    I've got the POWER!

    I agree with you 100% if the time ever comes I can throw a 90 amp in there and walk away no harm no foul, I might even do it anyway, because I don't think I could get enough equipment in my two car shop let alone run it all at once (although I could surprise myself) to pull even 80 amps (I have...
  2. N

    I've got the POWER!

    I do agree that it is very hard to misinterpret that section of the NEC, and it probablt should be on a 90 amp breaker, I am ok with it like it is (I wont be constantly pushing 100 amps anyway). I just want to make sure its good to go (inspection wise) should I ever decide to sell. The...
  3. N

    I've got the POWER!

    Heard back from electrician after sending this message: "Got an issue with the sub panel install, according to the NEC ampacity table 310.15(b)(16) max ampacity of #2 al is 100a under the 90*c column which is for derating only and feeders serving the entire load of a dwelling. t was I...
  4. N

    I've got the POWER!

    ok i sent him an email, we'll see what happens
  5. N

    I've got the POWER!

    Copy that thank you. How does this sound? "Got an issue with the install, according to the NEC ampacity table 310.15(b)(16) max ampacity of #2 al is 100a under the 90*c column which is for derating only and feeders serving the entire load of a dwelling, so it is below spec for the sub panel...
  6. N

    I've got the POWER!

    Thank you, so I guess I need to contact the electrician.... should I just tell him "yeah some guys on a forum said its not within code..." and either "I need the breaker changed to a 90 Amp" (and a partial refund since it was contracted for 100 Amp) or "I need it rewired with the correct gauge...
  7. N

    I've got the POWER!

    Southwire voltage drop calculator: http://www.southwire.com/support/voltage-drop-calculator.htm
  8. N

    I've got the POWER!

    I am not at home right now but I got these the other day. http://imgur.com/a/VqrXk
  9. N

    I've got the POWER!

    I dont plan on loading it to 100% for sure. I am ok with it like it is (I am probly going to push 60-70 amps max), I am just worried about if it gets inspected when/if I ever sell the house.....
  10. N

    I've got the POWER!

    100 amp
  11. N

    I've got the POWER!

    Now I got a delimma, should I just say screw it and throw a 90 amp breaker in the main (I don't really need the full 100 amps) or should I ask the electrician to come back and change it? If I ask them to come back before inspection, how would I go about telling them it is wrong? Thank you
  12. N

    I've got the POWER!

    No I dont think it is, looking at the jacket it reads "3 CDR AWG 2 0 HWG 4 COMPACT... AlumaFlex (TM) AA8176 TYPE SE CABLE STYLE SER Type XHHW-2 CDRS 600 VOLTS MADE IN USA" The electrician says it is up to code and guaranteed it to pass the inspection, so once I get the rest of the wiring done...
  13. N

    I've got the POWER!

    Hi there your right up the road :)
  14. N

    I've got the POWER!

    Sorry for the late reply. I didnt do the install, i didnt want to have to feed the feeder all the way from the main panel and through the tiny space it needed to go through. Its a Square D panel, only the one 30 amp circuit installed for now but i got room for plenty more (i think its a 20...
  15. N

    I've got the POWER!

    I think this is the first thread I have ever posted here, but I am super excited today, and had to share my excitment, and this video that feels so appropriate: I finally have a 100Amp sub panel in my garage, no more tools bogging down, no more lights flickering, and not more breakers...