Recent content by Lovthebass

  1. L

    MrCool 18K Mini split wiring help

    I’m sorry I started a thread that became unpleasant. When I spoke to my electrician he said as long as it is connected to the correct sized breaker an unfused disconnect can be used. I chose to use a fused disconnect and a surge protector just in case. It works fine and was only a few more...
  2. L

    MrCool 18K Mini split wiring help

    So I finished installing the unit and it came out well. I used 8 awg wire, 30 amp fused disconnect and a 30 amp breaker. I also installed a surge protector. I must say it was very easy to install and the unit works great for AC so far. I’ll see how the heat is in the winter. Using 8 gauge wire...
  3. L

    MrCool 18K Mini split wiring help

    If l use a 30 amp fused disconnect, it shouldn't hurt right?
  4. L

    MrCool 18K Mini split wiring help

    He said if it's connected to a 30 amp breaker, a fused disconnect is not needed. And If the breaker was bigger than 30amp, then a 30amp fused disconnect would need to be used. Is he mistaken? If so, how?
  5. L

    MrCool 18K Mini split wiring help

    I spoke to an electrician friend of mine and he said the following - I can connect to the existing 8awg wire and keep going to the disconnect box. Switch out the breaker to a 30 amp. He said the disconnect doesn't matter, I can get any size unfused disconnect as long as I have a 30amp...
  6. L

    MrCool 18K Mini split wiring help

    I'm looking at this wire closer and the text on it says 8 gauge with a 10 gauge ground, sorry for the mistake. So I can add onto this with 8/2 wire the rest of the way. Might be overkill but it's already half way there. And the manual says 8 AWG is "preferred"
  7. L

    MrCool 18K Mini split wiring help

    Yes, I know i need to change the breaker. So a 30A would be best?
  8. L

    MrCool 18K Mini split wiring help

    I apologize, it is 10/2 2 wires and a ground.
  9. L

    MrCool 18K Mini split wiring help

    Last night I looked at what is there and the existing heater has 10/3 wire going to it. If I can use the existing 10/3 wire I would need to add about 25 feet. The total run would be about 45-50 feet. Right now the breaker is 50A.
  10. L

    MrCool 18K Mini split wiring help

    Can anyone help on this? I was hoping to pick up what I need soon. Thanks!
  11. L

    MrCool 18K Mini split wiring help

    Here is the label on the side of the unit-
  12. L

    MrCool 18K Mini split wiring help

    OK, I will post the label later.
  13. L

    MrCool 18K Mini split wiring help

    I have 10 gauge going to an electric heater halfway to where I would want to mount the disconnect box. I'm going to decommission the heater so can I just connect to that wire once I disconnect the heater and run it to the disconnect box?
  14. L

    MrCool 18K Mini split wiring help

    Oh, I see the reply you got from MrCool that said a non-fused disconnect was OK. What fuse size did you need to get for the disconnect? I'm glad it's working good! I'm excited to install this.
  15. L

    MrCool 18K Mini split wiring help

    Ah, I see this can get confusing. I believe you have the same unit that I have but will confirm later. So you used 12 gauge wire, 25 amp breaker & a non-fused disconnect I see. Everything seems fine? How is the unit working for you? Also, which disconnect did you go with?