Checked code for garage receptacles, there is no exceptions for hard to reach, can't reach receptacles, all must be GFCI. I may be OK if I get the same inspector that said the nmb (romex) inside the flex whip going to the AC compressor, outside, was not a wet location therefore the nmb (romex)...
The light outlets were on a neutral from another circuit, that has been verified. The way this shed is wired, service comes in the back wall, a conduit run comes from the panel to the right front of the shed by the door where the switches for the fan and lights. A GFCI is the first outlet out...
Please be patient with me. We took out the GFCI temporally to get the lights working. This is at my son's garage, it will take a little time to get back to opening the outlets and checking the neutrals. I agree with dave*99. With the GFCI installed, all the downstream outlets worked and...
I have a similar situation as Model A Fan. I am using the downstream power from a GFCI through a switch to outlets for shop lights to plug into. The neutral on the shop light outlets is common to the neutral of the downstream GFCI. All outlets test OK. As soon as I plug in the shop lights...