Pressure switch is only six months old, could still be broken though, when I tried to start it there was about 30 psi in the system.
Correct 10-3, typo.
Yeah, I have no clue.. learning as I go on this stuff.
Distance from my basement breaker to the fused switch in the garage is about 50...
Motor spins freely, slight brushing noise.
I have a breaker in the garage next to the unit so I bumped the power with the belt off the motor, it spins but seems to hum louder than before, and the smell comes back. I fear this is not going to be a cheap fix..... What exactly goes wrong in...
I agree, no power to this thing until I figure it out. I pulled the shroud and loosened the belt, motor spins free and easy. Compressor wheel does not turn as easily as I remembered (especially when in a compression stroke), i use to be able to spin by hand over and over, now getting...
In a bind here and would really appreciate some guidance. I have an IR T30 80 gallon compressor with a WEG 184t frame 5HP single phase motor. I have been doing some light sandblasting with a 110lb pressure pot and the everything was going great but then it died. Its wired to a 30 amp cut/off...
So I found a pressure switch that can handle single phase 5hp but it's about the same price as a new mag starter for the unit.
If I purchase a new starter can I reuse the existing pressure switch? The switch is a square D with 2-pole HP rating of 2hp at 230v single phase.
If I understand you correctly I can eliminate the mag starter and wire directly to an appropriate pressure switch? Will this one work? http://www.ebay.com/itm/ingersoll-rand-pressure-switch-5-HP-/170795916739?pt=LH_DefaultDomain_0&hash=item27c43addc3#ht_500wt_1202 It appears to be rated for...
Hi,
I was wondering if anyone can help me figure out how to wire a 1 phase motor on my compressor. It is an ingersoll rand T30 that came with a 3-phase 5hp motor. I have purchased a used single phase but am totally confused on the wiring. The compressor has a pressure switch and a magnetic...