be able to do this. So, I'd have to put a junction box on the gable of the house, change to a different cable and run from there to the garage? If I do that, and put a main breaker panel in, and ground rods etc. what do I need to be able...
I'm running 1-1-1-3 AL SER cable in attic space from main panel in house to Main Lug panel in a detached garage. The garage is only 3ft separated from the house. I plan to exit the house on a gable end about 10ft from ground level and span the 3ft to the side of the 10ft tall garage and straight...