My apologies, I overlooked this posting. The heat load is approximately 72000 BTUs, The rooms are located in an old basement area. I would like to maintain temperature of 70 degrees. My budget is fairly low at $1000.
Thank you for your feedback. Do you have any suggestions for what I should do at this point? Would I be better off selling my units and purchasing the correct ones once I have the funds? I appreciate it.
Thank you everyone for your great comments. To clarify, it is the outdoor unit that ceases cooling once the outside ambient temperature dips below 64 degrees. I would prefer to avoid installation of an economizer or open air ventilation at this point, but I may consider it in the future. If I...
Hello Bruce,
Thank you for your response. The unit is a 24000 BTU AirCon Blue Series with a Mitsubishi Compressor and the specs list the cooling ambient temperature range for the outdoor unit as 64F-109F, meaning that the unit no longer cools when it is less than 64F outside in order to...
Hello,
I recently purchased and installed several mini split AC units in order to cool our server room, only to discover that these mini splits cease running below 64 degrees F. I would like to build an insulated enclosure around the unit with the proper clearances including an opening on the...
Hello,
I recently was in the process of tightening my air handler side lineset connections with a click torque wrench and the wrench never made the click sound. As a result I over tightened the liquid line and ruined the liquid line copper flare. With this said, I have two questions:
1) My...