  1. T

    Tapping feeder for subpanel using service disconnect.

    SIEMENS W0404MB1200CT 200 Amp Outdoor Trailer Panel, Gray I'd like to use this in place of the current disconnect.
  2. T

    Tapping feeder for subpanel using service disconnect.

    He's right...I was planning on running it inside but I'll do as you suggest and place a disconnect outside the workshop. I may also do as jeepxj suggests and add a feed-through panel in place of the service disconnect at the house. I also will use: 1/0-1/0-1/0-2 Notre Dame Quadruplex Aluminum...
  3. T

    Tapping feeder for subpanel using service disconnect.

    Thanks for the replies. So, I'll use the 1/0 1/0 1/0 Al Triplex URD cable tapped (using the Polaris 3 Tap connectors) from the load side of the service disconnect (given enough room if not I'll research for a different panel); buried 24". Conduit on the above ground both inside / outside to each...
  4. T

    Tapping feeder for subpanel using service disconnect.

    So I should be able to come through the bottom of the panel with 1/0 Al using Polaris Connector on the load side?
  5. T

    Tapping feeder for subpanel using service disconnect.

    So I should up to #1 AI. What about replacing that disconnect box with a QO1816M200FTRB as an example? Really appreciate the responses.
  6. T

    Tapping feeder for subpanel using service disconnect.

    Good morning everyone. I am planning on installing buried cable for my detached workshop. I plan on 100A (110 / 220) service run 175'. I will be doing all the work myself...I'm not an electrician but retired from the USAF in electronics and worked as an electrician apprentice for a couple years...