JackOfDiamonds
Well-known member
My mini split has the following specs:
Rated Current: 6.1 Amps
Minimum circuit ampacity: 16 Amps
Maximum circuit breaker: 25 Amps
Based on this, I should be good to run a 20A circuit and 12-guage wire, but I don't quite understand why there is a "maximum circuit breaker". Based on my industrial indoctrination, there is no such thing as a maximum circuit breaker for an appliance, because the circuit breaker is only intended to protect the installed wiring, not the appliance.
I know one day I will kick myself for not running 10ga, but 10ga wire is going to cost $300 and 12ga will be less than half that. Since actually continuous amps is only 6 Amps...
Rated Current: 6.1 Amps
Minimum circuit ampacity: 16 Amps
Maximum circuit breaker: 25 Amps
Based on this, I should be good to run a 20A circuit and 12-guage wire, but I don't quite understand why there is a "maximum circuit breaker". Based on my industrial indoctrination, there is no such thing as a maximum circuit breaker for an appliance, because the circuit breaker is only intended to protect the installed wiring, not the appliance.
I know one day I will kick myself for not running 10ga, but 10ga wire is going to cost $300 and 12ga will be less than half that. Since actually continuous amps is only 6 Amps...