He's right...I was planning on running it inside but I'll do as you suggest and place a disconnect outside the workshop. I may also do as jeepxj suggests and add a feed-through panel in place of the service disconnect at the house. I also will use:
1/0-1/0-1/0-2 Notre Dame Quadruplex Aluminum...
Thanks for the replies. So, I'll use the 1/0 1/0 1/0 Al Triplex URD cable tapped (using the Polaris 3 Tap connectors) from the load side of the service disconnect (given enough room if not I'll research for a different panel); buried 24". Conduit on the above ground both inside / outside to each...
Good morning everyone. I am planning on installing buried cable for my detached workshop. I plan on 100A (110 / 220) service run 175'. I will be doing all the work myself...I'm not an electrician but retired from the USAF in electronics and worked as an electrician apprentice for a couple years...