it's quite common that people to think you need 3 wire plus ground for 240 volts

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,069
I am aware its not 120 Volt. I am looking at using it to go to the spider box which has a 4 conductor SS2-50 plug which is for RV and offshore connection of 50 amp 240 volt. I was just unsure if the nema 6-50 to nema 14-50 adapter would allow it to work. Seems like the general consensus is no it won't.
my spiderbox has a CS6375 inlet on it. so now i have a 14-50 to CS63 adapter, and a 100' SOOW CS63 cable, and all my big toys are either 14-50 or CS63.
 
To avoid these ads, REGISTER NOW!

OccupantRJ

Well-known member
Joined
May 15, 2009
Messages
11,473
Location
Eastern North Carolina
NEC allows you to use metallic conduit as ground, so it's true that you only need 2. My lathe run consists of two 12ga THHN wires in 3/4 EMT. Perfectly safe and code compliant.
Before I retired from factory life I always ran a ground inside all conduit I installed because the company paid for the wire along with my salary and I could guarantee some careless drone worker was going to knock loose a conduit joint somewhere on something and not bother telling anyone about the damage. I had a contact pocket device that simply gets touched to a machine to tell if it is properly grounded.
 

rpcraft

Well-known member
Joined
Aug 14, 2014
Messages
1,069
Location
Waco
I can't promise the is the exact listing. But it sure looks like it. If the neutral were completely missing, this cord would function properly with the Emporia Vue EVSE that I posted. The adapter is not good for an RV as others have said. The description calls out it can be used with a dryer. Not good for many reasons.


That isn't the one I was looking at but the one I was looking at was on amazon and probably similar or the same given the pricing. I think it would have been fine if I was just running downstream to my powder coat oven or a similar 3 prong device. Wanting to run the spider box off it probably would cause me issues with the GFCI until I get a proper panel installed. I need the 120 right now more than 240 output so trying to avoid throw cash at a failure of an experiment. I'm existing off a HD 120 extension cord right now but pretty sure I won't be able to run my portable 12k midea AC unit off it and I know I certainly won't be able to run anything additional off it other than that.
 

whateg01

Well-known member
Joined
Mar 13, 2006
Messages
11,852
Location
doo dah, kansas, usa
Except for when it's not?
What point are you trying to prove by pretending that what you are describing is remotely relevant to this discussion? All you do by continuing to insist that 240 uses a hot and a neutral in the USA is confuse new people who don't know any better. Does it exist? Yes. Is it relevant? Not at all.
 

CGT80

Well-known member
Joined
Aug 29, 2014
Messages
893
Location
IE, SoCal, USA
NEC allows you to use metallic conduit as ground, so it's true that you only need 2. My lathe run consists of two 12ga THHN wires in 3/4 EMT. Perfectly safe and code compliant.
This is where I was going, when I asked what conductors were behind that 6-50r and whether it was metallic conduit.

I knew that NEC allowed it in the past, but was not sure if it is still allowed, plus some people prefer a dedicated ground wire instead of all the connection points that can exist with conduit.

Code, past code, and what works are all different things.
 

CGT80

Well-known member
Joined
Aug 29, 2014
Messages
893
Location
IE, SoCal, USA
Except for when it's not?
Line to neutral is often 277 volt as well.

It also is not relevant to this thread. A smart person wouldn't waste time either trying to show off or just picking nits for the sake of arguing.

How are your comments helpful or relevant to the topic in this thread?

Maybe you should go start an electrical trivia thread......
 

Snapped-off

Well-known member
Joined
Feb 22, 2012
Messages
4,853
Location
Indiana
What point are you trying to prove by pretending that what you are describing is remotely relevant to this discussion? All you do by continuing to insist that 240 uses a hot and a neutral in the USA is confuse new people who don't know any better. Does it exist? Yes. Is it relevant? Not at all.
No less relevant than what ya'll are discussing in a thread about a heater. Read the thread title.
 

rpcraft

Well-known member
Joined
Aug 14, 2014
Messages
1,069
Location
Waco
How much more are your taxes if it's no longer a storage shed. Seems like a huge hassle to avoid a few bucks
Year over year who knows but considering up front the electricians quoted me 15K to install a meter loop I'll start there. I'm also in the city so there is codes to be followed and you need a licensed sparky for all the inspections. After that figure out whatever the county wants to asses and charge over the years I will still be living here.. I'll pass.

Side note.. The electricians had to be high AF when they quoted me that but I didn't bother to get a second quote after that session to be honest.

Right now I have a grand total of $620 invested and maybe another 250 to 300 if I do go ahead and add the subpanel in my garage with the wiring, plugs, conduit and other nick-nacks.

I have the spider box on the way as well as the other proper connectors to go in and out of it so right now the 20$ mystery is if I can use the adapter and at this point I can experiment with the 14-50 to 6-50 adapter on the offshore cables I have. I just went ahead and bought it along with the spider box and stuff. I figure for the time being my powder coat oven is still in the garage, since I have been holding off moving it to the shop (have to move a few things around and get a buddy to help me push and pull it) and I can move the section of that test circuit out in the driveway and flip the breakers and see if the GFCI's trip on the spider box. If somehow it doesn't then I will plug the SS2-50 adapter for the output in and plug in my oven and give it a test.

Down the road when I do the solar I will probably have 1500 invested in that.

Still plenty less then 15k as the beginner entry.
 
OP
T

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
26,151
Location
Niagara Region, Ontario, Canada
Pre 1996 dryers and ranges were wired without a ground.
I don't think Canada ever had that , at least I've never seen it and our first drier was in the late 70's,
thinking more on this, our stoves & driers were basically hard wired with no plug & outlets till the late 70's or early 80's .
if you wanted to move them you had to disconnect the wire from the terminals
 
To avoid these ads, REGISTER NOW!

Cruzan80

Well-known member
Joined
Jul 22, 2015
Messages
4,445
Location
Denver, CO
What point are you trying to prove by pretending that what you are describing is remotely relevant to this discussion? All you do by continuing to insist that 240 uses a hot and a neutral in the USA is confuse new people who don't know any better. Does it exist? Yes. Is it relevant? Not at all.
I think the bigger issue is that he keeps trying to claim it is relevant to the thread title. Even if someone were to need 240V Hot/Neutral (in a super specialized 3ph service using only one leg), they would still only need two wires for it (plus ground). So not sure what he would use the third wire for, just like the OP states!
 

OccupantRJ

Well-known member
Joined
May 15, 2009
Messages
11,473
Location
Eastern North Carolina
My grandmother had a big shed as a workshop. There was a post with a receptacle outside it, like for an RV. The shed plugged in and was still considered movable and not a permanent structure.
I did the same with my first small workshop in my parent’s back yard. The electrical inspector who lived around the corner suggested it.
 

mikedodge

Well-known member
Joined
Jun 27, 2017
Messages
2,923
I don't think Canada ever had that , at least I've never seen it and our first drier was in the late 70's, it has a 14-30
I remember being at my now ex's friend in Syracuse NY in the mid 90's and seeing the drier plug, I thought it was odd .

Our old dryer was from the 60s and had a ground and was also hard wired. The first time I heard of a dryer having a plug I thought it was strange too.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,237
Location
Coronado, CA
My Welder and table saw are Connected to my 200 Amp service panel. The neutral and the Ground are tied together in the main panel, but are separated in the Sub Panels.

When I extended three phase 208-240 volt circuits i typically pulled in 5 conductors; 3 hots, a neutral and a Ground.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,219
Location
Modesto, CA
Many types of metallic conduit can be used as EGC. A low resistance ground is required. A ground wire is not.

NEC 250.118

the conduit would be counted as the third wire since its being used as the EGC but the code you cited is incorrect. saying only 2 wires are needed and nothing else is incorrect, which is what I was correcting
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,238
Location
NJ
Many types of metallic conduit can be used as EGC. A low resistance ground is required. A ground wire is not.

NEC 250.118
When using flexible metallic conduits as egc, only good for circuits 20A or less. 6' or less. Otherwise need a ground wire.
 
Last edited:

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,118
Location
Central Iowa
250.118(4)
250.118(A)(4) states EMT is an acceptable EGC. 250.118(B) states GEC's can't be used as EGC's and there is no #4.

Below is the quote that I originally quoted.
Many types of metallic conduit can be used as EGC. A low resistance ground is required. A ground wire is not.

NEC 250.118
A ground wire is not what? Going by what you said, it appears you are stating a ground wire is not an egc.
 

JackOfDiamonds

Well-known member
Joined
Jul 31, 2020
Messages
717
Location
Idaho (USA)
A metallic raceway can often serve as a equipment grounding conductor, such that a dedicated ground wire is not required. Common cases include a 240v circuit in EMT, which requires only two wires. I am not an electrician I just play one on the Internet. Consult your local AHJ.
 