My understanding is that with an old system, I shouldn't be adding dampers to close off certain ducts because the air handler wasn't designed for the increase in pressure that would result. But with a new system that uses the existing ducts, can it be set up with dampers to create what is essentially a 2 zone system?
I had my HVAC retrofitted to a two zone system. It wasn’t the easiest thing to get done, but I’m very happy with the results.
My house is an L shaped ranch. The front, rectangular section, is a 1950 ranch with blown in cellulose insulation (walls were originally not insulated, empty cavities) and new vinyl windows. Inside walls are all plaster over rock lath. The house faces south, with a huge picture window. A maple tree provides shade in the summer.
The back of the house, the leg of the L shape, was added in the 1970s. Sheetrock and fibreglass insulation, with north facing windows, and a cathedral ceiling. The thermostat was centrally located, in the front half of the house.
I have a high efficiency furnace, relatively new, with a variable speed motor. I also have a heat pump. The heat pump further complicates things. The ductwork fed each room in the front with a 9” round duct, and there was added on a large rectangular duct trunk to feed the back half of the house.
The problems were that these two halves offer very different heating and cooling action.
In the winter, sun through the picture window would heat the front of the house up, keeping the thermostat from calling for heat, and the back half of the house would cool off to uncomfortable temperatures.
In the summer, cooling the front would freeze the back.
I could, and did play with the dampers to balance this, but only at night when the sun wasn’t a factor.
I made changes to build this in to a two zone system:
The old 9” ducts were cut off the existing plenum on top of the furnace. A new horizontal rectangle plenum was built, and the ducts reattached to it. This allowed for two zones, front and back, with a minimum of new dampers.
Two of these electronic dampers were added:
A new set of controls were installed:
And a bypass damper was added:
The house now has two wireless thermostats. One for the front zone, one for the back. I went wireless because there was no way to get to the inside wall to mount and wire the rear zone ‘stat. The front zone could have been wired, but wireless is convenient.
The controller needed for this has to understand two zones, and be dual fuel capable. It is responsible for calling for heat from the heat pump when above the BECOP, or the furnace below it. Or cooling from the heat pump. The furnace itself has two heating levels, with the variable fan kicking up for “high” heat when called for.
The results are almost perfect. I can set the temperature at the thermostats, and then proceed to forget that they exist until it’s time to change them from heat to cool, or change the batteries. The house is now reasonably well balanced at all times, regardless of the time of day or how much sun we’re getting.