Recent content by nhraracer90

  1. N

    Wire size for radiant floor boiler help

    Okay gotcha. Thank you!
  2. N

    Wire size for radiant floor boiler help

    Awesome thank you!
  3. N

    Wire size for radiant floor boiler help

    Okay I figured the 10/2 is overkill but oh well lol. So I’ll run some 6/2 over and call it good then. The 18/2 for the stat would only need to go from where the boiler is to wherever I mount the thermostat right?
  4. N

    Wire size for radiant floor boiler help

    Not really. I would need to get gas which I don’t have installed here so electric is easier
  5. N

    Wire size for radiant floor boiler help

    I have attached the install manual for the boiler. I was quoted the model number B-12U FFB. It was a quote from BlueRidge Company and all he could tell me was that “I’ll need a 60a 240v breaker for the boiler and also 120v power to supply the pump relay that powers pumps and thermostats”. I...
  6. N

    Wire size for radiant floor boiler help

    Okay I will check with the 6/2 vs 6/3 wire but I could always run 6/3 just in case right and not use the extra wire? They told be I’d need a 120v circuit for the sensors, pumps and relays separate from the boiler circuit and I had some extra 10/2 laying around. I know the 10/2 is probably...
  7. N

    Wire size for radiant floor boiler help

    Hello! I need some help in determining wire size for my radiant heat boiler to run in the wall before I close the wall up (drywall). Boiler panel will be about 35-40 ft max from breaker box on the same wall. I already have the 120v wire ran (10/2) for the thermostat, some sensors, pump and...
  8. N

    HVAC recommendations

    I don’t know the electric rates. I have a separate meter for my building and it’s a different rate then my house. Looking online current LPG prices are around 3.30-3.40 gallon. During the winter we are in the high 20’s to 30’s occasionally in the teens. During the summer low 90’s and sometimes...
  9. N

    HVAC recommendations

    Okay thank you
  10. N

    HVAC recommendations

    Not yet. I’m more just looking to see what everyone’s opinions are on the difference types of systems. Of course I’ll have someone actually come figure out the correct unit size when I decide to get one
  11. N

    HVAC recommendations

    I live in WV and do not have NG so it would be propane. I would like to have AC yes. I know if I got those mini splits I’d probably need 3-4 of them placed throughout the shop. I know I would also have to run duct work for anything else. My shop is a 40x74.
  12. N

    HVAC recommendations

    Hello! I have a 2600 sq ft building w/ 14ft ceilings. It’s well insulated and so are the garage doors. I have some questions on what possible systems to get. Self contained unit: I know this unit will sit outside and you just run the duct work right inside. It would be gas heat/ac. What are the...
  13. N

    Home standby generator

    Thank you for this. Do I need 6 control wires? I was told just 2 I'm assuming a standard stranded wire?
  14. N

    Home standby generator

    What size control wires should be ran? Is it just 2?
  15. N

    Home standby generator

    Also, do I need to run control wires in a seperate conduit as well? To let the generator know when to turn on and off?