You are right....sorry i was looking at another forum that was talking abt similar topic and thats what one guy postd...but i did look up the 210.23 and still didnt see where its against code to put a lighting circuit on a 30 amp or where it would have to be hd fixtures (it may sound like im...
By figuring these fixtures at 105w per fixture you will only have 1260 watts which will equal out to 10.5amps at 120volts....you only are supposed to load a breaker 80% of its rating which on a 20 amp will be 16amps....so yes you will be perfectly fine by doing that...imo i had rather use a...