Can anyone point me to a replacement 2 pole 100A disconnect to replace the old disconnect next to my meter. I need 4 - 2 gauge positions on the grounding/neutral bar. Maybe there is a search term/name I just don't know. I've been looking for something but cannot find exactly what I need.
>You'll also need 2 ground rods at the barn, which will connect to the ground bar in the panel.
Do I need ground rods at the at the disconnect for the barn at farmers stand or is the ground coming from the house disconnect enough? I am guessing they are connected.
Looking at the code I need to trench this 24" deep. A warning ribbon needs to be 12" above it. I am thinking I can just run conduit out the back of the garage sub panel, through the wood, and then down. This would eliminate having to deal with avoiding the house sub panel.
What I still need to...
Hello! I have what is called a 'farmer's panel' or 'farmers stand' I believe. It is a wooden panel mounted on two posts and it supports my meter and two sub panels with 100A breakers in each. One of these goes to my house and the other is unused (it used to go to a garage that has since been...