Recent content by KRGaijin

  1. K

    Installing new subpanel; do manufacturer instructions supercede code?

    Appreciate all the responses and the spare wire issue is much clearer now. Thank you all for clearing that up!
  2. K

    Installing new subpanel; do manufacturer instructions supercede code?

    Agreed entirely, that's why I'm struggling a bit with making their vaguery match up with the specifics of the code. Agreed again! It's more of a "quick start guide" than an actual list of instructions to follow.
  3. K

    Installing new subpanel; do manufacturer instructions supercede code?

    Not pure reds. I was gonna use green tape to re-identify them and put a "SPARE" or "FUTURE EXPANSION" label on them. I didn't see any specific instruction in the code about how to deal with spare wires. It's my understanding that I can't leave unterminated wires in the box, so I figured the...
  4. K

    Installing new subpanel; do manufacturer instructions supercede code?

    Software. Yeah, I know I speak "engineer" instead of "english". :beer:
  5. K

    Installing new subpanel; do manufacturer instructions supercede code?

    The #8 was necessary to maintain 30A through the CCC and ambient temp deratings. As requested, here's the layout: All conduits affected by 9% ambient temperature derate Conduit 1, PVC 40, 1 1/4": 3 CCCs, #2 R/B/W. Final ampacity >=100. Conduit 2, PVC 40, 1 1/4": 8 CCCs, 2x #8 R/B/W (>=30A)...
  6. K

    Installing new subpanel; do manufacturer instructions supercede code?

    As detailed in the answer above, I now believe you're right, it appears my interpretation of the instructions was more strict than what they actually say. Sorry for the confusion, and I appreciate all you folks' patience and assistance in helping me to see my error!
  7. K

    Installing new subpanel; do manufacturer instructions supercede code?

    Thank you for making the effort to read the instructions, it's much appreciated! So, it's possible that it's an interpretation error on my part? Re-reading it, you're correct that they don't explicitly say "one ground per circuit in the conduit". I had come away from the instructions with...
  8. K

    Installing new subpanel; do manufacturer instructions supercede code?

    Right. I just went PVC because we're fairly near the coast and we get ocean water dumped on us whenever a hurricane comes through, and I didn't want to face corrosion issues. Also, thank you for all the lightning-quick replies, it's much appreciated!
  9. K

    Installing new subpanel; do manufacturer instructions supercede code?

    I would agree, I was just concerned that there might be some justification for the specifying of a ground per circuit for some reason I was unaware of. Or if there was any established hierarchy of (for example) "follow the NEC unless the manufacturer tells you to do something different". I...
  10. K

    Installing new subpanel; do manufacturer instructions supercede code?

    This is the panel at the current state of installation. I have run the aforementioned wires, #2 R/B/W and #6 G, and four 20A circuits #10 B/W/G, but they're just hanging loose at the moment. The only wires that are connected are the factory-wired red and black in the upper left, labeled L1/L2.
  11. K

    Installing new subpanel; do manufacturer instructions supercede code?

    Southeast Texas. It's a "smart" panel, an automatic transfer switch and subpanel all combined. For the purposes of the question I thought that was too many details (and yes I see the irony there!) Specific unit is this one.
  12. K

    Installing new subpanel; do manufacturer instructions supercede code?

    Sorry for all the word vomit. I try to give all the info up front, but yeah, I don't blame those who don't read it all. I understand the rule the same way you do, but... 110.3(B); I'm just asking if there's something I'm missing and any advantage to doing it the way they say? The TL;DR is: if...
  13. K

    Installing new subpanel; do manufacturer instructions supercede code?

    Hi all, I'm installing a new subpanel. The main panel is outdoors, this subpanel is indoors. Conduit is already installed (PVC, with one junction box between the panels). The conduit situation is 4 separate PVC conduits running to the junction box (2x1 1/4 and 2x1"). The wires being run are...