    6-12 panel with 8 spaces?

    i think 3. problem is my dad added onto the house so there is about 25 ft of wire from the panel in front to the back then a connection from the back of the house to the garage so i doubt id be able to pull in the new wire from the main panel to the back of the house. my dad use to run a...
  2. N

    6-12 panel with 8 spaces?

    yes im replacing the zinsco stuff. detached. 50ft away in pvc pipe. buried.
  3. N

    6-12 panel with 8 spaces?

    yes its a 40amp tandem breaker. everything is zinsco. im going to update the garage myself and pay a professional to do the main one on the house
  4. N

    6-12 panel with 8 spaces?

    the breaker for my garage has a double 40amp. the wiring coming into the garage is listed 8awg on all 3.
  5. N

    6-12 panel with 8 spaces?

    two 8awg should be rated for 40amps each correct?
  6. N

    6-12 panel with 8 spaces?

    damnit sorry. i forgot to add in the link. updated the post...
  7. N

    6-12 panel with 8 spaces?

    found a deal on this panel locally brand new with the extra ground bar but im confused. it says its a 6space 12circut panel but has 8 knock out spaces for breakers. can someone explain to me how that works? QO 12 Circuit Indoor Main Lug Load Center, 6 Space, 120/240V w/ Surface Mount Cover...