keep in mind even a TEFC motor is only rated for so many starts/hr. the only way to get "unlimited" is typically TEBC or controlled acceleration (drive/soft starter). but even the soft starters are rated for something like 5/hr.
so basically you need a lift VFD and an appropriate motor if you...
I have a similar issue, but it's because someone decided to put about 150' of pipe in my house that runs around their remodel instead of a more traditional layout - about half of which is still galvanized.
if you're at the water heater, however, the outlet is up to temp in <5s.
I also typically...
it's not gas furnace slow. pretty much it slams the gas on max then dials back once it hits temp. 199k BTU is a lotta fire.
DHW tankless units are typically way more aggressive on startup than a CH/boiler. no one cares if it takes 5 seconds to light off a boiler.
EVERYONE cares if it takes...
a friendly reminder - motor dataplates list RATED power/current. if your LOAD doesn't require it, it won't pull it.
lift with a car on it uses more amps than a lift without a car on it.
this is not at all how my rinnai works. basically zero cold water comes out the "hot" port. and yes it's in "eco" mode.
i mean it does all those things just nearly instantaneously. it even stays spun up for a bit for faster relight after a draw.
heh I asked AI how to keep a motor under it's rated limit, and it told me to use the drive's protection current limit feature, and to NOT use the PI logic with amperage as the input value. I asked it specifically to tell me how to use the PI logic.
lol!
there's more than a handful of models meant for small motors that take in 120V.
https://www.invertekdrives.com/variable-frequency-drives/optidrive-e3/drive-configurator
if we do the math we run out of amps pretty fast on 120V input power.
5.8A*1.73*2=20.068 A
so I assume that's why they stop...
120V input VFDs typically have voltage doublers. kinda like old computer power supplies had that 120/220v toggle switch. same thing.
fun fact, you can run a 400v class VFD on 200v class power with... a DIY voltage doubler feeding the DC bus! precharge resistor recommended. as always, try not...
I don't think size matters as much as what the application specifies.
I happen to have a rinnai i120cn, and i've got it set up for simultaneous DHW & CH (not the default), and the only downside is while you're drawing hot water, you get 140F CH water at whatever rate it decides it can give you...