Boy oh boy I feel retarded as ****, so like they always say if you need it done right do it yourself. My distance to the shop from the house is no where near 450-500' it is only 235'. That makes a huge difference in things correct? So back to the drawing board for wire size I guess. Anyone want...
So pulled the trigger and went with a 4/0-4/0-2/0-4 mobile home feeder of 500' disconnect on out side of house and go with 1/0 from disconnect to breaker in main panel of house 5-6' or so. Let the Sparks fly
Mobile home wire seems to be about the best deal around for direct burial, so here comes the next question I notice most are sized with the hot legs of same size then the neutral a bit smaller and ground even smaller. Is that all good for the shop wiring?
Thanks fellas for all the info, and appreciate all the help. Like others have said it will prolly never see full load and never experience the voltage drop and if it does I will shut something off and reset the breaker and roll with it.
Found my other thread I started and read some of this eresponses. May just drop down to 80 amp and go from there. Instead of fully taxing everything to the max now.
Thanks for these answers guys I actually started a second thread becuase I couldn't find this one. I guess in reality 100 amp is not fully needed as much as just a want. This isn't a production shop it is a hobby shop with occasional welding and fab work none of witch will be a team effort...
This is all going to be direct burial wire. Likely just go with mobile home direct burial. I get so confused because of have asked 3 different electricians and gotten 3 different answers now plus what I have gotten on here. One has told me that 1/0 is what I need and then another said 2/0 will...
So I have roughly a 450' run from my house to the new shop. I have ore wired the shop to accept 100amp service and that is what I plan to run from the house out. I know this is not the best method but it is the only one I am considering and just looking to accomplish it the best way. So here is...
Ran all electric over the weekend did 100amp service from house at a 420' run. Also put up ceiling and insulated overhead. Ran 3 rows of 7 lights all 4' led. I used Sunco shop lights and they are plenty bright during the day and even brighter at night if they hold up they are the best bang for...
I am looking at direct burial Aluminum wire. Even if I run Cooper from house breaker panel to a disconnect on outside of house and run direct burial Aluminum from there to the shop. Largest load in the shop would be a welder on occasion. Would I be ok with 2/0 wire or should I just step up to...
I have building that is 450' from my house and 850' away from my main transformer. The electric company wants 7500 bucks to install another transducer and the run a line to the shop for its own meter or they want 700 bucks to have me install a meter next to the transformer and I take care of the...