how long ago did you did you install solar? I would have thought the 120% rule would have let you add a (max) 40A backfed breaker to your existing 200A panel (since 20% of 200 is 40)
interesting bit about not allowing a solar connection to a sub-panel... I didn't know that was disallowed. I...
Thanks @AntonLargiader, and @Norcal for identifying the "era" when this thing was built ;)
I couldn't remember where I read about drilling your own hole but last night I found it in the Home Depot reviews... I'm not an electrician and I don't know if code prohibits drilling, so I'm hoping it's...
awww **** that's going to be a huge bummer if I can't use a hold down in there... would a CH125RB part not work (if I drill a hole for the screw)? https://www.cooper-electric.com/product/detail/25780/cutler-hammer-eaton-ch125rb
Here's a picture with the dead front off... even though it's old...
I would like to backfeed this older Cutler Hammer 100A main panel with a 2.4kW solar system that will be on a shed 25' away, and I'd like to ask if anybody knows what model panel this is, or sees any code issue with backfeeding the solar to it.
I can't find much identifying information on the...
thanks again everyone, this has been extremely helpful!
fwiw I do plan to upgrade to a 200A service, but that's a bigger project because I'm going to move it (and change windows/doors/framing in the process). I want to get this relatively small solar project done first, and possibly before the...
jeepxj... i agree about not wanting a line-side connection. but do you mean to say i'd be exceeding the 120% rule with a 2.4kW system (and if so, what calc did i mess up)? or do you mean i'd exceed the 120% rule if somebody increased it to 4.8kW it in the future (which i already know would be...
Hey thanks for the quick feedback folks! I do plan to use micro inverters (either 1 per panel or 1 per side with an APSystems model that lets you connect 4 panels to it).
And thank you jeepxj... I figured plan B would be to install a sub-panel at the shed and use 4 of the existing wires (2...
Hi,
I've got a shed about 25' from the main panel/meter which is mounted to my house, and I'd like to mount 8 solar panels on the shed roof (about 2.4kW total).
There are 2 sets of 10awg THHN wires (2 black/2 white/2 green) in 3/4 pvc conduit running from the main panel under poured concrete...