Recent content by tapia6185

  1. T

    110 Outlets not working

    If voltage at gfci, line side, is zero, then you have a problem between the breaker and the gfci. If voltage is good at line side, then your problem is at gfci, or down the line. Sent from my SM-G900V using Tapatalk
  2. T

    110 Outlets not working

    Sorry, can't Sent from my SM-G900V using Tapatalk
  3. T

    110 Outlets not working

    He is using the" pencil kind". Proximity tester. You can read voltage with that. Sent from my SM-G900V using Tapatalk
  4. T

    110 Outlets not working

    It sounds like you should be under supervision allot. You don't use a proximity tester to check for voltage. Find a good co-worker and ask, you'll be surprise, allot of people are willing to help. Sent from my SM-G900V using Tapatalk