HVAC recommendations 1800 sq ft garage

dieseldog

Member
Joined
Nov 14, 2012
Messages
6
I'm having a 30x60 garage built that will be spray foamed and drywalled. I'm wondering if I go mini split 4 zones (wall mounted or cartridge) or central air. If mini spilt thinking of ducted and run metal tube down the middle with vents every few feet. Ductless, wall mounted 2 every 20 ft? I'm in Texas, DFW area, and looking for what will be more efficient and cheaper on electric bill. Interior will look something like the picture. It's just a rendering but it's close. There will be an office up top.
 

Attachments

  • interior.jpg
    interior.jpg
    27.2 KB · Views: 28
To avoid these ads, REGISTER NOW!

462867aa

Well-known member
Joined
Jun 19, 2018
Messages
70
Location
Oklahoma
My opinion, make it easier and cheaper to do a couple of plain 24k btu models. Split them along the long side of the shop. If you're handy, it's very easy to do.
 

loganb

ALLIANCE MEMBER
Joined
Dec 29, 2011
Messages
5,675
Location
Omaha, NE
Dedicate a zone or head to the office....the main area can probably make it with 2 heads depending on how cool you need to keep it. Run some basic Manual J heat calculator online and see what they're saying. You can also always do the rough in electrical work for a future location so the wiring is there if you decide you need it down the road.

Circulation will be a big need though with ductless units so I think you're going to want a couple of Big *** style large diameter fans for airflow. The generics are really pretty cheap and seem to work well.
 

aggie113

Well-known member
Joined
Jul 22, 2015
Messages
484
Location
San Antonio, TX
Very small unit for the office (maybe even window unit), and then two units for the garage. How much foam? Closed or open cell? How many/what size garage doors? Working in the garage or just parking/storage? Eyeballing it off that rendering, the cubic volume would be good with two 2 ton units. That would allow for temperature maintenance and times when rapid cooling/heating is needed after opening up the doors.
 
OP
D

dieseldog

Member
Joined
Nov 14, 2012
Messages
6
Very small unit for the office (maybe even window unit), and then two units for the garage. How much foam? Closed or open cell? How many/what size garage doors? Working in the garage or just parking/storage? Eyeballing it off that rendering, the cubic volume would be good with two 2 ton units. That would allow for temperature maintenance and times when rapid cooling/heating is needed after opening up the doors.
1 inch closed cell, 2 garage doors 10x10, working in the garage. Two 2 ton units sound more ideal.
 

racecougar

Well-known member
Joined
Jan 26, 2021
Messages
5,305
Location
Missouri
A) 4 separate ducted heads for a 30'x60' garage is beyond overkill, IMO. I run a single 24k unit in my 30'x60' and it does fine. Temp gradient within the building is less than 2°F. I agree with running a separate head for your closed off office, but improve on your insulation plan and you won't need so many heads. Which leads us to...

B) 1" of closed cell foam is beyond underkill. Bare minimum, IMO, is R-13 for your walls and R-38 for the ceiling, but the more you improve upon that, the more efficient and comfortable your building will be. You mention you want the building to be "efficient and cheaper on electric bill"; insulation and air sealing is the path to this.

Hopefully the 10'x10' doors are insulated sectionals and not roll-ups.
 
To avoid these ads, REGISTER NOW!

finn

Well-known member
Joined
Mar 27, 2005
Messages
16,479
Location
The UP, God's country
A) 4 separate ducted heads for a 30'x60' garage is beyond overkill, IMO. I run a single 24k unit in my 30'x60' and it does fine. Temp gradient within the building is less than 2°F. I agree with running a separate head for your closed off office, but improve on your insulation plan and you won't need so many heads. Which leads us to...

B) 1" of closed cell foam is beyond underkill. Bare minimum, IMO, is R-13 for your walls and R-38 for the ceiling, but the more you improve upon that, the more efficient and comfortable your building will be. You mention you want the building to be "efficient and cheaper on electric bill"; insulation and air sealing is the path to this.

Hopefully the 10'x10' doors are insulated sectionals and not roll-ups.
How tall are your ceilings?

Your experience makes me wonder if I’m oversizing, as my HVAC dealer and I selected a 3 ton for my 32’x75’ shop (2400 sq ft) and an 8’ tall ~10’ x~8’ utility / boiler / compressor room with no door.

The 8’x16’ - 8 ‘high office / bathroom area will have its own 6000 btu head.

I wonder if a single 24000 btu head would have been adequate for 2400 sf, even with the 16’ ceilings.

Our summer temperatures are moderate compared to much of the country, but on occasion it can get fairly humid, although nothing like Florida, the gulf coast, or the Carolinas.
 
Last edited:
OP
D

dieseldog

Member
Joined
Nov 14, 2012
Messages
6
A) 4 separate ducted heads for a 30'x60' garage is beyond overkill, IMO. I run a single 24k unit in my 30'x60' and it does fine. Temp gradient within the building is less than 2°F. I agree with running a separate head for your closed off office, but improve on your insulation plan and you won't need so many heads. Which leads us to...

B) 1" of closed cell foam is beyond underkill. Bare minimum, IMO, is R-13 for your walls and R-38 for the ceiling, but the more you improve upon that, the more efficient and comfortable your building will be. You mention you want the building to be "efficient and cheaper on electric bill"; insulation and air sealing is the path to this.

Hopefully the 10'x10' doors are insulated sectionals and not roll-ups.
A) it would be 4 ductless wall or ceiling units. I have one in my 16x24 shed and it is not enough for Texas heat.
B) I agree with you and will upgrade it to 2"
C) they are insulated.
 
OP
D

dieseldog

Member
Joined
Nov 14, 2012
Messages
6
How tall are your ceilings?

Your experience makes me wonder if I’m oversizing, as my HVAC dealer and I selected a 3 ton for my 32’x75’ shop (2400 sq ft) and an 8’ tall ~10’ x~8’ utility / boiler / compressor room with no door.

The 8’x16’ - 8 ‘high office / bathroom area will have its own 6000 btu head.

I wonder if a single 24000 btu head would have been adequate for 2400 sf, even with the 16’ ceilings.

Our summer temperatures are moderate compared to much of the country, but on occasion it can get fairly humid, although nothing like Florida, the gulf coast, or the Carolinas.
Ceiling will be about 20 ft. AI told me for 1800 sq ft I would need 3-4 ton unit.
 

racecougar

Well-known member
Joined
Jan 26, 2021
Messages
5,305
Location
Missouri
A) it would be 4 ductless wall or ceiling units. I have one in my 16x24 shed and it is not enough for Texas heat.

Okay. This part was confusing.
If mini spilt thinking of ducted and run metal tube down the middle with vents every few feet.



B) I agree with you and will upgrade it to 2"
Again, I'd advise way more than that, particularly at the ceiling.


What does your attic venting consist of?
 

Overboost44

Well-known member
Joined
Apr 29, 2020
Messages
115
Location
MD
Interesting replies. Makes me think I am being oversold for my well insulated 1000 sq ft garage with 24k having 14' ceilings, and then 12k in my 16' x13' upstairs.
 

bob smith1

Well-known member
Joined
Jul 2, 2026
Messages
80
Details are being overlooked. Building size alone does not size the equipment. Only YOU can answer the dozens of others like temp set expectation, building air tightness, E value for building. Steel roof or? 1" is it for the ceiling? think again. ALL OH doors are major leakers and not efficient. Windows? Walk doors? In all, you need a load assessment.

Then there is the 'response factor', which means if those doors will open a lot, and you want that temp returned quickly, your 4T could be close, but I still believe if you need that, you need to fix your building.

And why do all DIY shop guys hug minis like they are so awesome? They literally wrote the book on reefer leaks, and no one will fix it once you screw it up. I don't hate them, but you DO get to jack with reefer lines.

My solution? A residential packaged unit. If not familiar, look it up. Just off the cuff, 2.5T is prob about right for your space with reasonable expectation. If you want office conditions 3T.

Ducting is ALWAYS going to give you more comfort, and how the ducting gets done and tuned matters! Sizing and such, you size office space with dampers. However, it's very common to separate office from shop due to fumes and return air. That's how I fly.
 