the most i would draw at one time would be 35-45 amps i reckon thats between the compressor when its running a overhead light and a small shop vac for the blast cabinet.
also i have a 60a breaker available because we no longer use our electric baseboard heat so could i just replace that breaker with a 50a breaker and be good?
ok went to the southwire web site it said the 6-6-6-6 is good for 60a. planned on running just a 220 to power my compressor and a couple of 110 lines for couple of smaller tools. so 2-2-2-4 would be a sure thing?
ok so im looking for some help on running power out to my shed/workshop. its aabout a 150 ft. run i have a 60a breaker i can use in the main box in the house. now i was told that i could use 6-6-6-6 AL but everything i have found says thats a big no no. so my question is 2-2-2-4 sufficient as i...